Results 1 to 12 of 12
  1. #1
    Join Date
    Sep 2008
    Location
    England
    Posts
    18
    Rep Power
    0

    Measurement of pipe lengths



    Hi,

    I am new here and very new to refrigeration. I have a simple question for you guys which I am failing to find a definitive answer to.

    What measurement should I add onto the total length of pipe for swept bends and 90 degree pulled bends please? I have asked a few refrigeration friends and they don't really equate the bends in as they argue it is the same internal diameter as it was, but surely frictional resistance must have relevance. Need a practical answer to this please

    Cheers,

    B



  2. #2
    Join Date
    Sep 2008
    Location
    England
    Posts
    18
    Rep Power
    0

    Re: Measurement of pipe lengths

    Just trying to work out the overall length including bends so we don't exceed the units pre-charged specification of 10m, otherwise I will get a refrigeration guy to weight in some more refrigerant.

  3. #3
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Measurement of pipe lengths

    I don't count bends when working out the aditional charge for ac systems, i just measure the pipe lenght, be it straight or wiggly.

    Jon

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Measurement of pipe lengths

    Quote Originally Posted by batfink View Post
    Hi,

    I am new here and very new to refrigeration. I have a simple question for you guys which I am failing to find a definitive answer to.

    What measurement should I add onto the total length of pipe for swept bends and 90 degree pulled bends please? I have asked a few refrigeration friends and they don't really equate the bends in as they argue it is the same internal diameter as it was, but surely frictional resistance must have relevance. Need a practical answer to this please

    Cheers,

    B
    http://www.copper.org/applications/p...th_table7.html

  5. #5
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Measurement of pipe lengths

    Assuming split or VRF air conditioning application.

    Every bend & fitting installed in the interconnecting refrigeration pipework will result in an extra pressure drop.
    This will result in performance reduction & higher amps / energy required to overcome the extra pressure drop.
    For split system air conditioning applications lots of manufacturers rate the system performance with only a short interconnecting pipe like 5 meters. Then most manufacturers provide some some sort of correction factor for longer length interconnecting pipe. This allows for the extra pressure drop for the extended pipe length.
    So the rated cooling capacity for the unit in the technical data is for 5m interconnecting & if you have 50m interconnecting pipe you can apply the coorection factor & work out what the actual reduced cooling capacity will be.
    But that all assumes straight pipe lenghts.
    If you have bends then a further correction can be calculated.
    Fare to say that some split system munufactures dont publish any correction factors for bends,,,, but if you step up to VRV / VRF then due to the much longer pipe lengths most VRF manufacturers do include a correction factor for bends.
    Now you start looking at actual pipe length & equivalent pipe length.
    Daikin quote for 3/4 inch tube
    0.35m extra length for swept bend.
    2.4m extra length for oil trap double U bend.
    0.5M extra length for refnet joint.
    You then calculate the equivalent extra length of pipe based on the fittings you have installed on the interconnecting pipe added to the total length of pipe from the outdoor unit to farthest indoor unit & you end up with the equivalent interconnecting pipe length.

    The actual measured interconnecting pipe length is needed for calculating the refrigerant trim charge.

    The equivalent pipe lenght is needed to ensure the interconnecting pipe length does not exceed manufacturers recomendations & to calculate the reduced performance of the system.

    For example
    Installing contractor complains to the manufacturer that the split system he has just installed has poor performance & frosted suction pipe in cooling mode but is within the maximum 50M interconnecting pipe lenght published by the manufacturer for this unit.
    The manufacturer sends an engineer to site to investigate & he finds the the pipework is 49M length but with 25 bends. Equivalent pipe legth is 25 by 0.35 = 8.75M + 49 = total equivalent length = 57.75M.
    As the correction for eqivalent pipe length makes a reduction of aprox 15% to 20% cooling capacity the system is actually undersized for the application.
    Result
    No warrantee
    Suggest relocate units to reduce pipe length.

    Get the idea.

    Very long pipe length with inverter systems can be a problem as the outdoor unit looks at the suction temp / pressure & if its get below target the outdoor unit ramps down the compressor. But because of the pressure drop the actual evaporating temp at the indoor unit is much higher & cooling performance is reduced.

  6. #6
    Join Date
    Sep 2008
    Location
    England
    Posts
    18
    Rep Power
    0

    Re: Measurement of pipe lengths

    Many thanks my friend for taking the time to respond This makes perfect sense to me and as I thought, they have to be factored in.

    It would be great to get some figures for 1/4" and 5/8" swept and 90 degree bends, this is all we use on split systems. I have spoke to diakin about how much I should allow for bends etc and didn't really get an answer

    Thank you for your help and appreciate your time

    Take care,

    B

    Quote Originally Posted by Thermatech View Post
    Assuming split or VRF air conditioning application.

    Every bend & fitting installed in the interconnecting refrigeration pipework will result in an extra pressure drop.
    This will result in performance reduction & higher amps / energy required to overcome the extra pressure drop.
    For split system air conditioning applications lots of manufacturers rate the system performance with only a short interconnecting pipe like 5 meters. Then most manufacturers provide some some sort of correction factor for longer length interconnecting pipe. This allows for the extra pressure drop for the extended pipe length.
    So the rated cooling capacity for the unit in the technical data is for 5m interconnecting & if you have 50m interconnecting pipe you can apply the coorection factor & work out what the actual reduced cooling capacity will be.
    But that all assumes straight pipe lenghts.
    If you have bends then a further correction can be calculated.
    Fare to say that some split system munufactures dont publish any correction factors for bends,,,, but if you step up to VRV / VRF then due to the much longer pipe lengths most VRF manufacturers do include a correction factor for bends.
    Now you start looking at actual pipe length & equivalent pipe length.
    Daikin quote for 3/4 inch tube
    0.35m extra length for swept bend.
    2.4m extra length for oil trap double U bend.
    0.5M extra length for refnet joint.
    You then calculate the equivalent extra length of pipe based on the fittings you have installed on the interconnecting pipe added to the total length of pipe from the outdoor unit to farthest indoor unit & you end up with the equivalent interconnecting pipe length.

    The actual measured interconnecting pipe length is needed for calculating the refrigerant trim charge.

    The equivalent pipe lenght is needed to ensure the interconnecting pipe length does not exceed manufacturers recomendations & to calculate the reduced performance of the system.

    For example
    Installing contractor complains to the manufacturer that the split system he has just installed has poor performance & frosted suction pipe in cooling mode but is within the maximum 50M interconnecting pipe lenght published by the manufacturer for this unit.
    The manufacturer sends an engineer to site to investigate & he finds the the pipework is 49M length but with 25 bends. Equivalent pipe legth is 25 by 0.35 = 8.75M + 49 = total equivalent length = 57.75M.
    As the correction for eqivalent pipe length makes a reduction of aprox 15% to 20% cooling capacity the system is actually undersized for the application.
    Result
    No warrantee
    Suggest relocate units to reduce pipe length.

    Get the idea.

    Very long pipe length with inverter systems can be a problem as the outdoor unit looks at the suction temp / pressure & if its get below target the outdoor unit ramps down the compressor. But because of the pressure drop the actual evaporating temp at the indoor unit is much higher & cooling performance is reduced.

  7. #7
    Join Date
    Sep 2008
    Location
    England
    Posts
    18
    Rep Power
    0

    Re: Measurement of pipe lengths

    Do these figures seem a bit low to anyone else? 1.5 feet for a 90 degree is under half a meter!

    Thanks for the link anyway

    [quote=nike123;120253[/quote]

  8. #8
    Join Date
    Sep 2008
    Location
    England
    Posts
    18
    Rep Power
    0

    Re: Measurement of pipe lengths

    Thermotech, do you know where I can find the Diakin specified distances for bends please, specifically for 1/4" and 5/8"?

    Many Thanks,

    B

  9. #9
    Join Date
    Mar 2007
    Location
    Warwickshire UK
    Posts
    723
    Rep Power
    21

    Re: Measurement of pipe lengths

    This sort of info is normally in the design technical manual.

    You might be able to down load from the daikin web site.

    I have an old VRV11 Basic training Manual which quotes the following equivalent length for 90 deg swept bends.
    1/4 = 0.16M
    3/8 = 0.18M
    1/2 = 0.20M
    5/8 = 0.25M
    3/4 = 0.35M

  10. #10
    Join Date
    Sep 2008
    Location
    England
    Posts
    18
    Rep Power
    0

    Re: Measurement of pipe lengths

    ah right, I will try and find something on the daikin site. I have been looking in all my product training, install manuals and f-gas training manuals.

    I would imagine those figures you noted would probably double using a bender.

    Thanks again will continue to look and will share if I find it

    Take care,

    B

    Quote Originally Posted by Thermatech View Post
    This sort of info is normally in the design technical manual.

    You might be able to down load from the daikin web site.

    I have an old VRV11 Basic training Manual which quotes the following equivalent length for 90 deg swept bends.
    1/4 = 0.16M
    3/8 = 0.18M
    1/2 = 0.20M
    5/8 = 0.25M
    3/4 = 0.35M

  11. #11
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Measurement of pipe lengths

    Batfink

    Have a look at page 23 here http://www.heronridge.co.uk/falt_cod...20training.pdf

  12. #12
    Join Date
    Sep 2008
    Location
    England
    Posts
    18
    Rep Power
    0

    Re: Measurement of pipe lengths

    nice one many thanks

    Quote Originally Posted by frank View Post
    Batfink

    Have a look at page 23 here

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Burst Pipe caused by Abrasion. (aka Only on a Friday)
    By Grizzly in forum Chit Chat & Service Stories
    Replies: 11
    Last Post: 19-09-2008, 06:59 PM
  3. Mitsubishi PUHZ-RP200YHA Pipe Sizes
    By gwilliamson in forum Air Conditioning
    Replies: 11
    Last Post: 14-05-2008, 09:43 PM
  4. Pipe sizes
    By benncool in forum Chit Chat & Service Stories
    Replies: 10
    Last Post: 08-07-2003, 10:58 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •