    Cold liquid line



    I have a customer with a very cold liquid line. About a month ago I recovered the refrigerant, removed the orifice from the liquid line that goes into the evaporator coil box. I cleaned it out, did not see any blockage in the orifice, made sure that I installed in the right direction, pulled vacume and recharged the system. Before I had a 50 psi suction and a 190 head. After the repairs I had a 75 suction and a 240 head.
    The customer call me back today and states the the liquid line going into the evap is very cold and sweaty. And not cool enough in the house.



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,479
    Rep Power
    45

    Re: Cold liquid line

    Despite my strong psychic powers, I can not get the wibes of what system we are looking at here.
    (Must be all the interference across the Atlantic)

    Sorry...

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Re: Cold liquid line

    With or without psychic powers, some thing is blocked between the condenser outlet and the TEV outlet.

  4. #4
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,847
    Rep Power
    21

    Re: Cold liquid line

    Quote Originally Posted by ruben feria View Post
    I have a customer with a very cold liquid line. About a month ago I recovered the refrigerant, removed the orifice from the liquid line that goes into the evaporator coil box. I cleaned it out, did not see any blockage in the orifice, made sure that I installed in the right direction, pulled vacume and recharged the system. Before I had a 50 psi suction and a 190 head. After the repairs I had a 75 suction and a 240 head.
    The customer call me back today and states the the liquid line going into the evap is very cold and sweaty. And not cool enough in the house.

    Did you check / replace the filter dryer?

    If the liquid line is cold ans sweaty then the dryer could be blocked.

    taz

    .

  5. #5
    Join Date
    Mar 2007
    Location
    Iraq
    Posts
    57
    Rep Power
    18

    Re: Cold liquid line

    Hi Ruben
    As said above,if there were no blockage in the liquid line (filter,hand valve,twisted pipe...etc).I think you have a leak .When the charged refrigerant gradually leaked ,it reached point that the suction act of the compressor would affects on the liquid line in some critical cases.I notice in three cases: in charging 35 tons water cooled system ,the liquid line became colder when the charge reach 1l4 ,but became warmer when the charging continue beyond this point.This happened three times in three 35 ton system had exactly the same design.It,outwardly, contradicts with the known PH relationship.
    Repairing the leak may solve the problem.

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Cold liquid line

    Since the OP says it isn't cool enough in the house, let's assume this is an A/C system.

    Let's also assume fixed orifice. Removing and cleaning the orifice accomplishes nothing because the orifice is downstream from the liquid line. The restriction is upstream.

    Or perhaps we are talking about the line between the orifice and the coil, which is not the liquid line and it is supposed to be cold. Perhaps you could clarify.
    Last edited by Gary; 28-09-2008 at 08:03 PM.

  7. #7
    Join Date
    Nov 2007
    Location
    Saudi arabia
    Posts
    20
    Rep Power
    0

    Re: Cold liquid line

    im sure filter is partially black

  8. #8
    Join Date
    Jan 2006
    Location
    Valrico, Florida
    Posts
    517
    Rep Power
    19

    Re: Cold liquid line

    Quote Originally Posted by The Viking View Post
    Despite my strong psychic powers, I can not get the wibes of what system we are looking at here.
    (Must be all the interference across the Atlantic)

    Sorry...
    I'm in Florida and about 3 hours from Jacksonville, and my psychic powers wont reach either it must be blocked

  9. #9
    ruben feria's Avatar
    ruben feria Guest

    Re: Cold liquid line

    Sorry about the lack of info. There is no liquid drier. it is a straight cool ac residential unit. 5 ton ac. I leak checked it originally and I leak checked it again recently. no leaks. By the time I got my superheat to about 6 degrees I ended up with a 325 head. I left it alone and I told the owner that I will have to remove the evaporator and inspect for dirt clogging up the coil. By the way it was about 90 degrees ambient outside temp with a 325 head. R 22 system. I know its way to high.

  10. #10
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Cold liquid line

    Why would you blame the evaporator? If there is a restriction, it is upstream from the cold line. Where the line turns cold is where the restriction is.

    BTW, "cold" doesn't tell us anything. Don't you have thermometers?
    Last edited by Gary; 30-09-2008 at 02:41 PM.

  11. #11
    Join Date
    Mar 2008
    Location
    upstate n.y.
    Age
    58
    Posts
    11
    Rep Power
    0

    Re: Cold liquid line

    less see i think your line temp should be and correct me if im wrong please at 90 amb r-22 system approx. 105 deg. I would say if all coils are clean u have a massive restiction or the unit is grossly overcharge (6deg super heat)

  12. #12
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34

    Re: Cold liquid line

    For a proper evaluation, we need the following information:

    Low side:

    Evap air in temp
    Evap air out temp
    Saturated suction temp (SST) converted from pressure
    Suction line temp at evap outlet

    High side:

    Cond air in temp
    Cond air out temp
    Saturated condensing temp (SCT) converted from pressure
    Liquid line temp at receiver outlet

  13. #13
    Join Date
    Sep 2008
    Location
    kent
    Age
    52
    Posts
    8
    Rep Power
    0

    Re: Cold liquid line

    . Before I had a 50 psi suction and a 190 head. After the repairs I had a 75 suction and a 240 head.


    dont listen to much to the client regards the cold liquid line you need to evaluate it yourself.check the h.p controll i.e fan speed controller or the condition of the coil ect.

  14. #14
    ticotech's Avatar
    ticotech Guest

    Re: Cold liquid line

    how u did the repair? did u pumped down the system and with the same amount of ***** the pressure changed to 75low -240 head or u added some. be honest

  15. #15
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,097
    Rep Power
    33

    Re: Cold liquid line

    fit a drier in the liquid line a 163 should do it

  16. #16
    Join Date
    Apr 2008
    Location
    LJUBLJANA
    Age
    42
    Posts
    28
    Rep Power
    0

    Re: Cold liquid line

    just check the condeser fans controler, I had lots of these kind of problems this winter

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 02:24 AM
  2. AmericAire 18,000 R410 liquid line cold HELP?
    By crunchtime2k in forum Air Conditioning
    Replies: 3
    Last Post: 20-05-2008, 01:11 AM
  3. Liquid line for multi evaporators
    By Kevin Yeo in forum Supermarket Refrigeration
    Replies: 1
    Last Post: 29-12-2005, 03:29 PM
  4. Parker levels in ammonia systems
    By Friobernal in forum Industrial
    Replies: 3
    Last Post: 04-08-2005, 03:46 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •