Thread: R22 to R410A retrofit
-
08-10-2008, 04:24 PM #1
R22 to R410A retrofit
We have switched out 6 R22 Carrier Split Heat Pumps for 6 R410A Carrier Heat Pumps. There is over 720ft of piping in the system, is there a need to replace the linesets, also we have purged the lines with nitrogen as well had them under pressure for two weeks?
-
08-10-2008, 07:53 PM #2
Re: R22 to R410A retrofit
Have you also cleaned the lines of contaminants and oil ?
Perhaps take out an accessible section of pipe and strength test it to R410a standards.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
09-10-2008, 02:46 PM #3
Re: R22 to R410A retrofit
Could clean the line sets with PF-16 Pro-Flush, but not entirely sure that this is necessary. The line sets are 99% horizontal line sizes are 7/8" and 3/8" on the liquid side. Were just talking about 3 ton systems.
-
09-10-2008, 06:07 PM #4
Re: R22 to R410A retrofit
i think the best is to flush them twice to be sure they are clean.
Ice
-
09-10-2008, 06:52 PM #5
Re: R22 to R410A retrofit
Think that client is going to try to make us change out the piping. This is a terrible waste of resources.
-
09-10-2008, 06:54 PM #6
Re: R22 to R410A retrofit
1/ Confirm wall thickness on the 7/8 tube & confirm with the copper tube manufacturer that the tube is strong enough for 410a pressure.
2/ Confirm with Carrier what the saftey HP cutout pressure is.
Some split & VRF systems have HP cutout at 41.5 bar for 410a & if the indoor unit air fillers get blocked because someone forgot to clean them or any other problem which causes reduced air flow then the system can run at over 40 bar on the 7/8 gas tube.
3/ Make sure you have an oil drain port on the compressor shell & carry out oil test with a refractrometer after the systems has been running for a few days. Then you can measure any mineral oil contamination & carry out an oil change.
-
10-10-2008, 09:33 AM #7
Re: R22 to R410A retrofit
The R-22 gas is used with mineral oil, but R-404a gas essentially requires synthetic lubrication oil. These two oils does not go together. Therefore abosolute cleaning is necessary
-
10-10-2008, 12:42 PM #8
Re: R22 to R410A retrofit
Jodem,
have you any more details about your flushing agent you mentioned - PF-16 Pro-Flush?Tony
-
13-10-2008, 05:07 AM #9
Re: R22 to R410A retrofit
Be very careful, R22 7/8" pipe is not rated for 410A use. 410A runs at a much higher pressure and the wall thickness of 410A pipe is much thicker. the oil problems may the least of your problems.
-
14-10-2008, 08:12 PM #10
-
14-10-2008, 09:04 PM #11
Re: R22 to R410A retrofit
Its all down to the gauge.
Check the link
http://www.hrponline.co.uk/hrp.stati...dInfo18xls.pdf
the copper also has to be undamaged - no scratches/gouges or dents as they will cause weakpoints in the wall
Brit
Brit
Similar Threads
-
Pressure Testing for R410a
By Pooh in forum Tools and CalculatorsReplies: 33Last Post: 13-08-2008, 11:41 PM -
R410A pressure in air conditioning
By irwinchong80 in forum Technical DiscussionsReplies: 4Last Post: 06-10-2007, 07:33 PM -
R410A - state of art
By MrReds in forum RefrigerantsReplies: 2Last Post: 04-03-2007, 10:56 PM -
Detection - is it air or R410A?
By stalker in forum Technical SpeculationsReplies: 21Last Post: 24-02-2007, 01:48 AM -
R410A captube sizing for 2.5 bar / 35 psi pressure drop
By DaBit in forum Technical SpeculationsReplies: 10Last Post: 27-11-2003, 09:05 AM