Results 1 to 6 of 6
Thread: Electronic expansion valve
-
02-10-2008, 06:08 PM #1
Electronic expansion valve
I need to know the brand of an electronic expansion valve, which comes in a Chiller of Trane.
The Chiller is RTHC with a number of series EKM ----
Please.
-
02-10-2008, 11:53 PM #2
Re: Electronic expansion valve
Are there any details on the valve or valve actuator that you can help us with?
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
03-10-2008, 01:42 PM #3
Re: Electronic expansion valve
The Chiller is not working and they do not know why; they think it is the valve or the actuator.
I think the brand is sporlan
-
03-10-2008, 02:09 PM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Electronic expansion valve
Who are they and how are they came to that conclusion?
What you done to came to that conclusion?
If chiller doesn't working how you/they know that EEV is faulty?
http://www.frigodesign.ru/sale/sporlan/100-20-1.pdfLast edited by nike123; 03-10-2008 at 02:35 PM.
-
03-10-2008, 02:20 PM #5
Re: Electronic expansion valve
What a jump to conclude you have a faulty expansion valve did you run a system test,you will find that the valve can be run to check the windings and voltage output very often the problem will be with the wire or plug.
-
07-10-2008, 09:18 PM #6
Re: Electronic expansion valve
Or in this case the expansion valve module.
An RTHC as a UCM-CLD. The expansion module can be at fault.
My sugestion is to get Trane out to the unit and have them check it out. Be sure to have enough load to get the machine running at full load, to check the refridgerant charge!
If you want to order the valve you'll have to order it from trane. You need the complete model number and serial number to order!
Similar Threads
-
the function of the electronic expansion valve
By Crystal-426 in forum FundamentalsReplies: 10Last Post: 22-06-2008, 12:29 PM -
Electronic expansion valve
By J-Roshdi in forum FundamentalsReplies: 3Last Post: 25-06-2007, 06:24 AM -
Electronic expansion valve for flooded chillers
By lowtempref in forum IndustrialReplies: 6Last Post: 15-10-2006, 11:36 PM -
Oversizing EXV electronic expansion valve
By aygul in forum Technical DiscussionsReplies: 5Last Post: 20-11-2003, 01:00 PM