    Change NH3 to CO2



    Dear Friends
    I am almost ready with the enginering project for a refrigeration system for an Ice Cream Plant. The design is a convetional two stage ammonia system. Two low temperature level -35C and -45C intercooler at -10C and condensing at 35C.
    So we will have load at all diferents sucction temperature.
    The owner call me up asking which will be the impact to change the project from Nh3 to CO2.
    The question look to me very interesting and I would like to chear with you all.
    Best regards
    Gwapa



  2. #2
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Change NH3 to CO2

    Some observations for your consideration....

    1) the CO2 compressors will be smaller because of the higher vapor density of CO2.

    2) A CO2 cascade system is a lot more complex than a simple two-stage NH3 system, i.e., fade-out drums or emergency power and cooling of CO2 during main power outage.

    3) I have heard some speculation that CO2 power input is not much better (if at all) than NH3 power input.

    4) Hot gas defrosting is more complicated with CO2 rather than the relatively simple system commonly used for NH3.

    Just some quick points for your review gwapa.
    If all else fails, ask for help.


  3. #3
    nh3 sweden's Avatar
    nh3 sweden Guest

    Re: Change NH3 to CO2

    Like the iceman says, during longer powerfailures it dosent take long before the safetyvalves blows. I have watched it a couple of times. Defrosting type is electric or with some kind of brine.

  4. #4
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: Change NH3 to CO2

    Hi, qwapa

    Quote Originally Posted by gwapa View Post
    Dear Friends
    I am almost ready with the enginering project for a refrigeration system for an Ice Cream Plant. The design is a convetional two stage ammonia system. Two low temperature level -35C and -45C intercooler at -10C and condensing at 35C.
    So we will have load at all diferents sucction temperature.
    The owner call me up asking which will be the impact to change the project from Nh3 to CO2.
    The question look to me very interesting and I would like to chear with you all.
    Best regards
    Gwapa
    ... stay with 2 stage ammonia .... don't make a headache to the owner and to yourself too ... ... down to -40C evaporating temp ammonia has a better COP then CO2 ...... definitely....

    .... need to use ammonia only for hardening tunnel at -45C... design plant with only 2 systems -10C intercooler and -45C with a back pressure valve on -35C connected to the -45C system...

    ...you can save more money

    .....if calculate condensing temp down to +30C ... we discussed that couple of times here on RE forums ....

    spent some more money...

    .... if using temper at -30C for cold rooms ...but less ammonia more safe... gravity feeding PHE with temper for cold rooms ....

    ... then again save some money ..... if install PHE as oil coolers oil/temper and use that heat for sanitary water or for heating/defrosting...

    .... bigger investment but you are building a factory to last many years ...

    ...of course this is only one of idea ... not the best one, but for sure enough good to think about....

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  5. #5
    t0nz06's Avatar
    t0nz06 Guest

    Re: Change NH3 to CO2

    We have a ice cream plant just like you want to design. We have -45 for the hardening tunnel & 35 for our warehouse and freezer barrels at low stage. we used frick compressors 3 pcsw 250hp at low stage at high stge we have -12ckt with 2pcs 600hp & 350hp frick compressors. we used intercooler at high side

Similar Threads

  1. How do you change oil on rotary?
    By Raadster in forum Fundamentals
    Replies: 6
    Last Post: 28-07-2008, 06:05 PM
  2. Change over 2 outdoor unit
    By bach in forum Air Conditioning
    Replies: 8
    Last Post: 08-06-2008, 06:55 PM
  3. Freus, water cooled, change gas?
    By Dennis Williams in forum Air Conditioning
    Replies: 2
    Last Post: 27-06-2007, 07:04 PM
  4. love to hear from the pros.(gas change)
    By jamcool in forum Refrigerants
    Replies: 9
    Last Post: 17-11-2006, 01:18 AM
  5. Change of Job
    By Brian_UK in forum Chit Chat & Service Stories
    Replies: 49
    Last Post: 20-09-2003, 03:26 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •