    Hi.
    I am trying to find out what gas & how much, & which gas to have my old compressor (in a soft serve ice cream machine) re-gassed.
    The manufacturer of the machine have been less than helpful.
    It is a DORIN:- T100S-M R12
    Any advice on how much or where to look would be appreciated.
    11,025
    Re: Dorin Compressor re-gas amount
    How much is a tricky question.
    Which gas? have a look at the expansion valve, it should have a label on it. Although, to be honest, you have already answered that question with your compressor information. You'll have to find an alternative refrigerant for it.
    A capable technician should be able to answer those questions for you when he recommissions it.
    desserts's Avatar
    desserts Guest
    He has suggested r406a but he said that the system has a "critical charge?" & he did not know exactly how much to put in as to much, or too little will effect the freezing capabilities.
    Somerset
    69
    4,697
    desserts.
    You say the manufacturer of the machine is unhelpful.
    How about letting us know what the machine is, because we are all about helping.
    If anyone has any info.
    I am sure they will help!
    desserts's Avatar
    desserts Guest
    Thanks for the replies.
    The machine is a Carpigiani Superbareco 1AP & all the information I can find on the machine & compressor is listed below.
    Ice Cream Machine
    Compressor Information
    Dorin
    T100S-M R12
    HP 1 V 220
    A Cos
    SUNISO OIL 3G KG 0.7
    Aug 2008
    5
    Hi desserts,
    Wow this one is from the ark....should have mock wood effect on vinyl sides and weighs a ton!!!
    Is an R12 system so you could use a drop in for this FX56 or alike. System requires 550g but if you have the sight glass on here it can be charged to this; but only in the production mode whilst ice cream is in the machine cylinder.
    Good luck!
  1. oil amount in mobile refrigeration system
    By freezingfan in forum Transport
    Last Post: 15-04-2008, 08:44 AM
  2. Dorin Semi hermetic Compressor
    By Samarjit Sen in forum Industrial Compressors
    Last Post: 02-07-2007, 04:06 PM
  3. optimize tube amount
    By hammurabi in forum Technical Speculations
    Last Post: 12-09-2006, 02:13 AM
  4. about the refrigerant fill amount
    By hammurabi in forum Refrigeration Books
    Last Post: 31-07-2006, 10:24 AM
  5. Rule of Thumb on Refrigerant Amount
    By rickmor in forum Refrigerants
    Last Post: 19-12-2005, 11:18 AM