Results 1 to 5 of 5
  1. #1
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18

    Retrofit on carrier 30bq035



    Hi everyone.
    Next week i'll make a retrofit from R22 to R407C on a chiller 30BQ035 /100 kw CARRIER.
    I'll change the semi-hermetic compressor to a new one and Carrier's company ask me only to fit new oil and new drier cartridge twice without changing expansion valve or anything else...
    Just need advise and comment.
    Yours sincerely
    cool#9



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Retrofit on carrier 30bq035

    Go with the advice from Carrier, they should know their own product.

    R22 TXVs are often found of R407c systems.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Mar 2008
    Location
    bradford
    Age
    48
    Posts
    5
    Rep Power
    0

    Re: Retrofit on carrier 30bq035

    Changing drier twice???

    Why?

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Retrofit on carrier 30bq035

    Quote Originally Posted by thisname View Post
    Changing drier twice???

    Why?
    Probably because of the oil cleanup being done.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Mar 2007
    Location
    France
    Posts
    236
    Rep Power
    18

    Re: Retrofit on carrier 30bq035

    Thanks everyone and hello.
    I'll change the compressor tomorrow morning: six cylinders, 250 kgs with the valves. I'll fit new POE oil inside after cleaning some parts of the refrigerant circuit with OZEON CLEAN.
    I'll change the oil and refrigerant a second time that's why i need 2 driers...
    I' m just afraid of the glide with the R407C in heating mode inside for the defrost of the outside heat exchanger in winter.
    rgds
    cool#9

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. carrier fault codes
    By richelli in forum Trouble Shooting
    Replies: 5
    Last Post: 18-06-2010, 07:35 AM
  3. Carrier Pro Dialog Plus help
    By borodave1973 in forum Air Conditioning
    Replies: 5
    Last Post: 11-11-2007, 06:47 PM
  4. Carrier Chiller Help
    By superswill in forum Trouble Shooting