    liquid level in Shell and Tube flooded evaporators



    i know in the ammonia flooded evaporators design there are two methods for liquid and vapor to separate. one is the separation is provided above the tubes in the shell, another is with an auxiliary vessel above the main evaporator.

    the questions are:
    1. if i take the first one, how to decide the liquid level and the tube arrangement in the shell.
    2. if there is an auxiliary vessel, should the tubes arrange all of the shell or also need some space? and the liquid level?
    3. how to calculate the auxiliary vessel?

    is this ok with Froen??

    thanks

    cygbob



  2. #2
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: liquid level in Shell and Tube flooded evaporators

    Hi, cygbob

    Quote Originally Posted by cygbob View Post
    i know.....
    ..... the questions are:
    1. if i take the first one, how to decide the liquid level and the tube arrangement in the shell.
    2. if there is an auxiliary vessel, should the tubes arrange all of the shell or also need some space? and the liquid level?
    3. how to calculate the auxiliary vessel?

    is this ok with Froen??

    thanks

    cygbob
    your question is not easy to answer....just opposite
    please, download and read this...

    http://neatbook.org/w/wolverine%20tu...ata%20book.php

    this one will tell you a lot....almost all
    http://www.engr.iupui.edu/me/courses/shellandtube

    some theory needed in practice...updated 2007... good for learning...

    http://www.wlv.com/products/databook/databook.pdf

    www.wlv.com/products/databook/db3/DataBookIII.pdf

    ...hope you will find all answers you need and some more

    ....hope you will find those links useful....enjoy

    ... of course if this is not enough ..... you can do Google or Google chrome browser ...


    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  3. #3
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: liquid level in Shell and Tube flooded evaporators

    No real easy answers...

    In TEMA (Tubular Exchanger Manufacturers Association) terms,
    BEM is a typical shell and tube design wher you use a separation drum over the exchanger. Typically you will leave the top 2 or 3 rows out of the shell. The vessels will have 2, 3 or 4 risers to connect the shells. Riser design is critical.

    One that has the disengaging area in the sheell can be a BEM that is only 1/2 full of tubes. Ans alternate design is a BEU or BKU, often refered to as a kettle type evaporator. The disadvantage of this type design is the extra refrigerant charge required to flood the tubes.

    On either design, you set the liquid level controller to operate about 2 or 3 rows of tubes below the top of the tubes. The agitation from boiling keeps the top row of tubes wetted at full load and at reduced load, the slight loss of wetter surface doe not matter.

    Next issue is the proper liquid entry into the evaporator...lots written on this, but I prefer a perforated distributor plate below the tubes. Larger vessels may require multiple entries.

    Next is the proper number and design of vapor outlets from the exchanger.

    There is very little written on the design of flooded evaporators and vendors guard their designs. You will probably need to hire an consultant to do the initial designs for you.

    Ken

  4. #4
    Join Date
    Aug 2006
    Location
    CHINA
    Posts
    29
    Rep Power
    0

    Re: liquid level in Shell and Tube flooded evaporators

    thanks all for the useful information.

    i think some of the questions need the experiential knowledge such as in which case you use the auxiliary vessel but not leave many space in the evaporator.

    thanks again!
    cygbob

Similar Threads

  1. Stal Water Cooled Shell & Tube Condensers
    By Samarjit Sen in forum Commercial
    Replies: 2
    Last Post: 18-02-2009, 01:46 AM
  2. What is the purpose of a flooded evaporator?
    By expat in forum Fundamentals
    Replies: 5
    Last Post: 22-02-2008, 02:08 PM
  3. Help!!! Shell and Tube Evap Leak
    By tommy Gun in forum Trouble Shooting
    Replies: 7
    Last Post: 22-07-2007, 12:45 PM
  4. Cryo dryer?
    By Air duster in forum New Technologies
    Replies: 9
    Last Post: 25-04-2007, 09:47 AM
  5. Flooded Systems
    By bernard in forum Industrial
    Replies: 9
    Last Post: 21-07-2005, 01:44 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •