    switch from cooling only to heat pump



    hello, i have a friedrich m18cf cooling only and i want the heat pump option. the m18cf already have the reversing valve in it, i thought i could change the electronic board of the outdoor unit and inside unit with a m18yf which is already a heat pump. guess i'll have to change remote control as well. what do you guys think?
    any of you already done this before?



  2. #2
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,083
    Rep Power
    23

    Re: switch from cooling only to heat pump

    Hi
    I thought the outdoor coil was bigger on heatpumps as opposed to RACs to help collect the heat? But keep us posted and let us know how you go.

  3. #3
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: switch from cooling only to heat pump

    If the reversing valve is already there, all you need is to wire up.

    You should have a heating mode in the remote control.

  4. #4
    Join Date
    May 2008
    Location
    Malta
    Age
    68
    Posts
    67
    Rep Power
    16

    Re: switch from cooling only to heat pump

    Probably as it has the reversing valve installed I would think that's part of the manufactures standardisation and I think it it would be worth converting it to a heat pump especially if your local ambient temp doesn't go below 5 degrees.

  5. #5
    crxshed's Avatar
    crxshed Guest

    Re: switch from cooling only to heat pump

    there is no heating mode on the remote control, and even if I plug the reversing valve, the outdoor electronic board dosn't have a defrost mode in it. so it will just freeze until it die.
    thats why i'm looking for the part number for each board and try to purchase those boards for a reasonable price on the web.

  6. #6
    Join Date
    Aug 2006
    Location
    China
    Age
    54
    Posts
    52
    Rep Power
    18

    Re: switch from cooling only to heat pump

    To my knowledge, it is difficult to change only cooling to heat pump. Are you sure there is a four-way reversing valve in the unit? Is there high pressure receiver in the refrigeration system? How to control the defrost ?
    A lot of things must be taken into account.

  7. #7
    Join Date
    Oct 2008
    Location
    USA
    Age
    45
    Posts
    6
    Rep Power
    0

    Re: switch from cooling only to heat pump

    do you have a suction line accumulator?

Similar Threads

  1. Capacity control
    By sparrow in forum Training
    Replies: 44
    Last Post: 18-01-2010, 07:49 PM
  2. Replies: 5
    Last Post: 14-09-2009, 07:33 AM
  3. Heat transfer coefficient - Coolpack
    By Graham in forum Fundamentals
    Replies: 10
    Last Post: 28-05-2008, 01:08 AM
  4. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  5. Hermetic analyzer " ANNIE" how do they work
    By kengineering in forum Tools and Calculators
    Replies: 11
    Last Post: 02-03-2008, 06:10 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •