    Pull thru vs blow over



    I am curious. Having worked a lot with exhaust fans, I believe that blowing air over an evaporator would result in more air flow than pulling air through the evap. Do you all agree?



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Pull thru vs blow over

    No, the more air is pulled or pushed if the fan is standing away from the coil, so to have a lower speed through the fins.
    A lower speed not just have a lower pressure drop, but also a better exchange because of longer crossing times.

    It doesn't matter whether you pull or push. Just put the fan inches away.

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Pull thru vs blow over

    Quote Originally Posted by bcampbell
    Do you all agree?
    No. Fans react to differences in static pressure. The only way to increase their capacity without changing the speed of rotation is to reduce the static pressure the fans operate at.

    If the fan is in a draw-thru or blow-thru configuration the volume flow should be the same.

    On coils, the fans are normally draw-thru because the air flow velocity is more uniform over the entire coil face. This is not the fact with blow-thru coils.
    If all else fails, ask for help.


  4. #4
    Join Date
    Jun 2006
    Location
    British West Indies
    Posts
    543
    Rep Power
    18

    Re: Pull thru vs blow over

    A housed blow through fan will have a 'non-ducted loss' as the air leaves the blower outlet.

    In cooling however, in particular when the load is extremely sensible in nature, the blow through fan will result in less total airflow and total cooling needed because the coil deals with the fan and motor heat directly.

    A draw through fan under these situations has to move a higher volume of air, and has to over cool this volume of air to compensate for the downstream fan/motor reheat.
    Last edited by Abby Normal; 19-09-2008 at 01:59 PM.
    Take the V out of HVAC and you are left with a HAC job

  5. #5
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: Pull thru vs blow over

    Though this has no direct link to the msg there is one more difference. in Blow through system the Fan motor is exposed to higher temp compared to Suck Through for the obvious reasons. That does matter a lot in an textile air washer system design. But ofcourse as US ICeman has pointed out the Such thru shall have more uniform flow across the coil.

Similar Threads

  1. Replies: 10
    Last Post: 20-10-2007, 02:56 AM
  2. freezer cold room pull down slow
    By nick clark in forum Commercial
    Replies: 10
    Last Post: 22-07-2007, 06:07 PM
  3. Replies: 6
    Last Post: 18-03-2007, 02:35 AM
  4. Replies: 5
    Last Post: 27-11-2006, 08:05 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •