    Problem with Trane RTAD100 chiller.



    Hello guys,

    I have a communication problem with a Trane chiller.
    At start-up I read on the display that there is a communication problem between machine module and option module. The option module in this case is a Siemens PLC. On the PLC module is a touchscreen that gives me a chiller alarm. I know nothing about plc's so I am a little bit stuck here .



  2. #2
    Join Date
    Apr 2007
    Location
    West Midlands
    Age
    45
    Posts
    55
    Rep Power
    17

    Re: Problem with Trane RTAD100 chiller.

    Hi,
    It looks like you have a communication fault caused by the ribbon cable, it's a common fault on these units, and it is normally around the ribbon connector, you may see signs of corrosion if you look closely. Most people just cut out the plastic connector and connector block it.
    The CH530 controller is a clever bit of kit, and without the techveiw software your going to struggle, if it's not an easy find on the cable your best to ring Trane.

    Chris.

  3. #3
    Join Date
    Oct 2007
    Location
    Belgium
    Age
    58
    Posts
    29
    Rep Power
    0

    Re: Problem with Trane RTAD100 chiller.

    Thanks Chris. I am going to that customer again this week and see if I can fix it.

    Eric.

  4. #4
    Join Date
    Aug 2003
    Location
    Netherlands
    Age
    49
    Posts
    620
    Rep Power
    21

    Re: Problem with Trane RTAD100 chiller.

    Rtad's in europe don't have the ch530 yet. They still come with the UCM-CLD.

    There's a connector called J1 that might make bad contact! This is the comm link between the modules.

  5. #5
    Join Date
    Oct 2007
    Location
    Belgium
    Age
    58
    Posts
    29
    Rep Power
    0

    Re: Problem with Trane RTAD100 chiller.

    Thanks Lowrider. I'll check that...

    Eric.

  6. #6
    Join Date
    Oct 2007
    Location
    Belgium
    Age
    58
    Posts
    29
    Rep Power
    0

    Re: Problem with Trane RTAD100 chiller.

    I went back to that customer today and found what the problem was. Inside the chiller you have 4 modules. The module on top isn't working anymore. I took a module out of a good working unit and then it worked, so it must be that module...

    Eric.
    Attached Images Attached Images

  7. #7
    Join Date
    Apr 2007
    Location
    West Midlands
    Age
    45
    Posts
    55
    Rep Power
    17

    Re: Problem with Trane RTAD100 chiller.

    Hi Eric, thats the main control board i think, bloody expensive one to replace i believe.

    Well doe anyhow mate (allways good when you can pinch a part from another unit to test! )

    Chris.

  8. #8
    Join Date
    Oct 2009
    Location
    merida mexico
    Age
    53
    Posts
    282
    Rep Power
    15

    Re: Problem with Trane RTAD100 chiller.

    this model unit has one port paar 5vcd verify voltages and 12VDC, check the configuration of the machine as a parameter changed or denied causing the main module will send alerts or communication problems

  9. #9
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Problem with Trane RTAD100 chiller.

    Quote Originally Posted by on4hf View Post
    Thanks Lowrider. I'll check that...

    Eric.
    good catch on the bug u might want to check the module for a blown fuse some of them have it inside or for a bad dip switch setting or else just buy a new one !

Similar Threads

  1. Trane chiller
    By Lman in forum Trouble Shooting
    Replies: 4
    Last Post: 13-11-2009, 03:51 PM
  2. Help to solve problem on York chiller
    By nassersh in forum Trouble Shooting
    Replies: 7
    Last Post: 03-06-2008, 08:38 PM
  3. York Chiller Excessive Purges Problem
    By imranmd in forum Commercial
    Replies: 5
    Last Post: 07-03-2008, 05:13 AM
  4. R11 Centrifugal Chiller Oil Problem
    By iceman007 in forum Trouble Shooting
    Replies: 8
    Last Post: 17-02-2008, 02:14 AM
  5. Connecting Trane Water chiller to air handling unit
    By celtictech in forum Fundamentals
    Replies: 10
    Last Post: 08-03-2007, 06:14 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •