electolux GP12TB
hi guys I am new to the site.. can anyone give me some help pls.? actually i am trying to solve a problem with a display bench having an electrolux GP12TB compressor which is continously burning out fuses after about 10 t0 15 min running.. I checked insulation resistance of starting and running coils and it seems to be fine but i noticed that the temp of the comp. itself is quite high while it is blowing up... pls help
-
04-09-2008, 09:22 PM #2
Re: electolux GP12TB
Hi, you need to supply more information to us.
Have you attached gauges? High and Low side pressures? Refrigerant? Is condenser clear of obstruction? Has unit been worked on recently - ie recharged.
What size fuse is blowing? How do you know it is compressor that is breaking down to cause the fuse to blow?
These are a few to start with!
-
05-09-2008, 02:23 AM #3
Re: electolux GP12TB
Is the start relay disengaging?
-
08-09-2008, 04:10 PM #4
Re: electolux GP12TB
10x anyway guys i resolved the problem the compressor was remaining on the the starting coil only...
-
08-09-2008, 06:35 PM #5
Re: electolux GP12TB
Wired up wrong or was it the relay not dis-engaging?
-
21-05-2010, 06:50 AM #6
Re: electolux GP12TB
relay not disengaging