23-09-2008, 06:00 PM #1
city multi V VRVIII questions questions
1 On a 30kw Mitsubishi does the outdoor have one or two compressors. If two can it run in emergency mode?
2 Can you multi them up to have 3 x 30kw and run 2 pipes down to 6 bs boxes
3 Does Mitsubishi have the 'self weighing' of charge like Daikin VRVIII
4 Will the allow shut off valves in the system unlike Daikin who won't warranty
5 Can you turn off one indoor unit and keep the rest running
Multisync
London
23-09-2008, 10:33 PM #2
Re: city multi V VRVIII questions questions
30 kw nominal would be size 300.
Latest unit ref PURY-P300YHM-A
1/ One inverter compressor on all outdoor units up to size 400.
2/ Can double up outdoor units to make up to size 800 about 90kw nominal cooling.
No too sure about 6 BC boxes but lates product catalogue indicates 3 B/C boxes 1 master & 2 slaves.
All B/C boxes available up to 16 ports , so that at least 48 indoor unit connected to each set of outdoor units.
3/ No auto charging. Need to calculate trim charge & add in traditional method.
4/ Shut off valves not a problem as far as I know , you would need to check with Mitsubishi sales rep for confirmation on this point.
5/ Turn 240v power off to any indoor unit & all other units continue to operate normally , no problem no fault alarms.
23-09-2008, 10:41 PM #3
If we lose one compressor does the whole system go down?
Daikin assist F-Gas by this feature with self check. Will Mitsi do the same?
Will do
Cool
Thanks Thermatech you are a star!
Multisync
london
23-09-2008, 11:13 PM #4
2/ On double outdoor units emergency operation available from remote controller when fault with one of the outdoor units.
Up to 60% capacity indoor units operational in this case.
I have not tested this on the latest YHM-A models but there is afull page in the service maunal explaining emergency operation.
3/ ME cover F-gas with detailed trimcharge calculation page in commissioning logbook.
Outdoor unit also has 'refrigerant adjust mode' for service enginner to test if refrigerant charge is adequate.
24-09-2008, 08:24 PM #5
Having tried this "self charge" function, I would say that it is a sales gimmick!
In real life it doesn't work.
One system charged using this method showed clear symptoms of undercharge during commissioning, proper calculation of the additional charge required gave us a result almost twice of what the unit had sucked in by itself.
Another system needed reclaiming and an indoor unit relocated (consultant not speaking to customer?), during recommissioning the engineer recalculated the charge and found the system 5kg overcharged.
Nah, Humbug I'll say.
(Don't get me wrong, I do like the VRVIII but this function...)
24-09-2008, 08:37 PM #6
Mitsubishi City multi problems
By cooltech1 in forum Air ConditioningReplies: 9Last Post: 24-01-2010, 06:03 PM -
Need input on City Multi
By TDfromNY in forum Air ConditioningReplies: 4Last Post: 09-06-2006, 03:31 AM -
r22 city multi problem
By mr slim in forum Trouble ShootingReplies: 3Last Post: 11-01-2006, 06:27 PM -
Mitsi City Multi Compressor Death
By aeb200 in forum Air ConditioningReplies: 4Last Post: 16-11-2005, 09:10 AM -
Mitsubishi city multi
By techni in forum Air ConditioningReplies: 2Last Post: 04-07-2005, 05:37 PM