    Red face R-404a running pressures



    hi can anyone tell me the approx running pressures for R-404a on an upright freezer. its been a while since i last used this gas. cheers dougie.



  2. #2
    Join Date
    Jan 2007
    Location
    scotland
    Age
    46
    Posts
    159
    Rep Power
    18

    Re: R-404a running pressures

    hi dougie,
    i tend to run suction at around 0.7/1.4bar and as long as the hp is below 15bar it should be okay but it really depends on the case.

  3. #3
    zosoguy's Avatar
    zosoguy Guest

    Re: R-404a running pressures

    it depands on the evaporation temperature...
    if evaporation temperature is -40 C then suction pressure is around 1 - 3 psig and condensing pressure around 200 psig.

    if evaporation temperature is -25 c then sp might be approx. 10-12 psig and condensing presssure might be up to 220-240 psig.

Similar Threads

  1. Problems with compressor running too cold
    By abrando1 in forum Trouble Shooting
    Replies: 8
    Last Post: 12-05-2009, 10:08 PM
  2. running pressures
    By sean1 in forum Fundamentals
    Replies: 33
    Last Post: 03-04-2008, 01:38 PM
  3. R 404a
    By Samarjit Sen in forum Refrigerants
    Replies: 59
    Last Post: 07-08-2007, 06:35 PM
  4. Walkin cooler running to warm need help
    By The Butcher in forum Trouble Shooting
    Replies: 7
    Last Post: 03-08-2007, 09:19 PM
  5. Running Pressures!
    By G_Young in forum Air Conditioning
    Replies: 12
    Last Post: 16-11-2006, 12:00 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •