    Refrigerant Charging



    Hi people,

    What I would like to discuss is charging a Refrigerant system using an Amp meter, and the merits for doing it this way, additional to this I would also like some advice on making a relay box, to test the system start coil etc.

    Regards

    Sparrow


    Always easy on the eye.

  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Refrigerant Charging

    And what would you do if your condenser is designed for 27°C ambient [as most European units] and it is 32°C outside???

  3. #3
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Refrigerant Charging

    Personally, I would never charge with an AMP meter.
    .
    .
    .
    I never found one that doesn't leak, the refrigerant sprays straight out to the atmosphere. A manifold is much better.

    Jokes aside, the current drawn is not nearly accurate enough indicator of charge to rely upon for charging.
    The only thing you could say is that if an inverted system you looked after for years (and recorded the running current of) suddenly draws less current, then you should check subcooling or reclaim the gas to confirm the charge.

    Re the tester, try and search this forum for [annie] and you should find what you are looking for.
    Last edited by The Viking; 26-09-2008 at 05:31 PM.

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: Refrigerant Charging

    I never found one that doesn't leak, the refrigerant sprays straight out to the atmosphere. A manifold is much better.
    now I understand why fingers freeze when charge a system,

  5. #5
    Join Date
    Sep 2007
    Location
    west midlands
    Posts
    98
    Rep Power
    17

    Re: Refrigerant Charging

    Cheers Viking, I take it from the the scepticism that this method is not really a viable one then? I will have a search for your suggested Annie thread, today.

    Sparrow
    Always easy on the eye.

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Charging additional 410a refrigerant
    By batfink in forum Technical Discussions
    Replies: 16
    Last Post: 15-06-2009, 02:52 PM
  3. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM
  4. Newbie. Charging Refrigerant. Mitsubishi SRK 40HG.
    By smoking_muzzle in forum Air Conditioning
    Replies: 14
    Last Post: 24-07-2007, 10:33 AM
  5. Refrigerant charging weighing scale
    By malik55 in forum Tools and Calculators
    Replies: 4
    Last Post: 06-11-2006, 11:14 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •