    Hi everybody:

    I have to select a compressor for a ammonia system, but i have a question what is the sucction temperature for the compressor if the evaporating temperature in the blast freezer is -42ºC. more characteristics are:
    • Inside temperaure -35ºC
    • Outside temperature +35ºC
    • freezing time 10 h
    • fish 12000 kg
    • Load aproximate 138000 Kcal/h
    please help me!!!!!!

    best regar

    Luis Sandoval.



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: selecction compressor

    It very much depends on the setup. I would tend to assume that the superheating is larger when the fresh food is loaded in the room, and suction temperature would progressively reduce as the temperature approaches the setpoint.

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: selecction compressor

    What type of evaporator are you using?

    I hope it is not a DX coil at that evaporating temperature!

    The superheat in the suction line of an ammonia system is usually minor if adequate insulation is used on the suction piping and vessels.
    If all else fails, ask for help.


  4. #4
    Join Date
    Feb 2008
    Location
    Lima - Peru
    Age
    41
    Posts
    49
    Rep Power
    0

    Re: selecction compressor

    i'm using pumpcirculated evaporator, what is the procedure for the correct selection of the compressor if i know the refrigeration load in the blast freezer.

  5. #5
    Join Date
    Aug 2008
    Location
    Lithuania
    Age
    45
    Posts
    6
    Rep Power
    0

    Re: selecction compressor

    If you have flooded system, you should calculate the pressure losts in suction line between compressor and recirculating receiver. Usually - normaly it is lower 0.6K. Then you get, that evap. temp. for compressor is -42.5ºC;

  6. #6
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: selecction compressor

    You need to determine the pressure loss in the suction line and discharge line. Then do this:

    Evaporating pressure - suction line pressure loss = Suction pressure. now convert the suction pressure to temperature.

    Now for the difficult part: you did not mention if this is a single stage compressor or a two-stage compressor, or of you are using a reciprocating compressor or a screw compressor.

    What type of compressor do you want? And, what type of systems is it? single stage or two-stage?
    If all else fails, ask for help.


  7. #7
    nh3 sweden's Avatar
    nh3 sweden Guest

    Re: selecction compressor

    It sounds like you need a two-stage plant with pumpcirkulation. Reciprocating compressor is my favourite. Depending on if you are running 100% all the time or going down to 25% for longer periods. Other wise a screw compressor will do the jobb on the low stage with reciprocating compressor on the high stage.

Similar Threads

  1. Thumping noise in the compressor
    By Husky250 in forum Air Conditioning
    Replies: 6
    Last Post: 16-05-2008, 10:48 PM
  2. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  3. SL/SB-400 Pump Down Procedures
    By absolute-zero in forum Transport
    Replies: 1
    Last Post: 29-01-2008, 09:27 PM
  4. Mitsubishi compressor lock
    By marc5180 in forum Air Conditioning
    Replies: 29
    Last Post: 08-10-2007, 05:48 PM
  5. Compressor pumping efficiency
    By shogun7 in forum Fundamentals
    Replies: 0
    Last Post: 25-02-2004, 10:50 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •