    imi expansion valve problem



    Hi there all, i was given a job to replace a small copeland scroll on an imi mcu50 condenser, after replacing and carrying out relevant pressure tests i started to gas the system but noticed that the pressures were no where near what i would be expecting on r22, after checking the system i discovered that there was no expansion valve on the evaporator and after investigating i found no expnasion valve anywhere on the system.

    this system is ten years old and looks like it has never had one fitted, also the fan speed controller and sensers had been removed. After speaking to imi there told me that an expansion valve should be fitted just after the service port on the condenser, is it just me or is this a strange place to locate the valve. please let me know your views on this.

    from a very puzzled brummie

    sorry its on an above ground cellar system



  2. #2
    Join Date
    Apr 2002
    Location
    scotland
    Posts
    114
    Rep Power
    23

    Re: imi expansion valve problem

    well, its strange right enough but they do work well, its a mechanical in line fitting that has a strainer and an injector fitted to it, unless you know what you are looking for it can be pretty hard to spot.

    I have also came across this fault, I fitted a new compressor to a system that was 'inefficient', the pressures were also not quite right - the customer had 6 compressors fitted to it over the last ten years and all with the same fault.

    there was NO expansion valve fitted to it . . . .

  3. #3
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: imi expansion valve problem

    Obviously, you have replaced compressor but cause of dead of old one is remained.
    System has to have some expansion device, that doesn't necessary need to be TEV. It could be also capillary tube or orifice.

  4. #4
    Join Date
    May 2006
    Location
    Isle of Wight, Uk
    Age
    47
    Posts
    424
    Rep Power
    20

    Re: imi expansion valve problem

    It's not an expansion valve, it has a fixed orifice which is within the extra bit of brass directly after the liquid shut off valve. Does the same as a cap tube, which on your system gives you an expansion line, just like a standard split air con.
    Did you make sure the coils were clean? The evaps on those old things get extremely dirty inside, which would give lower suction pressure and freezing up.

    Andy

  5. #5
    Join Date
    Sep 2008
    Location
    england
    Age
    50
    Posts
    5
    Rep Power
    0

    Re: imi expansion valve problem

    IMI!!!!! 10 yr old you say,box of matches and sum 4star.ha

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: imi expansion valve problem

    Quote Originally Posted by fridgemandan View Post
    Hi there all, i was given a job to replace a small copeland scroll on an imi mcu50 condenser, after replacing and carrying out relevant pressure tests i started to gas the system but noticed that the pressures were no where near what i would be expecting on r22...
    That's because refrigeration is not about pressures... it's about temperatures. The reason we use gauges is to find out the temperatures of the refrigerant.

    You say the pressures are not what you expected, but you failed to tell us what those pressures are. If you had told us the pressures, we could get out our P/T charts and find out what the temperatures are... because that's what is relevant here.

    You seem to have already decided that the expansion device is at fault, which is in fact the least likely fault. On what criteria do you base your decision?
    Last edited by Gary; 21-09-2008 at 03:16 PM.

  7. #7
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: imi expansion valve problem

    Also if the fan speed controller is faulty it needs replacing as without it you will have a low head pressure and hence a low suction pressure.

    Jon

  8. #8
    Lincoln's Avatar
    Lincoln Guest

    Re: imi expansion valve problem

    I have found that with this type of unit charge until you achieve 10 deg across evap approx and a reasonable suction superheat the compressor will be fine.

  9. #9
    Join Date
    Apr 2007
    Location
    The Netherlands
    Age
    67
    Posts
    20
    Rep Power
    0

    Re: imi expansion valve problem

    thats correct, it's a so called accurator expansion device, located in de liquid line just outside the unit (and with a strainer in it !!), Carrier used the same in the pasted, mostly on heat pumps because of the bi flow possibility

  10. #10
    Join Date
    Jul 2008
    Location
    birmingham
    Age
    39
    Posts
    23
    Rep Power
    0

    Re: imi expansion valve problem

    i have based this on speaking to imi technical who have given me the information on how the system whould have been installed. fan speed controllers were fitted as standard but apparently there has been a long running problem with installers not fitted components to the system as they have specified. All coils were spotless, as i had already cleaned and blown through, the part will arrive on friday so i will be sure to let you all know how it goes

  11. #11
    Join Date
    Dec 2001
    Location
    UK
    Posts
    137
    Rep Power
    23

    Re: imi expansion valve problem

    The most likely 'Fault' here is the strainer on the inlet to the expansion device if the problem is high head and low suction.
    If the problem is high suction and more or less equal head then either the compressor is going backwards (3phase scroll) and noisy or the bullet in the expansion device is not sealing over.
    Head pressure control is standard on MCU+ models but not on MCU although always recommended for UK use.
    Without knowing more on pressures/temperatures can't help you much more
    Brit

  12. #12
    Join Date
    May 2007
    Location
    Northants
    Posts
    290
    Rep Power
    17

    Re: imi expansion valve problem

    Hi

    i have had the same problem as you with low suction pressures, i have reclaimed and recharged to factory spec, but still had a low suction pressure and high superheat. the syptoms found indicate a undersized orifice or blocked liquid line, i have checked filters, strainers, pipe sizes, i checked the orifice size with IMI and it was correct. i thought the problem may be due to undersized equipment. Am i correct in thinking that under high evaporator loads the amount of refrigerant in the system and the quantity that can get through the orifice is not enough, or the quantity of refrigerant in the system (bear in mind the refrigerant charge is critical, there is no reciever for excess liquid)is not enough for the high demand. The system i have problems with works fine until summer then starts freezing the first couple of runs.
    I have spent hours on this system and can only assume that it's due to starvation of refrigerant in the evaporator, these system do not accomodate varying loads well due to the fixed orifice and critical refrigerant charge. Under normal operating loads the evaporator is fully utilized but under high loads the evaporator i believe is starved, which would be ok for short periods, as eventually the room temp would fall and the system would rebalance.
    Be careful if you overcharge/ charge the system under high load conditions, the system it will work fine during high loads but will flood liquid into the evap during an off cycle, when the comp restarts the excess liquid will enter the compressor, causing damage or failure, the same will happen under low load conditions, the superheat will fall and flood back to the compressor.

    Hope that makes sense

    CB

  13. #13
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: imi expansion valve problem

    Hi Guys,
    just a sugestion.

    If there was hot gas in the liquid line the amount of liquid passing into the evaporator would be reduced and a low suction pressure would exist.

    As the unit only causes problems in the summer, it could quite possibly be a condenser issue.

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

  14. #14
    Join Date
    May 2007
    Location
    Northants
    Posts
    290
    Rep Power
    17

    Re: imi expansion valve problem

    Hi Andy

    That may be correct, but the system i worked on had good subcooling.

    CB

  15. #15
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: imi expansion valve problem

    Quote Originally Posted by chillyblue View Post
    Hi Andy

    That may be correct, but the system i worked on had good subcooling.

    CB
    How much subcooling is "good subcooling"? How much superheat is "high superheat"? How much suction pressure is "low suction pressure"?

    Give us data, not conclusions. These are the same conclusions by which you have not figured out the problem.

    Give us temperatures/pressures and let us draw our own conclusions.

  16. #16
    Join Date
    Mar 2007
    Location
    uk
    Age
    51
    Posts
    120
    Rep Power
    18

    Re: imi expansion valve problem

    Hi all

    Worked on a lot of these in my time, as stated earlier the charge on these is critical and if right it will run for ever, if you weighed it in I bet it aint right. One thing about these units is that they can run fairly short of gas quite happy during low load conditions as the fan speed controller slows down the condenser motor and holds the back pressure up, I am assuming your issue with abnormal pressure is high discharge and low suction which makes you suggest the orifice at fault.

    I reccomend the following, when charging these systems.

    Note two adjustments on the FSC, temp & min speed. the meathod of head pressure control is by measuring the temp of the liquid line as it leaves the condenser coil via a sensor tyraped to it.

    1. turn the fan speed controller temperature setting so that the fan stalls.
    2. turn the min speed to maximum.
    3. Charge with gas using superheat measurements, you know your getting close when the frost on the orifice & expansion starts to go and sweats instead.
    4. throttle back min speed setting on fan speed controller to just before 275psi or the fan stalling, which ever comes sooner.
    5. turn up the temperature set point on FSC until the head pressure settles at 250psi.

    The unit should now work fine what ever load its under (in its kw range of course).

    FYI. the min fan speed is there to keep the fan running in the event of sensor error, it has to be set at a higher than normal running pressure or the unit would not control & over condence when running on cold days.
    If the FSC fails then pull the crimp wire of terminal No2 and put it straight to Neutral, this wires out the FSC and the fan will run on its own.

    If the condenser fan is not spinning fast enough to condense properly change the fans black and red wires over in the terminal block, this will turn the fan into high fan speed, not many people knowe these fans have two speeds.

    Thats all with it, good luck with

  17. #17
    Join Date
    Sep 2008
    Location
    kent
    Age
    52
    Posts
    8
    Rep Power
    0

    Re: imi expansion valve problem

    hi there just a suggestion that the wire filter located on the liquid valve could be blocked with carbon due to the compressor changes. you can remove and clean these.

  18. #18
    Join Date
    Mar 2007
    Location
    uk
    Age
    51
    Posts
    120
    Rep Power
    18

    Re: imi expansion valve problem

    Just realised, you said it has had the fan speeder removed, doh...!! must read better.

    It needs one to work effectivley, the head pressure has to be regulated around 250 psi.

  19. #19
    Join Date
    May 2007
    Location
    Northants
    Posts
    290
    Rep Power
    17

    Re: imi expansion valve problem

    Quote Originally Posted by coolments View Post
    Just realised, you said it has had the fan speeder removed, doh...!! must read better.

    It needs one to work effectivley, the head pressure has to be regulated around 250 psi.

    I'm not doubting you but thats seems high! why do they need to run at that high a discharge pressure?? most system would run fine with a much lower discharge pressure.

    How much subcooling is "good subcooling"? How much superheat is "high superheat"? How much suction pressure is "low suction pressure"?

    Give us data, not conclusions. These are the same conclusions by which you have not figured out the problem.

    Give us temperatures/pressures and let us draw our own conclusions

    Yes you are correct Gary, but i can't give you any data cause it was a while back and had to make my diagnosis when i was there.

  20. #20
    Join Date
    Sep 2008
    Location
    kent
    Age
    52
    Posts
    8
    Rep Power
    0

    Re: imi expansion valve problem

    How much subcooling is "good subcooling"? How much superheat is "high superheat"? How much suction pressure is "low suction pressure"?

    Give us data, not conclusions. These are the same conclusions by which you have not figured out the problem.

    Give us temperatures/pressures and let us draw our own conclusions



    you could always speak to imi for this infomation

  21. #21
    Join Date
    Mar 2007
    Location
    uk
    Age
    51
    Posts
    120
    Rep Power
    18

    Re: imi expansion valve problem

    Hi chillie

    I not going to the whole subcooling superheat conversation there are plenty of threads for that, just trying to help by giving advice based on experience, the person posting the problem needs to produce data.

    by the way way, there are no set head pressure pressures as every thing is relative to the aplication and that moment in time ie ambient conditions, 250psi is a giude line and good all round head pressure to be at for AC in uk conditions if you have to stick your neck out and state one, check your gauges and note the condensing temp of R22 & R407c at this pressure

  22. #22
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: imi expansion valve problem

    Quote Originally Posted by mwatts View Post
    you could always speak to imi for this infomation
    I don't care what imi has to say.

    I want to know what the pressure/temperature measurements are.

    Why do people say things like "the pressure is low", instead of saying "the pressure is ___psi"?
    Last edited by Gary; 08-10-2008 at 03:09 AM.

  23. #23
    Join Date
    Sep 2008
    Location
    kent
    Age
    52
    Posts
    8
    Rep Power
    0

    Re: imi expansion valve problem

    if you can gauge around a 10oc diff on air on and air off on the indoor and out door coil that will give you a clue or speak to imi and get thier sub cooling temps
    if your air on is at 21oc then you could look for 11oc off then you can determine from that

  24. #24
    Join Date
    Dec 2001
    Location
    UK
    Posts
    137
    Rep Power
    23

    Re: imi expansion valve problem

    imi units are designed for a suction pressure of around 60psig, a head pressure of 250 to 280psi with the headpressure control to maintain those conditions throughout ther year.
    Using a higher head pressure allows a smaller condenser coil or lower fan speed.
    If the system has been installed to imi spec the suction line pressure drop is going to be around 2°C
    Usually the cellar coolers will be evaporating between -2 and 4°c
    Brit

Similar Threads

  1. Expansion Valve Selection
    By raviperumal in forum Technical Speculations
    Replies: 12
    Last Post: 17-02-2010, 09:58 AM
  2. Need Divine Intervention - plugged drier or expansion valve?
    By archibaldtuttle in forum Trouble Shooting
    Replies: 4
    Last Post: 08-06-2008, 06:52 PM
  3. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM
  4. expansion valve aint cold
    By justinworne in forum Trouble Shooting
    Replies: 6
    Last Post: 26-07-2006, 10:52 PM
  5. pressure drop between expansion valve and distributor
    By aygul in forum Technical Speculations
    Replies: 10
    Last Post: 22-01-2004, 09:47 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •