    Dorin Compressor re-gas amount



    Hi.
    I am trying to find out what gas & how much, & which gas to have my old compressor (in a soft serve ice cream machine) re-gassed.
    The manufacturer of the machine have been less than helpful.
    It is a DORIN:- T100S-M R12
    Any advice on how much or where to look would be appreciated.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Dorin Compressor re-gas amount

    How much is a tricky question.

    Which gas? have a look at the expansion valve, it should have a label on it. Although, to be honest, you have already answered that question with your compressor information. You'll have to find an alternative refrigerant for it.

    A capable technician should be able to answer those questions for you when he recommissions it.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    desserts's Avatar
    desserts Guest

    Re: Dorin Compressor re-gas amount

    He has suggested r406a but he said that the system has a "critical charge?" & he did not know exactly how much to put in as to much, or too little will effect the freezing capabilities.

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,698
    Rep Power
    46

    Re: Dorin Compressor re-gas amount

    desserts.
    You say the manufacturer of the machine is unhelpful.
    How about letting us know what the machine is, because we are all about helping.
    If anyone has any info.
    I am sure they will help!
    Grizzly

  5. #5
    desserts's Avatar
    desserts Guest

    Re: Dorin Compressor re-gas amount

    Thanks for the replies.
    The machine is a Carpigiani Superbareco 1AP & all the information I can find on the machine & compressor is listed below.

    Ice Cream Machine

    Carpigiani Superbareco 1AP

    Compressor Information

    Dorin
    T100S-M R12
    HP 1 V 220
    A Cos
    SUNISO OIL 3G KG 0.7

  6. #6
    Join Date
    Aug 2008
    Location
    UK
    Posts
    5
    Rep Power
    0

    Re: Dorin Compressor re-gas amount

    Hi desserts,

    Wow this one is from the ark....should have mock wood effect on vinyl sides and weighs a ton!!!
    Is an R12 system so you could use a drop in for this FX56 or alike. System requires 550g but if you have the sight glass on here it can be charged to this; but only in the production mode whilst ice cream is in the machine cylinder.

    Good luck!

Similar Threads

  1. oil amount in mobile refrigeration system
    By freezingfan in forum Transport
    Replies: 9
    Last Post: 15-04-2008, 08:44 AM
  2. Dorin Semi hermetic Compressor
    By Samarjit Sen in forum Industrial Compressors
    Replies: 5
    Last Post: 02-07-2007, 04:06 PM
  3. optimize tube amount
    By hammurabi in forum Technical Speculations
    Replies: 17
    Last Post: 12-09-2006, 02:13 AM
  4. about the refrigerant fill amount
    By hammurabi in forum Refrigeration Books
    Replies: 12
    Last Post: 31-07-2006, 10:24 AM
  5. Rule of Thumb on Refrigerant Amount
    By rickmor in forum Refrigerants
    Replies: 7
    Last Post: 19-12-2005, 11:18 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •