    Airwell BS 36 Technical Manual



    New to R.E.and new to refrigeration.(Did Carnotīs cycle for school physics!)

    At 72, I am unlikely to ever earn money as a refrigeration engineer. But with a fixed income (pension rapidly losing value) the ability to understand and service all things technical around the house should help us to survive.

    Our house (in Spain) boasts an Airwell BS 36 reversible air-conditioner with remote control.

    The unit has been working fine in cooling mode during the summer. Last week it was a bit cool in the evening so tried it in heating mode. Hot air flowed for about half an hour but then the overcurrent breaker tripped in our consumer unit.

    Further tests during the week established that in heating mode it will run for anything from 10 mins to an hour, but then takes out the overcurrent breaker.

    I have an installation manual, but this is limited to showing the indoor and outdoor units as boxes with connection details for pipes and wires between the two boxes.

    52 years experience in the electronics industry has taught me that the "black box" approach to system fault finding is great if you have spare "black boxes" but doesn't help with understanding why the "black box" is failing.

    I guess that a detailed technical manual is needed. Does anyone know where I can get one?

    Scanning the web so far has only found disturbing news about Airwell AU in administration. Maybe a tech manual is more urgent than I anticipated!!

    Cliff Bell



  2. #2
    Join Date
    Nov 2007
    Location
    Scotland
    Age
    67
    Posts
    141
    Rep Power
    17

    Re: Airwell BS 36 Technical Manual

    You should be able to get the info you require direct from the France HQ I have a contact there but not the details to hand.Have you checked that the running current is OK and matches the breaker as the unit will probably run at higher current on heating as it probably has direct electric elements as a boost to the heat pump mode and it will be staged so maybe that is the problem.

  3. #3
    Join Date
    Aug 2007
    Location
    Russia
    Posts
    138
    Rep Power
    21

    Re: Airwell BS 36 Technical Manual


  4. #4
    Join Date
    Oct 2008
    Location
    Spain
    Age
    88
    Posts
    5
    Rep Power
    0

    Re: Airwell BS 36 Technical Manual

    Thanks for that Yin(?).
    We are new to this house, and Iīm told by the previous owner that it ran fine last winter, and doesnīt have an auxilliary heater. ( Never gets cold enough in this part of Spain!!! They say !!!!) Thats why I would like a comprehensive service manual to know what Iīm dealing with.

  5. #5
    Join Date
    Oct 2008
    Location
    Spain
    Age
    88
    Posts
    5
    Rep Power
    0

    Re: Airwell BS 36 Technical Manual

    Thanks Narcom.
    Guess I might need to research the Model No a bit more. There are no Bxxxx numbers on that web site.

  6. #6
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: Airwell BS 36 Technical Manual

    Are the filters clean on the indoor unit?

    Multisync
    London

  7. #7
    Join Date
    Oct 2008
    Location
    Spain
    Age
    88
    Posts
    5
    Rep Power
    0

    Re: Airwell BS 36 Technical Manual

    Yes, first thing I did without knowing anything about the unit. I find a lot of problems with computers in Spain are caused by clogged up cooling fins and filters, so thought the same might apply to air-con.

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Airwell BS 36 Technical Manual

    Quote Originally Posted by Electricliff View Post
    Yes, first thing I did without knowing anything about the unit. I find a lot of problems with computers in Spain are caused by clogged up cooling fins and filters, so thought the same might apply to air-con.
    If your outdoor temperature is higher than 15°C your air conditioner is overloaded and because it doesn't have High pressure switch, compressor keeps turning till point when his motor cannot overcome pressure. Therefore motor stalls and current breaker trips. Do not use air conditioner in heat mode when outdoor is higher than 15°C

  9. #9
    Join Date
    Aug 2007
    Location
    Russia
    Posts
    138
    Rep Power
    21

    Re: Airwell BS 36 Technical Manual

    Quote Originally Posted by Electricliff View Post
    Thanks Narcom.
    Guess I might need to research the Model No a bit more. There are no Bxxxx numbers on that web site.
    BS36 is an indoor unit.
    I guess you should search an OUTDOOR unit.

  10. #10
    Join Date
    Feb 2008
    Location
    stoke on trent
    Posts
    6
    Rep Power
    0

    Re: Airwell BS 36 Technical Manual

    easy answer is it will pull more current on heating and your fuse is probably not motor rated

  11. #11
    Join Date
    Nov 2006
    Location
    At home
    Posts
    181
    Rep Power
    18

    Re: Airwell BS 36 Technical Manual

    great link narcom thanks

  12. #12
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Airwell BS 36 Technical Manual

    As leestoke wrote; check that the MCB is motor rated.

    Ambient temps might be a problem.

    BUT

    If we trust the previous owner when he says that it worked last year, then we are looking at something that has gone wrong.

    The only bit that would be energised in heating but not in cooling is the 4-port valve's coil.
    This is a "header" thingie with one pipe attached from above and three pipes from below (hence 4 port). On its side will be a solenoid coil with 2 leads attached to it.
    (Normally it is fitted close to the compressor)

    Disconnect (or cut, but if you do you will have to make good) the leads and check that the coil isn't down to earth.
    If it's not down to earth, remove the coil and visibly inspect it (cracks or hot marks?), also check the resistance across the coil.

    Good hunting.


    P.S. Removing the coil should not cause any refrigerant leaks, on very rare occasions a shortened coil have burnt through the stem it been fitted to. If it has, then the whole valve will need replacing and that's a job for a professional.
    Last edited by The Viking; 17-10-2008 at 07:50 PM.

  13. #13
    Join Date
    Oct 2008
    Location
    Spain
    Age
    88
    Posts
    5
    Rep Power
    0

    Re: Airwell BS 36 Technical Manual

    OK guys and many thanks. you've given me a lot to think about and try. Will get the thermometer out next time the good lady wants heat and test the outside temperature. If that doesnīt work it's check this four port valve and keep fingers crossed that itīs only the coil.
    Thanks again

  14. #14
    Join Date
    May 2008
    Location
    England
    Posts
    101
    Rep Power
    16

    Re: Airwell BS 36 Technical Manual

    You could contact Airwell UK

    Head Office

    Airwell (UK) Ltd.
    St. Thomas Street Business Centre
    St. Thomas Street
    Newcastle upon Tyne
    Tyne & Wear
    NE1 4LE


    Tel: 0191 2221567
    Fax: 0191 2221307


    Good luck though!

  15. #15
    Austech5's Avatar
    Austech5 Guest

    Wink Re: Airwell BS 36 Technical Manual

    Sorry it has taken so long for this reply but only just started on the net. I was looking for manuals myself and read about your trouble.

    I have been working on Airwells for years now in Australia. Your model doesn't ring any bells but the same principle applies to all brands and models.

    Ambient temps above 18 are not ideal but it shouldn't trip the breaker.

    Some models will have a sensor on the indoor coil.(mainly hi-wall splits) This coils is designed to both hold the indoor fan off until the indoor coil warms up in heating mode, and to cycle the outdoor fan off when the indoor coil gets too hot. Cycling the outdoor fan off in heating mode reduces the amount of heat absorbed and reduces discharge pressure and power. Your next problem will be getting a sensor. Let me know if you still have trouble I may be able to get resistance to temperature chart to source a thermistor.

    One other common cause is too much refrigerant. You may need a tech to check the pressures it operates at on an 18 degree day. If there is no indoor sensor too much gas will be your problem. A quick test is to partially block the air flow through the outdoor coil. You should find the system will run for much longer. (I don't recommend doing this for too long though as damage to compressor valves can occur) If this is the case please ensure small amount refrigerant is reclaimed into a bottle by a qualified tech.

    Hope I wasn't too late finding this site for you. I'm sure there will be many of people who learn from it anyhow.

Similar Threads

  1. Carrier 30GX Service Manual Required
    By Hatchy in forum Refrigeration Books
    Replies: 25
    Last Post: 05-11-2010, 07:58 PM
  2. ALFA LAVAL Technical Manual
    By winfred.dela in forum Refrigeration Books
    Replies: 38
    Last Post: 11-07-2010, 12:16 PM
  3. Airwell Problem
    By meadows in forum Heat Pumps
    Replies: 4
    Last Post: 17-04-2009, 09:56 PM
  4. LG Technical Support
    By hendrag in forum Air Conditioning
    Replies: 38
    Last Post: 07-04-2009, 12:56 PM
  5. HP Switches (Manual or Auto)
    By Latte in forum Technical Discussions
    Replies: 9
    Last Post: 02-06-2005, 07:48 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •