    I'm in the process of designing a new air cooled chiller capable of operating at -20F/-29C brine temperatures. The unit will be air cooled and I would like to use R-410a provided I can find a suitable compressor.

    Capacity target is 10 tons /35kW at -20F/-29C.

    Can anyone recommend a compressor that's capable of this application?



  2. #2
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24
    Not easy. 35kW at -35°C boiling point, 45 to 55°C condensing temperature and 42 bar design pressure....
    Last edited by NoNickName; 04-09-2008 at 08:23 PM.

  3. #3
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: R-410a Compressors

    Why not use R-507? The pressures will be lower , which reduces some of your problems with the compressor selection but also the air-cooled condenser.
    If all else fails, ask for help.


  4. #4
    Crew Chief's Avatar
    Crew Chief Guest

    Re: R-410a Compressors

    R-507 is an option. I was trying to utilize the 410a option because I just designed a new air conditioner platform and wanted to use the same basic components. Also, R-507 requires a little more horsepower than R-410a as well as thermodynamics.

  5. #5
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: R-410a Compressors

    Quote Originally Posted by Crew Chief View Post
    R-507 is an option. I was trying to utilize the 410a option because I just designed a new air conditioner platform and wanted to use the same basic components. Also, R-507 requires a little more horsepower than R-410a as well as thermodynamics.
    OK, how much of an increase will this mean? Can you lower the condensing temperature 1° or so to compensate for it?

    Or, look at the total power (compressor + condenser fans). What kind of options can you find then?

    Air-cooled with R-410 is asking for a challenge... unless the peak ambient temperatures are low enough to allow reasonable discharge pressures.
    If all else fails, ask for help.


  6. #6
    Join Date
    Mar 2005
    Location
    wisconsin usa
    Age
    55
    Posts
    13
    Rep Power
    0

    Re: R-410a Compressors

    Im not sure you will find a 410a compressor for this application. Instead of 507, I would go with 404a which is essentially the same refrigerant except that 404a has 134a added to control discharge pressure. The 134a in the mix does not affect evaporator performance much at all as it is a much lower pressure refrigerant.

  7. #7
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: R-410a Compressors

    We've got these: http://www.frascold.it/pdf/CATALOGUES/FCAT22-01.pdf but you will need to build a rack and have liquid injection or head fan.

Similar Threads

  1. Compressors - screw or reciprocating?
    By Josip in forum Industrial Compressors
    Replies: 18
    Last Post: 27-01-2009, 10:36 PM
  2. FES screw compressors
    By negmy13 in forum Technical Speculations
    Replies: 0
    Last Post: 08-08-2008, 07:40 AM
  3. New types of Refrigeration Compressors
    By adjohnson208 in forum New Technologies
    Replies: 3
    Last Post: 03-07-2008, 07:35 PM
  4. Do we have some expert in replacing compressors
    By Zahid in forum Air Conditioning
    Replies: 2
    Last Post: 01-07-2008, 07:59 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •