    Heat Pump - 4 Way Valve.



    I was wondering if anyone could help please.

    I have a quick college question.

    Heat Pump -

    HEATING MODE - Discharge to indoor coil, indoor coil to compressor suction.

    COOLING MODE - Discharge to outside coil, indoor coil to compressor suction.

    When these cycles are switched how is the refrigerant metered by the TEV's ? or are the refrigerant flows bypassed and only sent through only one TEV on each cycle ? - I assume one way valves on each side and a bi-flow filter etc..

    Any imput ?



  2. #2
    Join Date
    Dec 2001
    Location
    UK
    Posts
    137
    Rep Power
    23

    Re: Heat Pump - 4 Way Valve.

    You will either have two metering devices (expansion valve/ accurator) in circuit one each for cooling or heating. Alternatively a two way device (capiiliary or electronic expansion valve).
    In the case of the TEV they will usually each have a bypass circuit with a check valve. An accurator will only provide expansion in one direction, the expansion orriface being pushed out of the way when not required.
    A capiliary is a fixed oriface and will provide the same pressure drop with flow in either direction. An electronic expansion device will regulate depending on the mode.
    A biflow filter can be used but usually only a strainer is needed
    Brit

  3. #3
    Join Date
    May 2008
    Location
    UK
    Posts
    50
    Rep Power
    16

    Re: Heat Pump - 4 Way Valve.

    Thankyou once again Sir !.
    All the best

  4. #4
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Heat Pump - 4 Way Valve.

    Quote Originally Posted by BritCit_Juve View Post
    A capiliary is a fixed oriface and will provide the same pressure drop with flow in either direction. An electronic expansion device will regulate depending on the mode.
    A biflow filter can be used but usually only a strainer is needed
    Brit
    in addition whit the capillary there is the strainer,where inside is like a metal marble ho is correcting the flow ore amount of refrigerant.try and find an old unit and dismount it completely, open the parts as well. thats how i learned it in the old days. you understand the working parts better then.

    Ice

Similar Threads

  1. Capacity control
    By sparrow in forum Training
    Replies: 44
    Last Post: 18-01-2010, 08:49 PM
  2. DIY heat pump 12kW
    By kimusabi in forum Fundamentals
    Replies: 11
    Last Post: 17-10-2009, 07:50 PM
  3. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  4. SL/SB-400 Pump Down Procedures
    By absolute-zero in forum Transport
    Replies: 1
    Last Post: 29-01-2008, 10:27 PM
  5. Domestic VRF heat pump?
    By electronicsuk in forum Heat Pumps
    Replies: 8
    Last Post: 30-10-2007, 08:53 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •