    arneg brema glass door freezers



    anyone experienced problems with new installations of these cabinets,having issues with snow on shelving and bad condensation on drain fittings.the snow problem appears to be from too much condensation when on defrost,defrost settings are termination 8degrees,defrost time,half an hour ever 4 hours.All doors are sealing ok and no air is getting into cabinet.The other problem is the drain fitting sweating,the cabinets come with a plastic fitting so a drain heater is not an option,arneg in italy not interested in problems anyone else come across these problems



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: arneg brema glass door freezers

    What is the 'drip time' and 'fan delay time' ?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Feb 2007
    Location
    oldham
    Age
    49
    Posts
    44
    Rep Power
    0

    Re: arneg brema glass door freezers

    3 mins drip time,-2 fan delay

  4. #4
    Join Date
    Jun 2002
    Location
    UK
    Posts
    628
    Rep Power
    23

    Re: arneg brema glass door freezers

    Quote Originally Posted by fazzamouse View Post
    anyone experienced problems with new installations of these cabinets,having issues with snow on shelving and bad condensation on drain fittings.the snow problem appears to be from too much condensation when on defrost,defrost settings are termination 8degrees,defrost time,half an hour ever 4 hours.All doors are sealing ok and no air is getting into cabinet.The other problem is the drain fitting sweating,the cabinets come with a plastic fitting so a drain heater is not an option,arneg in italy not interested in problems anyone else come across these problems
    Defrost every 4 hours seems a bit extreme to me in this application.
    I would look into the control side,settings and probe location.

    Mark

  5. #5
    alberto.fgn's Avatar
    alberto.fgn Guest

    Re: arneg brema glass door freezers

    Hi fazza
    Set point at -25, end defrost at 8° is ok, 3 min drip-off, and 3 min delay fans (or -15°C).
    2 defrost for day its enough and better when the shop is closed.

    Bye

  6. #6
    Join Date
    May 2007
    Location
    scotland
    Posts
    756
    Rep Power
    19

    Re: arneg brema glass door freezers

    hi these freezers on electric defrost should be 2 defrosts a day max time 40 minutes minimum time 20 mins with fans on during defrost as these freezers have term klixons on the right hand side of evaporator the defrost term probe if fitted should be positioned on the midle pass of evap end at the top with a 10 d/c term kiss bye bye to the frost build up

  7. #7
    bazza23's Avatar
    bazza23 Guest

    Re: arneg brema glass door freezers

    Hi I have had same problem in NZ and found that base of unit below doors has expanded due to moisture in timber frame

Similar Threads

  1. Estimating savings for low-e glass
    By Larry2 in forum Technical Discussions
    Replies: 0
    Last Post: 17-09-2007, 12:25 AM
  2. Leaking sight Glass!?!!
    By The MG Pony in forum Fundamentals
    Replies: 10
    Last Post: 19-04-2007, 06:09 AM
  3. liquid line sight glass mystery
    By austech in forum Technical Discussions
    Replies: 19
    Last Post: 18-07-2006, 08:16 PM
  4. Sight Glass Located
    By Abe in forum Trouble Shooting
    Replies: 3
    Last Post: 22-01-2002, 01:22 AM
  5. Sight Glass,
    By Abe in forum Trouble Shooting
    Replies: 4
    Last Post: 03-08-2001, 08:36 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •