Results 1 to 12 of 12
    Split Croatia
    57
    6,151
    36
    Theory of capilary tube
    Oct 2003
    5,630
    34
    Re: Theory of capilary tube
    Nike, you need a password to enter this site
    Split Croatia
    57
    6,151
    36
    Cheking! .....
    Sorted.
    You could delete this now!
    Thanks!
    Oct 2003
    5,630
    34
    some extractions out of the article which I disagree
    'Liquid refrigerant flows faster than vapor'
    'The colder the liquid ,the faster the flow'
    Page 4, second paragraph, the example he describes is in my opinion not right. He sees a blocking condenser as something that always escalates till the compressor shuts out on its HP.
    Jun 2007
    At sea
    367
    This description by Henry Ehrens is an adjunct to his previous paper but its size is too large to attach to this reply. If you send a PM I will send you a copy.
    Or I can send it to a Moderater who can then post it.
    Peter - I can send it to you?
    It describes nicely the whole process and includes pressures and temps at various points for all conditions and is very good indeed. It covers low charge and high charge plus general understanding of how to troubleshoot systems.
    I also agree some of the statements he makes are a little confusing like the 'liquid flows faster than vapour' and can only assume he is refering to mass flow for any given pressure drop otherwise it does not make sense. What is actually happening inside the tube is a topic of intense study.
    Chef
    Oct 2003
    5,630
    34
    You may mail it to my private email address Chef
    May 2008
    66
    802
    can you put it on the forum to or to my private mail ??.always in for something nice to read & learn.
    thnx peter & chef
    Ice
    Feb 2007
    2,473
    45
    If someone email it to me I will post it on my site for public download
    Jun 2007
    At sea
    367
    Having looked again at this 'Theory article' it seems to be misleading.
    When a cap tube is sized for a specific duty the two phase flow region provides most of the pressure drop. Lets assume this length is calculated to be 1 metre.
    If we then add 0.5 metres for a total length of 1.5 metres then this extra lenth is the stability part and means the liquid must be subcooled as it enters the tube. This subcooloing is then lost (as a pressure drop) as it passes down the first 0.5 metres of the tube.
    Once you've decided on a certain subcooling and hence length in the design the actual amount the subcooling varies is very little over the load ranges of a typical system. Perhaps just 2 or 3 degrees C and certainly not the 10C that the article invokes.
    Generally though it gets the point across about the subcooled pressure loss zone and is good for that.
    Really the only way to figure it all out is to connect the cap tube calculations to the system and include changing pressures and tempertures at the evap and condenser and the compressor power to see how it all moves together as a system, how it balances. Now there is a challenge! Anyone up for it?
    Chef
    May 2008
    66
    802
    sounds to me it is something for someone ho is most of the time at sea ;-)) .
    Ice
    Oct 2003
    5,630
    34
    I placed the article Chief send me on an external server.
    You can download it on http://www.megaupload.com/nl/?d=IK0AP453
    Fill in 3 letter Antispamcode -> Download - > NEw Screen -> Free column, -> Countdown timer at the bottom of +/- 45 seconds -> Then button Free Download Appears instead of the countdown timer.
    Split Croatia
    57
    6,151
    36
    Or, you could download it here immediately!
    Peter, try to use this server:
    http://www.mediafire.com/
  1. Capillary tube sizing
    By Sledge in forum Refrigerants
    Last Post: 16-11-2010, 11:44 PM
  2. Cap Tube Design Program - Results
    By Chef in forum Fundamentals
    Last Post: 01-09-2008, 09:49 AM
  3. excess tube length on condenser tube plate
    By onquin in forum Fundamentals
    Last Post: 15-11-2007, 06:03 AM
  4. Coils - Inline vs Staggered tube
    By nh3simman in forum Fundamentals
    Last Post: 03-04-2007, 08:25 PM
  5. metric capillary tube
    By tralex in forum Fundamentals
    Last Post: 21-02-2006, 06:57 AM