    Btec heating help



    Ground floor

    Living room = 4m x 3.8m x 3m
    Kitchen = 2.9m x2.1m x 3m
    Dining room = 2.9m x 2.8m x 3m
    Toilet = 1.5m x 1.5m x 3m
    Hall = 3.5m x 1.3m x 3m

    First floor

    Bedroom1 = 3.1m x 2.8m x 2.9m
    Bedroom2 = 3.1m x 2.5m x 2.9m
    Bedroom3 = 2.5m x 2.4m x 2.9m
    Bathroom = 2m x 2.1m x 2.9m
    Upperhall = 2m x 1.9m x 2.9m

    Can anyone help work out the heat load for this building I have been trying to do this but i keep coming ouy with different figures each time.

    I calculated the whole area of the house assuming the outside temperature was 8c and the indoor 21c. So I did

    Area = 22458 x (T1 - T2) 13 x U value of walls = 0.35, which gave me 102183.9. Around 29 kw. Is this correct



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Btec heating help

    Dear W Miller

    It says in your profile that you are an engineer? Surely, this heat gain calc should be a doddle to you.

    However, to do a full heat gain calc, you have to look at each external wall individually, and take into consideration, glazing area, type of glazing, shading, orientation, sun azimuth for the time of year you are calculating, fabric construction details, insulation type, reflectance, building material colour, and then roof type, colour, construction, shading etc.

    On top of all that, you need to look at degree days.

    Simple init?

    No wonder most 'engineers' just guess.

    Good luck with the Btec.

    Edit.

    Just noticed that you are asking for heatloss calcs. Sorry chap, this is a Refrigeration forum
    Last edited by frank; 22-09-2008 at 08:30 PM.

  3. #3
    Join Date
    Apr 2008
    Location
    West Yorkshire
    Age
    42
    Posts
    62
    Rep Power
    17

    Re: Btec heating help

    I think I worked it out to be 8.5 kg. I wanted to add to my nvq level 2 in refrigeration. So i started doing an btec level 3 advanced dimploma in refrigeration, heating and air conditioning.

  4. #4
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    18

    Re: Btec heating help

    Whether you're calculating the load for heat loss (heating load) or heat gain (cooling loads) you should also allow for ventilation, be it natural or mechanical.

    You're study notes and reference books should give you further indication of the whole requirement, and complexity, for you to complete the exercise.

    study hard and enjoy!
    Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]

  5. #5
    Join Date
    Apr 2008
    Location
    West Yorkshire
    Age
    42
    Posts
    62
    Rep Power
    17

    Re: Btec heating help

    The actual answer to this is around 8kw of the top of my head. I finally worked out how to do the sums correctly. This course has taught me alot and is a good addition to my nvq2. I'm glad I done it.

Similar Threads

  1. Fuji AOY45 cassette Problem (no heating)
    By R B M 72 in forum Air Conditioning
    Replies: 8
    Last Post: 09-03-2011, 08:30 PM
  2. fresh air heating in cold area
    By Lc_shi in forum Air Conditioning
    Replies: 7
    Last Post: 14-05-2009, 01:37 AM
  3. Replies: 0
    Last Post: 10-05-2008, 04:16 PM
  4. Heating problem
    By meadows in forum Trouble Shooting
    Replies: 7
    Last Post: 01-07-2006, 11:03 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •