    What would happen if you added R134A to R12?



    Further to Richard Ellison's question.
    What would happen if you added R134a to a system charged with R12.
    IE Topped up with R134a without realising that the system had not been "Retro Fitted" (remember that term guys?)
    Surely if R134a is truly a "drop in" Nothing???
    Grizzly



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: What would happen if you added R134A to R12?

    Don't forget that solubility of mineral oil in R134a is not good and that R134a is not "drop in" just because of that. They seem to coexist just fine, but, since mineral oil is not miscible with R-134a, you'll need to use a suitable oil.

    Since you have some amount of R12 in system, that could work perfectly fine, but that depend on ratio of R12 in mixture.
    And, as we know, you have mixture of unknown thermal properties to be able to properly measure and diagnose system.

  3. #3
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: What would happen if you added R134A to R12?

    I have seen systems where this has happened and you would not be able to tell from the way it operated that it had a mixture of refrigerants. If there was little R12 left in the system you would get a milky looking refrigerant flow in the sight glass and as you know poor oil return.

    When i used to do retrofits years ago we did a few backwards, that is to say changed the oil and refrigerant on the first visit (due to no R12 on the van) and then call back over the next few weeks to do three more oil changes with no problems.

    Jon

  4. #4
    Shadab's Avatar
    Shadab Guest

    Re: What would happen if you added R134A to R12?

    i ve charged R 134a in a Thermoking equiped airconditioned bus instead of R12, which has fouled condenser coil.. my observations are
    1. good cooling without changing compressor oil
    2. good circulation of oil
    3. But starting the system, heavy flooding of liquid on compressor cylinders, crank case, while the compressor got to warm up

Similar Threads

  1. R507 in an R134a compressor: any danger?
    By DaBit in forum Technical Speculations
    Replies: 30
    Last Post: 21-12-2009, 12:44 AM
  2. r134a as a substitute for r22?
    By m-nelson in forum Supermarket Refrigeration
    Replies: 5
    Last Post: 24-08-2007, 11:16 PM
  3. Pressure Transmitter R134a Setpoints
    By cooltrain in forum Technical Speculations
    Replies: 0
    Last Post: 28-02-2005, 09:05 AM
  4. Replies: 5
    Last Post: 01-03-2004, 09:59 PM
  5. R507 in an R134a compressor: system design
    By DaBit in forum Technical Speculations
    Replies: 17
    Last Post: 01-05-2003, 09:25 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •