Results 1 to 2 of 2
  1. #1
    Join Date
    Aug 2008
    Location
    California
    Posts
    28
    Rep Power
    0

    Oversize Relief Valve



    I have an oil pot that needs a relief valve. My calculations say I need a relief valve that has at least a 2.5 lb air/min flow. The smallest relief valve I can find is a 11.11 lb air/min but its 10 weeks out! I have a 40 lbs air/min relief valve in stock. The location has no diffusion tank, nor does it have a common relief header. This relief valve will have a separate line that vents to atmosphere.

    Is there a problem if I install this oversize relief valve on this oil pot?

    Dan



  2. #2
    Join Date
    May 2008
    Location
    New York
    Age
    53
    Posts
    93
    Rep Power
    16

    Re: Oversize Relief Valve

    You can do it if your pipe away is sized correctly. Did you check with Cyrus Shank? The 800 has 9.34 lbs/min of air @ 250