    please help me to solve the problem in trane rtac 275 chiller.
    circuit 1a low oil flow alarm.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: trane rtac 275

    Check the oil
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: trane rtac 275

    If the intermediate oil pressure transducer was out of acceptable range for 15 seconds while the pressure difference was greater them 35psid.

    Was this during start up or after 2.5 minutes?

  4. #4
    Join Date
    Aug 2007
    Location
    Russia
    Posts
    138
    Rep Power
    21

    Re: trane rtac 275

    I guess this manual will be useful (13.5 MByte)
    http://www.mark-off.ru/fam/eqpmnt/ma...aintenance.RAR

  5. #5
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: trane rtac 275

    Quote Originally Posted by narkom View Post
    I guess this manual will be useful (13.5 MByte)
    http://www.mark-off.ru/fam/eqpmnt/ma...aintenance.RAR
    Hi Narkom.
    Your kindness is well received.
    Sadly your link does not appear to work, well from the U.K. anyway!
    Sorry Steve

    Sorry I lied as on the way out of the post I tried the link once more and for some reason it worked!!!!
    How did and where did you post it to enable us to share it?
    Others have suggested Mediafire, but if I want to post anything larger than 100kb.
    I have to pay!
    Steve
    Last edited by Grizzly; 01-10-2008 at 04:19 PM.

  6. #6
    Join Date
    Aug 2007
    Location
    Russia
    Posts
    138
    Rep Power
    21

    Re: trane rtac 275

    OK!
    http://www.mediafire.com/?1nmvygiyygr
    Mediafire free upload limit is 100Mbyte ))

  7. #7
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: trane rtac 275

    Quote Originally Posted by narkom View Post
    OK!
    http://www.mediafire.com/?1nmvygiyygr
    Mediafire free upload limit is 100Mbyte ))
    Thanks for the info I will check it out
    Grizzly

Similar Threads

  1. Trane RTAC Software Download
    By sean in forum Commercial
    Replies: 4
    Last Post: 30-09-2008, 12:36 PM
  2. Trane Defrost Control Board Energize "W" in cooling
    By jcmorris2 in forum Heat Pumps
    Replies: 6
    Last Post: 02-06-2007, 03:40 AM
  3. Trane nomenclature
    By Claudio in forum Fundamentals
    Replies: 3
    Last Post: 12-04-2007, 09:59 AM
  4. Similarities (differences) McQUAY vs. TRANE
    By Jacek in forum Air Conditioning
    Replies: 3
    Last Post: 01-04-2007, 09:46 PM
  5. Trane CROE1
    By Peter_1 in forum Industrial
    Replies: 10
    Last Post: 06-03-2004, 07:42 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •