    Liebert hiross



    Hi, i sevice a couple of these units and i am looking for some manuals if not tips, all units only have the standard lcd and was wondering what it is capable of? What does t1 t2 etc etc ......mean?

    Rgrs phil



  2. #2
    Join Date
    Aug 2008
    Location
    indonesia
    Posts
    8
    Rep Power
    0

    Re: Liebert hiross

    ok, t1 : return temperature, t2 supply temperature ( no recomend ), h1 :The humidity of the air entering the air conditioning
    unit, ACT :This Value shows the actual Temp / Hum set point. for information detail please email yana_jastek@yahoo.co.id, YM :yantahyana

  3. #3
    Join Date
    Mar 2007
    Location
    uk
    Age
    51
    Posts
    120
    Rep Power
    18

    Re: Liebert hiross

    Hi phil

    Been so long since i worked on these i dont remember much, one thing i do remember is the master password to unlock all functions on the controller was 501, maybe that helps you navigate in.

  4. #4
    Join Date
    Aug 2008
    Location
    indonesia
    Posts
    8
    Rep Power
    0

    Re: Liebert hiross

    for setting temperature use pasword 501, but for another setting can be use password 221, and for calibration use password 476

  5. #5
    dlisjak's Avatar
    dlisjak Guest

    Re: Liebert hiross

    Hi my friend, can you supply me with some ICOM or service manual for this controler and machine! Where could I find it if you don't have it?

  6. #6
    dlisjak's Avatar
    dlisjak Guest

    Re: Liebert hiross

    Hi, I have problem with my Hiross MATRIX machine. Problems are with alarm code 082-share room sensor failure! Which sensor is that? I have stand alone unit! t1,t2,t3 ok!please advice me what to do!

  7. #7
    Join Date
    Nov 2008
    Location
    romania
    Age
    47
    Posts
    45
    Rep Power
    0

    Re: Liebert hiross

    Another code is 149 446 445

  8. #8
    zcoco's Avatar
    zcoco Guest

    Re: Liebert hiross

    How can I disable the alarm sensor failed

  9. #9
    Join Date
    Dec 2003
    Location
    Rome Italy
    Age
    56
    Posts
    29
    Rep Power
    0

    Re: Liebert hiross

    passwords are 149-221-501 and 674 for calibrating all the probes.When on all Liebert Hiross you get an alarm indicating a faulty probe the first thing to do is check the machine has the correct programming,for example if you get a RSF (room sensor failure) on a direct expantion unit most likely there's a humidity setpoint set above 0 while the machine hasn't got a humidity probe!Same thing for water chillers,if you get a probe failure check if there's a setpoint (external temp or chilled water evap exit) set at a value (other than "NO") while the probe isn't installed.
    Every unit has its own Microface-Hiromatic-Icom-powerface manual that's because on any of these boards you can put so many different EPROMS.A wrong parametre sometimes gives you a totally different alarm and you can get crazy!

  10. #10
    Join Date
    Dec 2003
    Location
    Rome Italy
    Age
    56
    Posts
    29
    Rep Power
    0

    Re: Liebert hiross

    to disable alarms just press the arrow up and wait til you get a code in the display (A1-A2A3 etc) then press again arrow up and enter button almost simultaniously.

  11. #11
    Join Date
    Feb 2008
    Location
    Wellingborough
    Age
    56
    Posts
    35
    Rep Power
    0

    Re: Liebert hiross

    Quote Originally Posted by Leo1967 View Post
    to disable alarms just press the arrow up and wait til you get a code in the display (A1-A2A3 etc) then press again arrow up and enter button almost simultaniously.
    This doesn't disable alarms, it resets them if the fault condition is noi longer present.

    In regard to share room sensor failure, make sure that the controller is not set to a teamwork mode as if the units are standalone & they are trying to reference a sensor on another machine, this will cause the fault.

Similar Threads

  1. Hiross PIN Code
    By Whisty in forum Technical Discussions
    Replies: 18
    Last Post: 17-06-2011, 02:24 PM
  2. Liebert A/c unit with low suction pressure
    By dbanker in forum Trouble Shooting
    Replies: 9
    Last Post: 29-07-2008, 09:23 PM
  3. Hiross Hirange and Stulz literature
    By garyjh24 in forum Air Conditioning
    Replies: 2
    Last Post: 08-06-2008, 07:06 PM
  4. liebert system 3
    By JPM in forum Air Conditioning
    Replies: 8
    Last Post: 20-04-2008, 06:14 AM
  5. liebert hiross
    By cruzeiros in forum Air Conditioning
    Replies: 3
    Last Post: 20-04-2008, 05:49 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •