Thread: Heat Pump - 4 Way Valve.
04-10-2008, 09:36 PM #1
I was wondering if anyone could help please.
I have a quick college question.
Heat Pump -
HEATING MODE - Discharge to indoor coil, indoor coil to compressor suction.
COOLING MODE - Discharge to outside coil, indoor coil to compressor suction.
When these cycles are switched how is the refrigerant metered by the TEV's ? or are the refrigerant flows bypassed and only sent through only one TEV on each cycle ? - I assume one way valves on each side and a bi-flow filter etc..
Any imput ?
04-10-2008, 09:52 PM #2
Re: Heat Pump - 4 Way Valve.
You will either have two metering devices (expansion valve/ accurator) in circuit one each for cooling or heating. Alternatively a two way device (capiiliary or electronic expansion valve).
In the case of the TEV they will usually each have a bypass circuit with a check valve. An accurator will only provide expansion in one direction, the expansion orriface being pushed out of the way when not required.
A capiliary is a fixed oriface and will provide the same pressure drop with flow in either direction. An electronic expansion device will regulate depending on the mode.
A biflow filter can be used but usually only a strainer is needed
Brit
05-10-2008, 09:38 AM #3
Thankyou once again Sir !.
All the best
05-10-2008, 02:35 PM #4
in addition whit the capillary there is the strainer,where inside is like a metal marble ho is correcting the flow ore amount of refrigerant.try and find an old unit and dismount it completely, open the parts as well. thats how i learned it in the old days. you understand the working parts better then.
Ice
Capacity control
By sparrow in forum TrainingReplies: 44Last Post: 18-01-2010, 08:49 PM -
DIY heat pump 12kW
By kimusabi in forum FundamentalsReplies: 11Last Post: 17-10-2009, 07:50 PM -
frostles heat pump
SL/SB-400 Pump Down Procedures
By absolute-zero in forum TransportReplies: 1Last Post: 29-01-2008, 10:27 PM -
Domestic VRF heat pump?
By electronicsuk in forum Heat PumpsReplies: 8Last Post: 30-10-2007, 08:53 AM