    I have 3 - 30XA5006 Carrier Chillers, air cooled.
    What lemons they are.
    They are 24 months on the job and I have noting but problems.
    Replaced heaters 3-times.
    Replacing flow switches.
    repalcing condensing coils.
    Numerous oil trip outs.
    Numerous compressor over heating trip outs.
    carrier is now in the process of changing all, all condensing fan motors and blades.
    Carrier is also in the process of changing out one compressor.
    Carrier has rep[laced suction service valves.
    Carrier seems not to be able to establish oil levels or proper refrigerant charges.
    Oil sensors have been changed, so on and so on.
    Any one else having these problems??
  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,024
    Rep Power
    60
    Re: Carrier Chillers
    Quote Originally Posted by Ed Burris View Post
    Nope, not yet, it seems that you drew the lucky straw this time
    Brian - Newton Abbot, Devon, UK
    Retired March 2015
  3. #3
    Join Date
    Oct 2007
    Location
    Scotland
    Posts
    12
    Rep Power
    0
    Question Re: Carrier Chillers
    Got lots running in UK with no major probs, but they are built in Montluel, France not USA so can't comment. I reckon the 06T screw compressors are excellent though- they have been around for years in US made, can't understand why you have had such trouble.
  4. #4
    Join Date
    Jun 2008
    Location
    chuyer
    Age
    46
    Posts
    6
    Rep Power
    0
    Good morning,
    If the serial number beginnig by 12. This the code of fab of Montluel Factory.
    If it isn't, it was made in Charlotte (us)
    The biggest size in Montluel is 30XA1702 (with 4 cp 06TU)
    Or the last possibility, it's a prototype.
    I'm in France and i've never heard such problems on this unit type.
  5. #5
    Join Date
    Feb 2005
    Location
    london
    Posts
    32
    Rep Power
    0
    I have the same problem need to establish the oil level
    keeps tripping oil level switch
    no sight glass no plug to fill to
    no tech as to oil quanity
  6. #6
    Join Date
    Sep 2005
    Location
    Atlanta Georgia USA
    Age
    69
    Posts
    80
    Rep Power
    19
    We have installed and service many in harsh enviroments and have had very few problems. Have power quality?
  7. #7
    Join Date
    Jan 2008
    Location
    India
    Age
    70
    Posts
    171
    Rep Power
    17
    The series of 30XA of carrier is fit only for European market even in Muscat brand new chillers used to have some problem or other.Probably the condenser designs are not meeting the ambient conditions
Similar Threads
  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Air cooled chillers vibration isolation
    By vijay_study in forum Air Conditioning
    Last Post: 06-10-2009, 08:53 PM
  3. Carrier Water Chillers
    By Latte in forum Air Conditioning
    Last Post: 11-10-2008, 08:43 PM
  4. carrier remote
    By superswill in forum Trouble Shooting
    Last Post: 26-04-2006, 09:17 PM
  5. Chillers versus packs
    By Peter_1 in forum Technical Speculations
    Last Post: 17-01-2004, 09:48 PM
Posting Permissions
  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts