    display units



    Hi every one I am from East Africa Tanzania I have this problem in supermarket display units previous ones used expantion valves and new ones use capillary , we usually have frequent power failures and we have to switch off main aircon and immediatly temp goes high on units but older one with expantion it used to maintain its cooling why can some one educate me on this.Thanks in advance



  2. #2
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46
    hi jay,

    do each display unit has its oun condensing unit or its a rack?
    are they pumpdown system or jujt on/off?

    give us some more details please.

    chemi

  3. #3
    Join Date
    Mar 2003
    Location
    Tanzania(East Africa)
    Age
    59
    Posts
    27
    Rep Power
    0

    display units

    It has indivisual condencing units .
    with mechanical defrost timer and no heater to defrost .

  4. #4
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Post

    hi jay.

    I guess in the old display units the evaporator is at the top and when the power stops the refrigerant migrates to the cold spot which in this case its the evaporator at the top. this slow circulation lasts for about two minuts before it starts to get hot. and thats explains why it stays cool.

    the new units which have the evaporator at the bottom under the steel plates "pull" the hot air in dou to higher ambient air pressure and gets hoter more quickly.

    I think that what is happening there.

    is the serengeti park still as beutiful as used to be 20 years ago?

    chemi
    Last edited by chemi-cool; 30-01-2004 at 08:25 PM.

  5. #5
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,119
    Rep Power
    26
    This thread must win the poll for bad......ahem......awful spelling!!!
    But, talk of serengeti has got me going!!!

    Ahhh......Ngoro goro Crater............and Mount Kilomanjaro.
    Wow

    Ill give my eye teeth to go there
    Hey, Jay........you got a job going there??? In return for some lessons in spelling !!!

    Lol
    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.

  6. #6
    Join Date
    Mar 2003
    Location
    Tanzania(East Africa)
    Age
    59
    Posts
    27
    Rep Power
    0
    it still wild and under german management but animals are too less it is worth to visit once again you will not be dissapointed i bet you . thanks for help both have their evoporator in same position at bottom with fans blowing air through them and coming back from top, and we have many other places worth visiting but its real costly

  7. #7
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,645
    Rep Power
    34
    Originally posted by Aiyub
    This thread must win the poll for bad......ahem......awful spelling!!!
    But, talk of serengeti has got me going!!!

    Ahhh......Ngoro goro Crater............and Mount Kilomanjaro.
    Wow

    Ill give my eye teeth to go there
    Hey, Jay........you got a job going there??? In return for some lessons in spelling !!!

    Lol
    Aiyub,
    Sorry, I have to say this but English talking peoples - especially sorry again .....Americans - thinks that the whole world speaks English. Don't forget that the English language is only on the fifth ranking of world languages.
    Also I have to use some spelling corrections - mostly typing errors - but don't let us fall in the same trap as alt.hvac where a pure technical question is mostly responded with sarcastic answers. That's the reason why I moved to here.

    Don't take this personally Aiyub, but this was what I felt when I read your response. Lucky for Jay he mentioned something about Africa. I also had difficulties reading the post but I waited what others should say, ..technically.
    He was understandable, because Chemi tried to help him.

    I will be the first to ask to correct my spelling because I wanna write down as correct as possible.

    Not everyone in this big world has the possibility to learn proper English and even worser, ...going to school to learn elementary things like reading and writing,.... let's take aside learning another language.

    I once worked a time together with Romanian (here goes my spelling again) and Polish peoples (here in Belgium),... well ...you should start crying if you hear there stories and especially when you realize why they came working here in Belgium.

    I will give you an example how we Flemish (Dutch speaking part of Belgium) think: if we Belgians go to Spain, we try always to speak Spanish, or Italian in Italy, or German in Germany. We (try) to adapt us to the country we're going. In the first place, we never try to speak our own language in a foreign country, we try to speak their language. If this doesn't work, we then switch to what we think they will understand the best (for example French in Italy) and last to English. And I speak much better English then French and even then, we try it in French. That's an attitude we learned in school and all the Flemish peoples I know do it like that.

    I will end Aiyub with this..... all - and I mean ALL - your posts were more of worth reading them , with always a humoristic undertone.
    No hard feelings at all but that's me..... I say or at least ,... I try to explain what I feel.
    Last edited by Peter_1; 31-01-2004 at 02:33 PM.

  8. #8
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46
    hi peter.

    my mother never spoke to me in english so I do my best.
    please dont take it personal, some people have that thing about perfect writing, some about perfect cleaness and so on.

    I would like instead to be corrected when I make a spelling mistake and not use a programme to do it for me. this way I will learn better.

    take it easy and have a great day.

    chemi

  9. #9
    rbartlett's Avatar
    rbartlett Guest
    i can't speak any other language so really apreicate how well chemi, peter etc cope with the more technical aspects..and i love miltons posts for there directness ;-)

    however very often i write thinking everything was correct only to read it back with mistakes all through it....:-/

    (i personally believe this has something to do with bill gates deliberately trying to undermine my obviously superior intellect ;-)

    anyway nuff said...

    cheers

    richard

  10. #10
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,632
    Rep Power
    24
    Hi
    English is the language I am supposed to speak and my spelling is terrible. Personally I don't mind spelling as long as the point of the conversation is not lost to the reader.
    Anyway I speak an english dialect, which has not really got a written form, you would not want to see the attempts people make at trying to write Ulster Scot's.
    Kind Regards. Andy.

  11. #11
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,119
    Rep Power
    26
    Hello Peter,

    I know exactly where you coming from, and no, I take it on the chin and bear no hard feelings.

    I am not critical of anyone whos first language is not English who makes spelling errors, in fact 100% marks to them for having tried in the first place.

    I assume a very laid back and humurous stance on this forum, I never get too serious or worked up any anything. I do appreciate the fact that we are a collection of people from around the world, all with a common ground, "a love of refrigeration"

    Thats all that matters, and we try and help each other out, like I have been helped out in many times.

    No one is superior, there is no class or language barrier. We are all one happy big family.

    I would just be estatic if a Mongolian from upper Siberia or an Argentinian from Cape of Horn posted here, good english or bad, its the contribution that counts.

    My first language is not English............( surprise, surprise!!! ) so for me to be sarcastic of anyone else would be like the pot calling the kettle black!!!!

    So, please, Im just the joker in the pack, and my brand of humour gets me in trouble sometimes, but I got that from the Brits........they joke about everything, from the minute they wake up in the morning.

    And, lastly.......if you want me to help with a technical question.......forget it!!! I can help with legal and business issues.....but to tell you psychometric properties or enthalpy.......or why evap is not cold..........Im not your man.

    Funny because I run my own fridge business

    So, to all in this happy melting pot of ours...........read my lips......your spelling does not matter!!!!! Keep on posting.

    And this is for Jay.

    Namesti bhai, aoo be gujerati waat keroo. Mene taroo telephone dewanu, aoo tene phone keraaa

  12. #12
    rbartlett's Avatar
    rbartlett Guest
    [Namesti bhai, aoo be gujerati waat keroo. Mene taroo telephone dewanu, aoo tene phone keraaa [/B][/QUOTE]


    that's easy for you to say !! ;-)

    cheers

    richard

  13. #13
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46
    ok guys,

    now that we have finished with language issue, lets go back to the original problem. jay's supermarket display units.

    please read it again and think of an answer.

    chemi

  14. #14
    Join Date
    Jun 2002
    Location
    UK
    Posts
    633
    Rep Power
    23

    Post Display Units

    hello jay
    surely the compressor units are integrally mounted in the base.
    And the temperature rise in the case is due to the ambient temperarure in the shop rising having a proportional effect on how the unit condenses.I cant see the compressor/condenser being remotely mounted using capillary tube .
    I have seen it done and im not saying it wont work,however as well as being very bad practice i think the compressor would soon reach the end of its working life.Lol
    Capillary systems dont cope very well with high ambients(in the uk anyway)maybe its just the design of our equiptment in the uk.
    regards mark

  15. #15
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,119
    Rep Power
    26
    The way I read the posting.

    One unit has an expansion valve
    One unit has a cap tube
    Air conditioning is switched off............ie: ambient increases
    Display units still running.

    Unit with expansion valve works better
    Unit with cap tube struggles

    So, I put it down simply to: Expansion valve offers superior cooling performance, especially as condensing units are remote

    How far are the condensing units from the evaporator?
    With remote units, cap tube is not a good idea

    Replace cap system with expansion valve. You will see an improvement in efficiency

    Someone can explain why on a remote system expansion valve is better then cap tube

    There are also lots of other factors to consider
    Are both condensing units same, same capacity, similar age, are both compressors working properly, valves in good condition
    Are the line distances the same
    Are condenser coils clean, condenser fans working ok

    You need to log all the pressures, temperatures of both systems so an analisis can be made
    Any opinions, statements and facts expressed in this message do not constitute legal advice in any shape or form and is given for a general outlook in nature. You are advised to seek appropriate and specific professional assistance from a regulated and authorised advisor for definitive advice.

  16. #16
    Join Date
    Jun 2002
    Location
    UK
    Posts
    633
    Rep Power
    23

    Post Display Units

    hello all
    Capillary tube cabinets are mostly used on small cabinets with very short pipe runs due to the critical refrigerant charge.
    Lets take the scinareo that the liquid and suction line are extended, the accumulator is not sized to hold this extra volume of refrigerant the compressor goes off cycle ,the liquid refrigerant migrates to the evaparator on start up the compressor trys pumping liquid .So therefore a typical TEV/RECIEVER system would be more cost effective long term.The case temperature pull-down would be dramatically improved due to increased liquid refrigerant entering the metering device,and better heat transfer .
    The cap tube is a critical charge insufficient charge starves the evaparator ,overcharge has an adverse effect on operation and any refrigerant in excess will back up into the condenser therefore the evaparator temperature would go up.
    I have attended jobs in the past with capillary/liquid lines installed 30+ meters by cowboys, both times the compressors were u/s.This in my opinion is very bad practice.
    hope this helps
    regards mark

  17. #17
    Join Date
    Dec 2002
    Location
    sunshine-coast, australia
    Posts
    88
    Rep Power
    22
    [QUOTE]Originally posted by Peter_1
    [B]Aiyub,
    Sorry, I have to say this but English talking peoples - especially sorry again .....Americans - thinks that the whole world speaks English. Don't forget that the English language is only on the fifth

    Dear Friend,

    I feel what you mean, I migrated to Australia after a Uni education
    and being good in various languages. Upon working in Europe and USA I was always admired about my language knowledge by
    person in which country I worked. Now being 20 years in Austrlia I am asked each time after 2 minutes of talking .Where do you come from and what an accent you still have. Writing papers in a second langauage is difficult but even proper speaking in another language ( not your own) is extremely difficult. Just let people accept what you have to say and do it as good as you can.

    Anybody with comments-- shoulder it of and see it as stuped.

    jg/oz
    jg/oz,
    sunshine coast,
    australia

  18. #18
    Join Date
    Nov 2003
    Location
    NSW, Australia
    Age
    40
    Posts
    243
    Rep Power
    21
    I will give you an example how we Flemish (Dutch speaking part of Belgium) think: if we Belgians go to Spain, we try always to speak Spanish, or Italian in Italy, or German in Germany. We (try) to adapt us to the country we're going. In the first place, we never try to speak our own language in a foreign country, we try to speak their language. If this doesn't work, we then switch to what we think they will understand the best (for example French in Italy) and last to English. And I speak much better English then French and even then, we try it in French.
    you could move to australia peter, the way things are going over here is un-uniform languages... which is really bad. i have the attitude that if you migrate to a country which speaks english, german, bolgarian or whatever language - you should learn or at least try your best to speak the native language, which is english in my case.

    the problem with our country now is we let too many foreigners into our country no questions, which is fair enough if they are willing to adapt to the aussie way of life, or are legit assylum seekers but many are not.

    this causes the majority to segregate themselves from our society and many choose not to adapt into the free aussie way of life and start treating everyone in australia like their native homeland, which is sad because this great country used to provide freedom of speach, freedom of religion, a fair and just go for all. but day by day this is slowerly being erroded away by the ones who take all your handouts and agree to your way of life to get here then bite your arm off once they are.
    "Old fridgies never die, they just run out of gas!"

  19. #19
    Join Date
    Dec 2003
    Location
    Rome Italy
    Age
    56
    Posts
    29
    Rep Power
    0
    hi all....i agree with Peter 1 but don't forget that english speaking people don't really feel the need to learn another language and anyway.......why should they?while it's true that english language ranks 5th it's true that it's the most spread around the globe!To Jay i have to say i really loved his country!The Kilimangiaro is just impressive but i enjoyed other places too!Keeping my fingers crossed i might go there again this year to follow a project in Dar Es Salaam......see you there Jay!

  20. #20
    Join Date
    Mar 2002
    Location
    San Francisco Bay Area
    Posts
    180
    Rep Power
    23
    An expansion valve will (theoretically) close off when the compressor stops.

    A capillary tube system will continue to feed until presssures are equalized. Hot gas in the condenser will migrate to the evaporator and condense, warming the evaporator.

    And regarding the language issue, I appreciate anyone trying to communicate in a second (or more) language, especially one as strange as English.
    Last edited by RogGoetsch; 01-02-2004 at 08:55 AM.

  21. #21
    Join Date
    Jun 2002
    Location
    UK
    Posts
    633
    Rep Power
    23

    Post Display Units

    So jay asked why do TEV cabinets work better than capillary on fluctuations in ambient temperatures

    On capillary a change in load or condensing temperature has a effect on pumping capacity and flow rate in the capillary.Leading to changes in case temperarure.

    The TEV with MOP limits flow at a predetermined rate therefore limiting condensing pressures and keeping refrigerated case temperatures down.Thats the fundamentals.

    Hope this helps jay

    regards mark

  22. #22
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46
    hi mark,

    I think what jay meant is why the temperature in the cases operates with TEV, remains lower then those with cap tube when electricity supply goes off.

    I need more details to come up with more then a guess.

    chemi

  23. #23
    Join Date
    Jun 2002
    Location
    UK
    Posts
    633
    Rep Power
    23

    Post Display Units

    Chemi-cool as we know language over the www is not allways easy .
    A simple explanation is misinterpreted.My post was only intended to aid someone if possible.

  24. #24
    Join Date
    Mar 2002
    Location
    San Francisco Bay Area
    Posts
    180
    Rep Power
    23

    Re: Display Units

    Originally posted by markfiddy
    So jay asked why do TEV cabinets work better than capillary on fluctuations in ambient temperatures

    On capillary a change in load or condensing temperature has a effect on pumping capacity and flow rate in the capillary.Leading to changes in case temperarure.

    The TEV with MOP limits flow at a predetermined rate therefore limiting condensing pressures and keeping refrigerated case temperatures down.Thats the fundamentals.
    Actually, the TEV is able to respond to changes in load, while the cap tube system is not. The cap tube is designed for a given set of conditions and changes in load or condensing temperature have very little effect.

  25. #25
    Join Date
    Nov 2003
    Location
    NSW, Australia
    Age
    40
    Posts
    243
    Rep Power
    21
    its possible the systems are slightly undersized for there proper stand alone application, having them run with the air con on would reduce the heat needed to be removed by the cabinets as well as lower ambient and therefore lower head pressures causing units to operate properly.

    turn air off, heat is too much, raising general ambient temp, therefore raising head pressures resulting in a higher COP and system stuggles to work.

    the system with the TXV would tend to feed more liquid to evap when it sensed a change, becasue it would have the capacity to be able too as more then likely there would be a receiver with spare gas in it. whereas cap tube systems are designed to work within a specific ambient temp range, temp gets too low it could freeze, too high everything gets hotter because it is trying to work outside its design conditions.

    hope this helps a little if you havent counted it out already...
    "Old fridgies never die, they just run out of gas!"

  26. #26
    Join Date
    Mar 2003
    Location
    Tanzania(East Africa)
    Age
    59
    Posts
    27
    Rep Power
    0
    I thank you all for the help, in fact it helped me in solving my problem.
    I had to defend my case in front of engineers from south Africa KOXKA company.
    With all the explanation done it shows that these units were not designed for supermarket. We have this supermarket on sea front, so we have high temp plus humidity causing this display units to fail when we loose aircon support.

    I apologise for my English and thanks a million for all the support .

    Leo 1967: Thankyou. Where r u from?
    Whenever you come over to Tanzania, do get in touch. I am based in Dar-es-salaam
    phone(mobile) # is +255 748 225507

    Regards,
    Jay

  27. #27
    Join Date
    Jun 2002
    Location
    UK
    Posts
    633
    Rep Power
    23

    Post Display Units

    Hi jay
    Im glad you have reached a solution.There are many genuine,methodical,helpfull people who will give advice when needed.Which not all trades have.

    regards mark

  28. #28
    Join Date
    Jun 2002
    Location
    UK
    Posts
    633
    Rep Power
    23

    Re: Re: Display Units

    Originally posted by RogGoetsch
    Actually, the TEV is able to respond to changes in load, while the cap tube system is not. The cap tube is designed for a given set of conditions and changes in load or condensing temperature have very little effect.
    .

    Actually .If the condensing / evaparator temperature rises the flow through capillary remains constant.Raising superheat of vapour and saturated condensing pressure.
    As the condensing pressure rises the flow through the capillary increases ,causing evaparator pressure to rise,decreasing pressure differential across the capillary until the system stabilizes.Reducing sub cooling increases flashing decreasing flow rate until system returns to normal operating conditions.

    regards mark
    Last edited by Mark; 03-02-2004 at 07:31 PM.

  29. #29
    Join Date
    Jun 2002
    Location
    UK
    Posts
    633
    Rep Power
    23

    Post Display Units

    hi marc
    Basically my point was that cabinets working on capillary need a liquid seal at the entrance port .On the event of condenser fan failure or rise in condensing pressure ,would increase flash gas at the capillary.Until flow rate or load returns to normal .
    My opinion was that yes course condensing temperatures have a large effect on how the case operates.
    mark

  30. #30
    Join Date
    Jun 2002
    Location
    UK
    Posts
    633
    Rep Power
    23

    Post Display Units

    marc
    I see what you mean .

  31. #31
    Join Date
    Jun 2002
    Location
    UK
    Posts
    633
    Rep Power
    23

    Post Display Units

    so marc subcooling increases flow rate.
    Flashing reduces flow rate.

    regards mark

  32. #32
    Join Date
    Mar 2002
    Location
    San Francisco Bay Area
    Posts
    180
    Rep Power
    23
    A properly designed cap-tube system is critically charged. Under design conditions, the charge is not large enough to flood back to the compressor.

    The entrance to the capillary loses its liquid seal all the time. Gas bubbles recondense in the first inches as flow slows and the seal is restored. (Most cap tubes are soldered to the suction line or coiled in the evaporator cabinet for this reason.)

    Changes in condensing temperature/pressure change feed rate only minimally for two reasons:

    1) The capillary tube is not a strictly pressure-dependent flow device, as an orifice would be, but as the name suggests, flow is very much dependent on the capillary effect due to the surface tension and surface wetting characterisitics of the molecule within a cylinder whose surface area is maximized while its volume is minimized.

    (For example, capillary action is what allows trees to grow higher than about 33 feet, since that is the highest that water can be elevated by atmospheric pressure at sea level. Redwoods grow many times this height, in part due to the extremely powerful force of capillary action carrying water far above 33 feet.)

    2) There isn't enough refrigerant to feed more than its full-flow design conditions. (See first paragraph.)

    The simple fact is that capillary systems do not respond well to changes in demand. They only do three things well: cool at design conditions, starve the coil at high demand, and flood the coil if the load drops.

    A TEV, on the other hand, can respond to changes in demand by monitoring superheat and increasing the feed rate. This allows the compressor to operate at a higher point on its performance curve to match the demand.

    A TEV with a MOP charged bulb merely limits the top end to prevent a compressor from over-amping when coming out of defrost, for example.

    Hope this helps.

    Rog
    Last edited by RogGoetsch; 04-02-2004 at 06:41 AM.

  33. #33
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46

    Question

    hi marc,

    help me to get wiser: I know the problems with capillary tubes in small refrigeration units but in air condition its a different story, from the smallest split to large rooftop units are all using cap tubes and no problems.

    what is then, the difference between the two if any?

    thanks

    chemi

  34. #34
    Join Date
    Mar 2003
    Location
    Tanzania(East Africa)
    Age
    59
    Posts
    27
    Rep Power
    0
    from the smallest split to large rooftop units are all using cap tubes and no problems.

    what is then, the difference between the two if any?

    as chemi-cool asked above I too am curious to know about it please

  35. #35
    Join Date
    Jun 2002
    Location
    UK
    Posts
    633
    Rep Power
    23

    Re: Display Units

    Originally posted by markfiddy
    so marc subcooling increases flow rate.
    Flashing reduces flow rate.

    regards mark
    marc i was referring to a capillary set up.

  36. #36
    Join Date
    Mar 2002
    Location
    San Francisco Bay Area
    Posts
    180
    Rep Power
    23
    Originally posted by Marc O'Brien

    Rog, lol, capillary action in cap-tubes ?? !! Lol !! That's good humour
    Okay, perhaps a bit of exageration to make a point. I see too many trying to apply the Bernoulli equation and coming up with faulty conclusions.

    Liquid flows through a cap tube easily, while vapor does not. This is the primary design principle of a cap tube.

    AC systems work fine with cap tubes because after initial pull-down, air across the evaporator is almost always within a few degrees of the design value, hence the load remains relatively constant. Perfect for a cap tube.

    It will starve the coil at first if the initial load is high, but that limits compressor amps, keeps condensing pressures in the ball park even on hot days and provides a simpler and lower cost system: no expansion valve or start capacitor on single phase units.
    Last edited by RogGoetsch; 05-02-2004 at 05:44 AM.

  37. #37
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    78
    Posts
    5,072
    Rep Power
    34
    In any discussion of subcooling, it is important to remember that this involves two temperatures, i.e. SCT (saturated condenseing temperature) and liquid temperature. Lower liquid temperature is a good thing. Higher SCT is a bad thing. Therefore it is incorrect to think of increased subcooling as being good or bad. Which of the temps has increased/decreased to increase the subcooling?
    Last edited by Gary; 05-02-2004 at 02:56 PM.

  38. #38
    Join Date
    Jun 2002
    Location
    UK
    Posts
    633
    Rep Power
    23

    Post Display Units

    Rog
    I have just read your thread ,you make some valid points regarding capillary systems.
    The scenario i was explaining was an extreme condition as jay was explaining.
    I have to disagree that single phase units dont need a capacitor when fitted with capillary,i would say a good proportion of equiptment in the uk has capacitor start.One of The only type i have seen that dont require this are chest freezers which have adaquate time off cycle for pressures to equalize.
    I think that our(uk) integral equiptment is made only to cope in cooler ambients Lol
    mark
    Last edited by Mark; 07-02-2004 at 05:46 PM.

  39. #39
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,266
    Rep Power
    46
    hello mark,

    most of commercial compressors from the 1/6 hp comes with a start capacitor for the reasons you have mentioned.

    if they dont, you can add one yourself by using the manufacturer instructions or use supco starting kits.

    these compressors will work fine in high and low ambients, giving them long life.

    chemi

Similar Threads

  1. What units you'll see in your country?
    By nova in forum Transport
    Replies: 25
    Last Post: 07-11-2010, 03:31 PM
  2. Need help with a dual compressor display case
    By kengineering in forum Technical Discussions
    Replies: 15
    Last Post: 15-03-2006, 08:32 PM
  3. AC units as cooling units
    By Peter_1 in forum Commercial
    Replies: 11
    Last Post: 18-03-2005, 07:42 AM
  4. Big Display Case
    By Abe in forum Commercial
    Replies: 4
    Last Post: 02-07-2003, 10:53 PM
  5. Parellel Condensing Units
    By bersaga in forum Technical Speculations
    Replies: 9
    Last Post: 08-05-2003, 02:12 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •