    Hi all, I have a qestion about when is best to take your superheat readings to set your TX valve. I have a freezer that is set at -25c, Lets say the ambient temperature +30c when the freezer is turned on, as it starts to cool down when should i be taking my superheat readings?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: TX Troubles

    When the freezer is at -25°C.

    Do NOT adjust the TXV unless absolutely necessary.

    A search on this forum will find a great range of discussions on superheat and not adjusting the TXV.

    http://www.refrigeration-engineer.co...ight=superheat

    http://www.refrigeration-engineer.co...ad.php?t=11903
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: TX Troubles

    That also applies to fixed metering devices always at the control set point.

  4. #4
    440hardtop's Avatar
    440hardtop Guest

    Re: TX Troubles

    If it isn't to much hassle could somenoe explain to me why this is the best time to check your superheat?

  5. #5
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: TX Troubles

    The whole point in using a TXV is to have high refrigerant flow when the refrigerated space temp is high and low refrigerant flow when the space temp is low.

    The refrigerant flow can only be high when the superheat is high and can only be low when the superheat is low.

    High space temp = high flow = high superheat.

    Low space temp = low flow = low superheat.

    Normal space temp = normal flow = normal superheat.

    You should expect to have design superheat only when you have design space temperature.
    Last edited by Gary; 04-09-2008 at 01:10 PM.

  6. #6
    440hardtop's Avatar
    440hardtop Guest

    Re: TX Troubles

    Cheers Gary, ive had it explained to me before but never had it put that simply, it's all making sense now. Thanks again.

  7. #7
    Join Date
    Jun 2007
    Location
    saskatchewan
    Age
    56
    Posts
    70
    Rep Power
    17

    Re: TX Troubles

    From what I have read,around 10f evaporator superheat is good.Some say to shoot for 20f sh at compressor.Others say that 20f at compressor is not important as long as you have some sh at the compressor.
    Last edited by cretan; 05-09-2008 at 10:38 AM.

  8. #8
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: TX Troubles

    Quote Originally Posted by cretan View Post
    From what I have read,around 10f evaporator superheat is good.Some say to shoot for 20f sh at compressor.Others say that 20f at compressor is not important as long as you have some sh at the compressor.
    TXV superheat should always be adjusted according to evaporator outlet superheat.

    Compressor manufacturers want at least 15-20F superheat at the compressor inlet. Proper superheat at the evap outlet will generally result in sufficient superheat at the compressor inlet.

    But that isn't the whole story. Many compressors are refrigerant cooled, so high superheat at the compressor inlet can also be a problem.

    If the TXV is adjusted for proper evap outlet superheat and the compressor inlet superheat is high, then better suction line insulation and/or mechanical de-superheating may be needed.

    The TXV should never be adjusted to achieve compressor inlet superheat, but rather to achieve evap outlet superheat.
    Last edited by Gary; 06-09-2008 at 07:02 PM.

  9. #9
    Join Date
    Mar 2008
    Location
    johannesburg, south africa
    Age
    42
    Posts
    18
    Rep Power
    0

    Re: TX Troubles

    Hie,first time post. Iwould like to ask
    1.what is definition of sensible heat of an air handling unit (chilled water) and how do you determine it?

  10. #10
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: TX Troubles

    Quote Originally Posted by oupak View Post
    Hie,first time post. Iwould like to ask
    1.what is definition of sensible heat of an air handling unit (chilled water) and how do you determine it?
    http://www.daikin.co.uk/faq/items/se...atent-heat.jsp

Similar Threads

  1. Hussmann 2 Dr Frzr Troubles
    By daddyfixit in forum Trouble Shooting
    Replies: 15
    Last Post: 14-01-2009, 05:57 AM
  2. Copeland Oil Migration/Pressure Troubles
    By daddyfixit in forum Trouble Shooting
    Replies: 12
    Last Post: 18-04-2008, 12:53 PM
  3. Chiller Troubles
    By Stiff Nipples in forum Supermarket Refrigeration
    Replies: 9
    Last Post: 15-03-2008, 06:32 AM
  4. furnace troubles
    By t-bone in forum Technical Discussions
    Replies: 5
    Last Post: 05-02-2007, 04:20 AM
  5. Ice machine troubles
    By bfarmer in forum Trouble Shooting
    Replies: 18
    Last Post: 10-01-2007, 09:12 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •