    Thumbs up Reason for suction line very hot
    As i went for a site visit i noticed that one of the split or VRV (iam not confirm ) suction line is very hot what would be the possible cause or the unit is designed like that. to the best of my knowledge i beleive that as long as the suction temperature is low we can protect the compressor from overheat and abnormal head pressure. or this may be due to indoor or outdoor capillary can anybody brief me pls
    with regards,
    S. Balaji
    TRASH101's Avatar
    TRASH101 is offline Veteran Poster I am starting to push the Mods: of RE
    Mar 2007
    394
    Re: Reason for suction line very hot
    It may have been in reverse cycle. A brief look at a system is never enough to make an informed opinion of performance.
    If it is bothering you go and have a proper look
    Jul 2007
    Australia
    1,845
    Service valve hot or hot between reversing valve and compressor?
    The external suction line running hot means it's running on heat mode.
    The real suction line is inside the unit and runs between the reversing valve and compressor, that part shouldn't be hot at any time.
    Nov 2007
    Saudi arabia
    I experienced da same trouble in a ac unite after investigating found compressor valves R leaking internally causing hi back prs & hi such line temp,u need to check both side prss.
    zosoguy's Avatar
    zosoguy Guest
    Compressor suction valve plate might got damaged so dischrge gas come out of suction valve...
    Feb 2008
    Sudan
    89
    I think that depends on the refrigerant type and the circuit design. Revise the service manual of the unit and look for the suction line temp and pressure at the heating mode.
    May 2008
    66
    802
    most vrv systems have a computer program to see what is going on. don't go on wet finger technic whit vrv or vrf. always have a trustworthy back-up at hand.