    manutecamp's Avatar
    manutecamp Guest
    Electronic expansion valve
    I need to know the brand of an electronic expansion valve, which comes in a Chiller of Trane.
    The Chiller is RTHC with a number of series EKM ----
    Please.
    11,025
    Re: Electronic expansion valve
    Are there any details on the valve or valve actuator that you can help us with?
    manutecamp's Avatar
    manutecamp Guest
    The Chiller is not working and they do not know why; they think it is the valve or the actuator.
    I think the brand is sporlan
    Split Croatia
    57
    6,151
    36
    Quote Originally Posted by manutecamp View Post
    Who are they and how are they came to that conclusion?
    What you done to came to that conclusion?
    If chiller doesn't working how you/they know that EEV is faulty?
    http://www.frigodesign.ru/sale/sporlan/100-20-1.pdf
    May 2008
    Malta
    68
    67
    What a jump to conclude you have a faulty expansion valve did you run a system test,you will find that the valve can be run to check the windings and voltage output very often the problem will be with the wire or plug.
    Aug 2003
    Netherlands
    49
    620
    21
    Or in this case the expansion valve module.
    An RTHC as a UCM-CLD. The expansion module can be at fault.
    My sugestion is to get Trane out to the unit and have them check it out. Be sure to have enough load to get the machine running at full load, to check the refridgerant charge!
    If you want to order the valve you'll have to order it from trane. You need the complete model number and serial number to order!
  1. the function of the electronic expansion valve
    By Crystal-426 in forum Fundamentals
    Last Post: 22-06-2008, 12:29 PM
  2. Electronic expansion valve
    By J-Roshdi in forum Fundamentals
    Last Post: 25-06-2007, 06:24 AM
  3. Electronic expansion valve for flooded chillers
    By lowtempref in forum Industrial
    Last Post: 15-10-2006, 11:36 PM
  4. Oversizing EXV electronic expansion valve
    By aygul in forum Technical Discussions
    Last Post: 20-11-2003, 01:00 PM