Results 1 to 6 of 6
  1. #1
    hvac4178's Avatar
    hvac4178 Guest

    SUBCOOLING Problem



    Hello Everyone,
    I am a colllege student and I am currently enrolled in a class dealing with Refrigeration engineering.I am attempting a homework problem but I am having a rather difficult time with it. It deals with Subcooling of refrigerant R134A and states for R134a analyze the effect of subcooling from 0 to 10 Deg F and plot the refrigeration effect and COP as a function of sub degrees of cooling. I have no clue on this one. I am trying to plot my points on my PH Diagram but i cant get my points to calculate COP or refrigeration effect. How do I solve this?

    I know COP in this case would be=(h2-h1')/(h3-h2)

    I am also going to try to use EES for this problem. Anyone ever use it? I am in need of help, i dont understand.



  2. #2
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: SUBCOOLING Problem

    play whit coolpack for a wile.

    you wil figgered out.

    Ice

  3. #3
    hvac4178's Avatar
    hvac4178 Guest

    Re: SUBCOOLING Problem

    is coolpack available in English Units by chance?

  4. #4
    Join Date
    Jun 2007
    Location
    At sea
    Posts
    367
    Rep Power
    17

    Re: SUBCOOLING Problem

    Quote Originally Posted by hvac4178 View Post
    .....analyze the effect of subcooling from 0 to 10 Deg F and plot the refrigeration effect and COP as a function of sub degrees of cooling.
    Is this the actual thing you are looking for? It seems you want to plot a graph of COP versus subcooling.
    Your idea to use EES would be quite easy but maybe the course tutor wants to see how you solve it, so maybe rewrite your equation for COP to include a term for the effect of subcoling.
    Chef

  5. #5
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: SUBCOOLING Problem

    yep, coolpack is standaard English.

    and try to follow the tips from Chef. now you gone learn something.

    Ice

  6. #6
    Join Date
    Jun 2007
    Location
    At sea
    Posts
    367
    Rep Power
    17

    Re: SUBCOOLING Problem

    Quote Originally Posted by hvac4178 View Post

    I know COP in this case would be=(h2-h1')/(h3-h2)

    .
    hvac - I am not sure we are using the same nomenclature here but your COP seems to negative or even an imaginary number (like SQRT(-1) or similar). But the problem seemed interesting so investigating this in more detail brings more complications.

    The problem seems to be with what type of system has the subcooling.

    Case 1
    If the system was designed to have subcooling, with say an after cooler, then the equation might look like COP=(h1-h4')/(h2-h1).

    Case 2
    BUT if the system actually needs subcoolng to regulate and balance then it would be very different and be more like COP=(h1-h4)/(h2"-h1)

    We can see here that h3"=h3 but h2">h2 so again it shows a drop in the COP by requiring more power input for the same cooling effect.

    In case 1 the subcooling gives an increase in COP and is therefore 'useful' but case 2 gives a reduction in COP and is therefore 'not useful' so the type of system being modelled is key to defining the slope of the final graph of subcool versus COP.

    Bottom line is subcooling is not always good but maybe necessary.

    The PH diags I have show it better.
    (h' is deltaT and h" is deltaP)

    Chef

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. A strange problem
    By MuhengineeR in forum Air Conditioning
    Replies: 14
    Last Post: 27-10-2010, 05:21 PM
  3. Furance problem
    By ALONEI in forum Trouble Shooting
    Replies: 10
    Last Post: 14-05-2008, 11:32 AM
  4. Subcooling
    By terryw in forum Supermarket Refrigeration
    Replies: 12
    Last Post: 07-03-2007, 09:53 AM
  5. Subcooling & Refrigerants
    By US Iceman in forum Fundamentals
    Replies: 40
    Last Post: 29-04-2006, 02:59 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •