Results 1 to 5 of 5
Thread: clogged liquid line drier
-
09-09-2008, 07:49 PM #1
clogged liquid line drier
what pressures would i expect with a clogged filter drier
-
09-09-2008, 08:11 PM #2
Re: clogged liquid line drier
Hi Pat.
Follow the link for a similar thread I posted earlier.
Grizzly
http://www.refrigeration-engineer.co...ad.php?t=14739
-
10-09-2008, 01:57 AM #3
Re: clogged liquid line drier
To many variables to be able to calculate. The obvious is temperature diff. across the drier and low suction pressure.
-
10-09-2008, 02:58 AM #4
Re: clogged liquid line drier
With great power Comes Great Responsibility
-
10-09-2008, 03:00 AM #5
Re: clogged liquid line drier
depends on the clogged on your drier and the ambient temperature of your condensing/outdoor unit.. expect that your suction pressure will be low compared to normal suction pressure..
when you touch your drier.. if it is cold expect that it is clogged and if its warm it is good..With great power Comes Great Responsibility