    mitsubishi mr slim P6 error



    hi chaps,
    i have a re-occuring error code p6 on a mitsi mr slim unit .

    have followed the mitsi fault code sheets and have found no fault.

    the unit checks out fine in all modes of operation and works fine for a period of time then fails with the same problem.

    have any of you any pointers ,or have come across this before,

    any input would be greatful

    thanks..



  2. #2
    Join Date
    Dec 2006
    Location
    Mansfield
    Age
    57
    Posts
    231
    Rep Power
    0

    Re: mitsubishi mr slim P6 error

    I have come across this before and allways found it to be refrigerant charge problem.

    Regards

    PP

  3. #3
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: mitsubishi mr slim P6 error

    Mr Slim A control R407c & R410a systems.
    P6 = indoor coil frost protection in cooling or indoor coil overheat protection in heating.

    Cooling
    One of the 2 indoor coil sensors reads minus 15 deg C for 3 mins.
    Heating
    One of the indoor coil sensors reads over 70 deg C.

    If you are sure the refrigerant charge is correct & system operation is correct then it could be a coil temperature sensor reading wrong temperature.
    If you have one of those little monitor things which plug into the outdoor circuit board you can monitor the indoor coil temperature.
    On later type remote controllers you can get all operating data like temp sensor data but you will need a service manual to do this.
    Or you can measure the ohms resistance of the temp sensors & compare with the chart in the service manual.

  4. #4
    hishvac's Avatar
    hishvac Guest

    Re: mitsubishi mr slim P6 error

    Having the p6 error code problem with a mr slim pu42ek21. any advice. pressure washed evap section . was plugged> topped off charge was 88 degrees in space with a 75 back.

  5. #5
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: mitsubishi mr slim P6 error

    I suspect that you have an R22 K control cooling only system.
    On the old R22 K series Mr Slim systems sold in the UK P6 is coil frost fault in cooling mode & the indoor coil temperature sensor must be reading below +1 deg C.
    So if you are sure indoor fan is working correctly & coil is clean most likely cause could be.
    1/ indoor coil temp sensor fault
    2/ short of gas
    3/ part blockage of liquid line capillary

    On the old UK models from early 1990's you could read the aprox indoor coil temp using the hard wired remote controller. In test mode the remote controller gave a code for the indoor coil temp & a chart in the service manual to convert.
    As your unit is USA model & deg F I suspect it my be slightly different

Similar Threads

  1. mr slim p8 error code
    By Krups in forum Air Conditioning
    Replies: 23
    Last Post: 17-02-2011, 07:18 PM
  2. Mitsubishi Mr Slim Error Codes
    By Iceman410 in forum Air Conditioning
    Replies: 9
    Last Post: 11-02-2011, 07:44 PM
  3. mitsubishi mr slim
    By derekbradbury in forum Trouble Shooting
    Replies: 7
    Last Post: 13-01-2010, 07:26 PM
  4. Mitsubishi Mr Slim
    By RatsPom in forum Air Conditioning
    Replies: 4
    Last Post: 12-08-2008, 06:46 PM
  5. mitsubishi mr slim master and slave
    By r600a-bang in forum Air Conditioning
    Replies: 2
    Last Post: 24-07-2006, 10:24 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •