    Air conditioning ceiling cassettes



    I quite rarely get involved with the installation of ceiling cassettes as I'm a service engineer, and deal with quite a bit of refrigeration as well as air conditioning. The thing that I always seem to take quite a while with is hanging ceiling cassettes. Usually I remove the tiles etc, put the threaded rods in and make a frame from channel before hanging another four rods to hold the cassette, but I'm sure there must be better ways than this as I seem to take quite a while to get the cassette centred. I know this probably sounds a bit trivial but any better ideas would be gratefully received.


    a problem shared is a problem halved

  2. #2
    Join Date
    Dec 2001
    Location
    UK
    Posts
    137
    Rep Power
    23
    Why the intermediate chanel frame and second set of drop rods? Get the manufacturers installation instructions for the spacing requirement ie details of their hanging brackets / fixing requirements and locate the drop rods to suit.

    Most cassette units are well balanced so anti vibration shouldn't be a problem unless the rods are extremely long (over a metre). This would be the time to use an intermediate frame just for dampening purposes.

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60
    Iceman, I think you are probably using the normal method; that's the same as the install guys used at my last firm.

    I have recently seen a cassette suspended using eye-bolts and crimped wire-cable supports, so I suppose anything is possible as long as it takes the weight.

    You might find that the extra time you think you are taking is not actually that long. Your install guys will probably rib you about it because that's what they do After a while I expect that your time will improve, at the moment you daren't make a 'bad job' of it as your service tech. comments about the install are coming back to roost.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Feb 2004
    Location
    Australia
    Posts
    286
    Rep Power
    21
    Thanks for the replies. I used to be an install engineer when I started in the business, and worked mainly on large industrial and commercial ducted systems, chillers etc, where we were under quite alot of time pressure to turn the job around. I've always used the method above because it's just the way I was shown all that time ago, using the extra rods to enable adjustments to the position, but had just wondered if there was a quicker way that someone else may employ in order to get the cassette centred quickly without having to make adjustments to the frame.
    a problem shared is a problem halved

  5. #5
    rbartlett's Avatar
    rbartlett Guest
    the extra channel isn't really needed -it's just to make you feel 'safe' it's like they aren't too sure of their marking out so need adjutment in all directions

    some like it as they feel it's more 'professional' looking
    i feel it just spends more time/money on the job

    i don't see quite get the vibration aspect either
    i just looked at a job to replace 2 cassettes and they were on rods of about 8 metres length-no one mentioned vibration

    take out the tiles and from your centre (say where the bars cross) from the cardboard template mark out where the fixing points are on the ceiling grid. (do the same on the opersite side)

    the use either a sprit level and project up to the ceiling
    or use one of these http://www.screwfix.com/app/sfd/cat/...67061&id=29941

    you should have 4 dots on the ceiling to mark two lines-this is where you fix your channel.

    you don't need any movement in that plane but the channel will allow you to slide the rods back and forth to align in the other plane

    complex to describe but easy and cheaper to perform


    cheers

    richard
    Last edited by rbartlett; 12-02-2004 at 08:44 AM.

  6. #6
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34

    Re: Air conditioning ceiling cassettes

    We do it like drawn in this raw sketch. We need 4 standard channels (omega channels we call it) of 2 m.

    The 2 channels whereon the unit is attached is not fixed on the 2 upper channels. They're just laying on the upper 2.

    With this system, you can slide almost 60 cm in each direction, enough to fit in a tile ceiling of 60/60 (cm)

    The threated rods are parallel fixed so you can regulate the height very easy (just release the parallel 'nuts' movng up, adjust the height of the 2 rods a little bit and slide the parallel nut down again)
    Attached Images Attached Images
    Last edited by Peter_1; 12-02-2004 at 08:24 AM.

  7. #7
    rbartlett's Avatar
    rbartlett Guest
    how do you 'do' attachments?

  8. #8
    Join Date
    Nov 2003
    Location
    NSW, Australia
    Age
    40
    Posts
    243
    Rep Power
    21
    click the post reply button, takes you to a more advanced reply screen with more options. one of them is to attach a file limit of 10mb i think.
    "Old fridgies never die, they just run out of gas!"

  9. #9
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46
    hi guys ,

    you are late online so I'm always on the next day.

    so many ways to hang a cassette, my way is a bit different,

    I mark the ceiling with a plumb bob from four corners of the lower ceiling, the rods (concrete) or cables (wood) or weld (steel construction)

    this way the four rods are a bit bigger then the holes on the cassette.

    when connecting, it forms a piramide like shape and two nuts from each side securing it .

    this way it can not swing and easy to adjust in place.

    chemi

  10. #10
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46
    richard,

    when you scroll down, at the bottom right you have the "post reply" icon.
    click it and it will take you to another page where you can add smilies, attachetments - watch the size!

    chemi












    '

  11. #11
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34
    Hey,
    perhaps a good tip for some of you:
    we use a not very expensive pneumatic lift (a sort of a piston) to lift loads from +/- 250 kgs (or 500 pounds )t o a heigght of +/- 5 m (or 15 ft)
    You only need an air compressor or nitrogen.
    We even use it to mount cold room panels (ceilings)
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  12. #12
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34
    Was not able in previous post to post the picture.
    Attached Images Attached Images

  13. #13
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60
    Yes, the good old Genie hoist, we have also used CO2 as the lifting gas.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  14. #14
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46
    marc,
    out of curiosity, how much do customers pay in the UK for cassette instalation with pipes, run up to 60 feet?

    your idea looks good on paper but you will need in practice quite a few sizes of these H frames.

    if it is wood construction, why not cables

    chemi

  15. #15
    rbartlett's Avatar
    rbartlett Guest
    chemi -i don't think anyone would let you use wood for these installs

    marc's idea still uses one more length of unistrut than my idea with no advantages as far as i can see..


    cheers

    richard

  16. #16
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46
    richard,
    I did not mean to use wood!?!?

    in many places, there is a wooden construction over the ceiling which holds the roof.

    what would you do if you had to install a cassette in such situation?

    chemi

  17. #17
    rbartlett's Avatar
    rbartlett Guest
    sorry chemi my mistake...;-)

    i would still use my method of attaching the unistrut channel to the wood with coach bolts

    http://www.screwfix.com/app/sfd/cat/pro.jsp?id=16973

    of course there is an idea that we only use channel because we can't mark out accurately...


    cheers

    rihard

  18. #18
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Thumbs up

    hi richard,

    this is what I use for marking.

    what do you call it in the UK?

    chemi
    Attached Images Attached Images

  19. #19
    rbartlett's Avatar
    rbartlett Guest
    it's called a plumb bob

    like this-

    http://www.screwfix.com/app/sfd/cat/...89283&id=10856

    cheers

    richard

  20. #20
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34
    Isn't there a drill pattern in cardboard delivered with each indoor unit?
    Mitsu's have this .
    Do you guys use the parallel nuts, like you can see in this picture;
    You hold the 2 rods together and sldie the nut over it. You can turn both rods or remove the nut, position the rods in another position and slide the nut over it again. Very easy.
    Last edited by Peter_1; 13-02-2004 at 11:02 PM.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  21. #21
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34
    pICTURE

    And who knows this products

    http://www.erico.com/products.asp
    Attached Images Attached Images
    • File Type: jpg s.jpg (33.8 KB, 58 views)
    Last edited by Peter_1; 13-02-2004 at 11:02 PM.

  22. #22
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,733
    Rep Power
    51
    The wire suspension system that Brian mentioned is called Gripple. www.gripple.com We have used it on a few jobs and found it easy and quick to use. Here is a link to a case study where they mention hanging fan coils with a 65% saving in labour costs. http://www.gripple.com/casestudy/cas....cfm?StudyID=6

    We only use the double unistrut hanging method when we install cassettes in a building where the suspended ceiling is not yet in place as in a new build project. We can then have upto 150mm adjustment available to align the cassette with the ceiling once it has been installed. As we all know - suspended ceiling contractors are a law unto themselves, fixing the grid where they think it should be installed with no regard for other trades or agreed datums

Similar Threads

  1. Air Conditioning Courses
    By stesmith1981 in forum Industrial
    Replies: 8
    Last Post: 09-03-2010, 07:33 PM
  2. Ceiling Cassettes
    By paul39 in forum Air Conditioning
    Replies: 1
    Last Post: 06-07-2006, 10:42 PM
  3. Air conditioning maintenance procedure
    By Andy T in forum Air Conditioning
    Replies: 12
    Last Post: 27-05-2006, 06:57 PM
  4. Ceiling casettes
    By daddymac in forum Air Conditioning
    Replies: 8
    Last Post: 20-12-2005, 06:10 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •