    what pressures would i expect with a clogged filter drier



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: clogged liquid line drier

    Quote Originally Posted by Pat schluter View Post
    what pressures would i expect with a clogged filter drier
    Hi Pat.
    Follow the link for a similar thread I posted earlier.
    Grizzly
    http://www.refrigeration-engineer.co...ad.php?t=14739

  3. #3
    Frigman's Avatar
    Frigman Guest

    Re: clogged liquid line drier

    To many variables to be able to calculate. The obvious is temperature diff. across the drier and low suction pressure.

  4. #4
    Join Date
    Apr 2008
    Location
    philippines
    Posts
    95
    Rep Power
    17

    Re: clogged liquid line drier

    Quote Originally Posted by Pat schluter View Post
    what pressures would i expect with a clogged filter drier
    depends on the clogged on your drier.. and the ambient temperature in your condensing/outdoor unit..

    expect that your drier will be cold if it is clogged and expect that it is warm when it is good...
    With great power Comes Great Responsibility

  5. #5
    Join Date
    Apr 2008
    Location
    philippines
    Posts
    95
    Rep Power
    17

    Re: clogged liquid line drier

    Quote Originally Posted by Pat schluter View Post
    what pressures would i expect with a clogged filter drier

    depends on the clogged on your drier and the ambient temperature of your condensing/outdoor unit.. expect that your suction pressure will be low compared to normal suction pressure..

    when you touch your drier.. if it is cold expect that it is clogged and if its warm it is good..
    With great power Comes Great Responsibility

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Suction gas <-> liquid line heat exchange and performance gains
    By DaBit in forum Technical Speculations
    Replies: 30
    Last Post: 18-05-2010, 01:52 PM
  3. Liquid line for multi evaporators
    By Kevin Yeo in forum Supermarket Refrigeration
    Replies: 1
    Last Post: 29-12-2005, 02:29 PM
  4. Parker levels in ammonia systems
    By Friobernal in forum Industrial
    Replies: 3
    Last Post: 04-08-2005, 03:46 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •