    city multi V VRVIII questions questions



    1 On a 30kw Mitsubishi does the outdoor have one or two compressors. If two can it run in emergency mode?

    2 Can you multi them up to have 3 x 30kw and run 2 pipes down to 6 bs boxes

    3 Does Mitsubishi have the 'self weighing' of charge like Daikin VRVIII

    4 Will the allow shut off valves in the system unlike Daikin who won't warranty

    5 Can you turn off one indoor unit and keep the rest running

    Thanks



    Multisync
    London



  2. #2
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: city multi V VRVIII questions questions

    30 kw nominal would be size 300.
    Latest unit ref PURY-P300YHM-A
    1/ One inverter compressor on all outdoor units up to size 400.
    2/ Can double up outdoor units to make up to size 800 about 90kw nominal cooling.
    No too sure about 6 BC boxes but lates product catalogue indicates 3 B/C boxes 1 master & 2 slaves.
    All B/C boxes available up to 16 ports , so that at least 48 indoor unit connected to each set of outdoor units.
    3/ No auto charging. Need to calculate trim charge & add in traditional method.
    4/ Shut off valves not a problem as far as I know , you would need to check with Mitsubishi sales rep for confirmation on this point.
    5/ Turn 240v power off to any indoor unit & all other units continue to operate normally , no problem no fault alarms.

  3. #3
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: city multi V VRVIII questions questions

    2/ Can double up outdoor units to make up to size 800 about 90kw nominal cooling.

    If we lose one compressor does the whole system go down?

    3/ No auto charging. Need to calculate trim charge & add in traditional method.

    Daikin assist F-Gas by this feature with self check. Will Mitsi do the same?

    4/ Shut off valves not a problem as far as I know , you would need to check with Mitsubishi sales rep for confirmation on this point.

    Will do

    5/ Turn 240v power off to any indoor unit & all other units continue to operate normally , no problem no fault alarms.

    Cool

    Thanks Thermatech you are a star!

    Multisync
    london

  4. #4
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: city multi V VRVIII questions questions

    2/ On double outdoor units emergency operation available from remote controller when fault with one of the outdoor units.
    Up to 60% capacity indoor units operational in this case.
    I have not tested this on the latest YHM-A models but there is afull page in the service maunal explaining emergency operation.
    3/ ME cover F-gas with detailed trimcharge calculation page in commissioning logbook.
    Outdoor unit also has 'refrigerant adjust mode' for service enginner to test if refrigerant charge is adequate.

  5. #5
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: city multi V VRVIII questions questions

    Quote Originally Posted by multisync View Post
    [B]Daikin assist F-Gas by this feature with self check.]


    Having tried this "self charge" function, I would say that it is a sales gimmick!

    In real life it doesn't work.
    One system charged using this method showed clear symptoms of undercharge during commissioning, proper calculation of the additional charge required gave us a result almost twice of what the unit had sucked in by itself.

    Another system needed reclaiming and an indoor unit relocated (consultant not speaking to customer?), during recommissioning the engineer recalculated the charge and found the system 5kg overcharged.

    Nah, Humbug I'll say.

    (Don't get me wrong, I do like the VRVIII but this function...)

  6. #6
    Join Date
    Jul 2008
    Location
    London
    Posts
    848
    Rep Power
    17

    Re: city multi V VRVIII questions questions

    Quote Originally Posted by The Viking View Post


    Having tried this "self charge" function, I would say that it is a sales gimmick!

    In real life it doesn't work.
    One system charged using this method showed clear symptoms of undercharge during commissioning, proper calculation of the additional charge required gave us a result almost twice of what the unit had sucked in by itself.

    Another system needed reclaiming and an indoor unit relocated (consultant not speaking to customer?), during recommissioning the engineer recalculated the charge and found the system 5kg overcharged.

    Nah, Humbug I'll say.

    (Don't get me wrong, I do like the VRVIII but this function...)
    I agree with you there and would want to be doublely sure the right amount was added. But wonder if the self check works only if you let the system self charge rather than self charge + - what it should really have.

    Multisync
    london

Similar Threads

  1. Mitsubishi City multi problems
    By cooltech1 in forum Air Conditioning
    Replies: 9
    Last Post: 24-01-2010, 06:03 PM
  2. Need input on City Multi
    By TDfromNY in forum Air Conditioning
    Replies: 4
    Last Post: 09-06-2006, 03:31 AM
  3. r22 city multi problem
    By mr slim in forum Trouble Shooting
    Replies: 3
    Last Post: 11-01-2006, 06:27 PM
  4. Mitsi City Multi Compressor Death
    By aeb200 in forum Air Conditioning
    Replies: 4
    Last Post: 16-11-2005, 09:10 AM
  5. Mitsubishi city multi
    By techni in forum Air Conditioning
    Replies: 2
    Last Post: 04-07-2005, 05:37 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •