    Problem with plugged condenser



    Insalled new 3 phase scroll compressor, R22 system.
    the old one was rattling and making noise and not pumping.

    now the new one runs fine for a minute and starts pumping down and all the sudden the high pressure internal safety valve on the compessor pops. the high side guage is only reading 180 psi at the discharge of the condenser. so this tells me the condenser must be plugged.

    i backflushed the condenser with nitrogen today and nothing came out and seemed free from any kind of plug or chunks of anything.

    also installed a shrader valve near the discharge of the compressor to check psi there but it sure seems like the condenser is plugged up. i will try running it again later and check the PSI just after the compressor on the discharge side..

    any ideas?? i have a bad feeling its going to do the same thing even after i flushed the lines with nitrogen because they sounded clean and nothing came out.????????????????



  2. #2
    rd_shetty2003's Avatar
    rd_shetty2003 Guest

    Re: Problem with plugged condenser

    hi friend
    did u checked compressor rotetion? i feel compressor running in wrong rotetion. just change the phase and run the compressor .hope it will work well
    Quote Originally Posted by kurt s View Post
    Insalled new 3 phase scroll compressor, R22 system.
    the old one was rattling and making noise and not pumping.

    now the new one runs fine for a minute and starts pumping down and all the sudden the high pressure internal safety valve on the compessor pops. the high side guage is only reading 180 psi at the discharge of the condenser. so this tells me the condenser must be plugged.

    i backflushed the condenser with nitrogen today and nothing came out and seemed free from any kind of plug or chunks of anything.

    also installed a shrader valve near the discharge of the compressor to check psi there but it sure seems like the condenser is plugged up. i will try running it again later and check the PSI just after the compressor on the discharge side..

    any ideas?? i have a bad feeling its going to do the same thing even after i flushed the lines with nitrogen because they sounded clean and nothing came out.????????????????

  3. #3
    Join Date
    Sep 2008
    Location
    usa
    Posts
    27
    Rep Power
    0

    Re: Problem with plugged condenser

    yes tried that wirring is ok, pumping well as stated but internal pressure safety still pops. i will find out more very soon.
    thank you though

  4. #4
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Problem with plugged condenser

    I've had a vibration eliminator collapse internaly and do something similar.

  5. #5
    rd_shetty2003's Avatar
    rd_shetty2003 Guest

    Re: Problem with plugged condenser

    hi kurt s
    is it split a/c unit? u didnt mention brand of the unit. some unit has filters in indoor distibuter.if its 180 psig condersor outlet pressure then u r outdoor units is ok.plz check u r indoor unit
    regards
    dinesh shetty

  6. #6
    Join Date
    Feb 2007
    Location
    newcastle but now carlisle
    Age
    53
    Posts
    195
    Rep Power
    18

    Re: Problem with plugged condenser

    is this the comp you had problems with running the wrong way ?

  7. #7
    Vishwaprasanna's Avatar
    Vishwaprasanna Guest

    Re: Problem with plugged condenser

    Have u compair old and new compressor's specification?

  8. #8
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: Problem with plugged condenser

    if the outdoor unit comes whit a capillary,there must be a small filter and valve build to it. try to change the complete capillary set whit filter and reverse valve. it might work.
    the filter and valve is a thicker tube at the end or beginning of the capillary and functions like a injector.
    hope you now what i mean,pitty i don't have pictures at hand.

    Ice

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. A strange problem
    By MuhengineeR in forum Air Conditioning
    Replies: 14
    Last Post: 27-10-2010, 05:21 PM
  3. Air Cooled Condenser Leakage Problem with R-404A
    By RADHAKRISHNARAO in forum Technical Discussions
    Replies: 19
    Last Post: 30-07-2008, 12:21 PM
  4. Furance problem
    By ALONEI in forum Trouble Shooting
    Replies: 10
    Last Post: 14-05-2008, 11:32 AM
  5. Condenser Length Problem
    By tanveerkuet in forum Technical Speculations
    Replies: 5
    Last Post: 01-02-2008, 12:05 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •