Pull thru vs blow over
I am curious. Having worked a lot with exhaust fans, I believe that blowing air over an evaporator would result in more air flow than pulling air through the evap. Do you all agree?
-
19-09-2008, 01:19 PM #2
Re: Pull thru vs blow over
No, the more air is pulled or pushed if the fan is standing away from the coil, so to have a lower speed through the fins.
A lower speed not just have a lower pressure drop, but also a better exchange because of longer crossing times.
It doesn't matter whether you pull or push. Just put the fan inches away.
-
19-09-2008, 01:42 PM #3
Re: Pull thru vs blow over
Originally Posted by bcampbell
If the fan is in a draw-thru or blow-thru configuration the volume flow should be the same.
On coils, the fans are normally draw-thru because the air flow velocity is more uniform over the entire coil face. This is not the fact with blow-thru coils.If all else fails, ask for help.
-
19-09-2008, 01:46 PM #4
Re: Pull thru vs blow over
A housed blow through fan will have a 'non-ducted loss' as the air leaves the blower outlet.
In cooling however, in particular when the load is extremely sensible in nature, the blow through fan will result in less total airflow and total cooling needed because the coil deals with the fan and motor heat directly.
A draw through fan under these situations has to move a higher volume of air, and has to over cool this volume of air to compensate for the downstream fan/motor reheat.Last edited by Abby Normal; 19-09-2008 at 01:59 PM.
Take the V out of HVAC and you are left with a HAC job
-
22-09-2008, 07:04 AM #5
Re: Pull thru vs blow over
Though this has no direct link to the msg there is one more difference. in Blow through system the Fan motor is exposed to higher temp compared to Suck Through for the obvious reasons. That does matter a lot in an textile air washer system design. But ofcourse as US ICeman has pointed out the Such thru shall have more uniform flow across the coil.
Similar Threads
-
Temperature pull down in large cold stores( -25 deg c)
By smpsmp45 in forum NH3Replies: 10Last Post: 20-10-2007, 02:56 AM -
freezer cold room pull down slow
By nick clark in forum CommercialReplies: 10Last Post: 22-07-2007, 06:07 PM -
procedure for Pull down calculation in compressor pakages
By f4760249 in forum IndustrialReplies: 6Last Post: 18-03-2007, 02:35 AM -
Pull down consideration in -35/+40 double stage ompression system
By desai_bangalore in forum New to REReplies: 5Last Post: 27-11-2006, 08:05 PM