    Split 3 way valve



    Hi

    Regarding ductless mini-split systems

    I have a doubt about the 3 way valve on the outdoor unit gas side

    Are them all only 2 position (closed/open) with a schrader valve on the service port ?

    Or are some of them 3 position, like in the compressor valves in refrigeration system ?

    Moises



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Split 3 way valve

    They are normally only 2 position valves, some have a Schraeder, some do not.



    They are not back-seating valves only open/close.

    Back-seat Valve ---
    Last edited by Brian_UK; 12-05-2009 at 11:48 PM.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Split 3 way valve

    Are you talking about the reversing valve, if you are they are oneway or the other, no in-btween.
    magoo

  4. #4
    Join Date
    Dec 2008
    Location
    Brazil
    Posts
    106
    Rep Power
    16

    Re: Split 3 way valve

    Thank you Brian and Magoo

    Brian answered my question

    Now I know that the 3 way air conditioning valve
    has only 2 positions and the 3 way refrigeration system valve has 3 positions

    Most service manuals does not make it clear

    This is a great forum with great techs

    Moises

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Split 3 way valve

    Forgot to add that with the 2 position valve when you close the valve the Schraeder is open to the pipework side of the valve.

    This is so that you can pressure test/evacuate etc the pipework without the condensing unit.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Dec 2008
    Location
    Brazil
    Posts
    106
    Rep Power
    16

    Re: Split 3 way valve

    Thank you Brian

    But now there is a doubt left:

    When I close the valve the Schraeder is open to the pipework side, as you said.

    When I open the valve, does the pipework side gets closed or is the Schraeder valve that closes the pipework side by itself ?

    I am asking this because you told some valves do not
    have a Schraeder on them.

    Moises
    Last edited by Acrisoft; 29-05-2009 at 11:15 PM.

  7. #7
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Split 3 way valve

    No, when you open those valve all you have done is open the port between the two pipes.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

Similar Threads

  1. Replies: 2
    Last Post: 06-02-2009, 07:35 PM
  2. R22 Flooded System - Trawler
    By chiefbecker in forum System Optimization
    Replies: 18
    Last Post: 07-02-2008, 11:11 PM
  3. Service Procedures For TK Scroll
    By absolute-zero in forum Transport
    Replies: 0
    Last Post: 03-02-2008, 07:42 PM
  4. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM
  5. Replies: 5
    Last Post: 16-10-2002, 12:38 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •