    how to use a refrigerant comparator



    Hi,

    looking for guide on how to use a refrigerant comparator for working out suction pressure on all systems .



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: how to use a refrigerant comparator

    Why do you want to work out the suction pressure for all systems?

  3. #3
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: how to use a refrigerant comparator

    Quote Originally Posted by ActiveEngineer View Post
    Hi,

    looking for guide on how to use a refrigerant comparator for working out suction pressure on all systems .

    Your question is too vauge.

    A comparator only converts pressure to temp or temp to pressure for the refrigerant you are using.

    So you fit your gauges and read the pressure. You then slide the comparator along untill the line is at the same pressure displayed on your gauges. You then look up the refrigerant you want and where the line intersects the refrigerant line you have your temp.

    You will have different pressures if you have different temps.

    taz.

  4. #4
    Join Date
    Aug 2008
    Location
    UK
    Posts
    19
    Rep Power
    0

    Re: how to use a refrigerant comparator

    Is there know such guide?

    looking find out how you work out what the suction pressure/tempature

    For the likes of a HVAC system running on r59 what suction tempaturte would be and how you work it out


    Hope i have come over bit better this time cheers for any help you guys can give me

  5. #5
    Join Date
    Oct 2006
    Location
    England
    Posts
    1,843
    Rep Power
    21

    Re: how to use a refrigerant comparator

    Quote Originally Posted by ActiveEngineer View Post
    Is there know such guide?

    looking find out how you work out what the suction pressure/tempature

    For the likes of a HVAC system running on r59 what suction tempaturte would be and how you work it out


    Hope i have come over bit better this time cheers for any help you guys can give me

    Active Engineer.

    Have you ever done any training?

    I ask because the information you are asking for does not exist (not in the form you want) but you would know that if you had any training.

    Why don't you introduce yourself and explain what you want. We can work from that point and perhaps give you some assistance.


    taz

    .
    Last edited by taz24; 20-09-2008 at 08:31 PM.

  6. #6
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: how to use a refrigerant comparator

    Quote Originally Posted by ActiveEngineer View Post
    Hi,

    looking for guide on how to use a refrigerant comparator for working out suction pressure on all systems .
    Hi Active, Have a look at this site
    http://www.marineair.com/pdfs/L-2270.pdf, found by Google

    Norm
    My wife used to say you never listen to a word I say at least I think that what she said

  7. #7
    Join Date
    Aug 2008
    Location
    UK
    Posts
    19
    Rep Power
    0

    Re: how to use a refrigerant comparator

    Quote Originally Posted by taz24 View Post
    Active Engineer.

    Have you ever done any training?

    I ask because the information you are asking for does not exist (not in the form you want) but you would know that if you had any training.

    Why don't you introduce yourself and explain what you want. We can work from that point and perhaps give you some assistance.


    taz

    .



    Hello Taz,

    I am a mechical tech and i work offshore in the north sea and have know refrigeration training at all.

    Like my other questions i would like to know how you guys work out the suction pressure/temperature of systems.

    suction pressure/temperature of a HVAC system running on R59 would be ?

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: how to use a refrigerant comparator

    Quote Originally Posted by ActiveEngineer View Post

    Like my other questions i would like to know how you guys work out the suction pressure/temperature of systems.

    suction pressure/temperature of a HVAC system running on R59 would be ?

    You need to know design TD (difference between evaporation temperature and air/water/brine entering temperature) for your heat exchanger.
    Subtract evaporator design TD from evaporator actual air/water/brine entering temp to obtain required evaporation temperature, and add condenser design TD to actual entering air/water/brine temperature to that condenser to obtain condensation temperatures.
    Then convert that temperatures to saturation temperatures of refrigerant in system and you have your expected pressures. Now compare that with your measured pressures (or temperatures, if gauge has scale in temp. for that refrigerant) to establish is your system pressures are OK.

    http://www.refrigeration-engineer.co...ighlight=table
    Last edited by nike123; 21-09-2008 at 01:47 PM.

  9. #9
    Join Date
    Aug 2008
    Location
    UK
    Posts
    19
    Rep Power
    0

    Re: how to use a refrigerant comparator

    This helps alot mate thank you very much.

  10. #10
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: how to use a refrigerant comparator

    It's not about pressures.

    You convert the pressures to temperatures, but it's not about temperatures, either.

    It is about temperature differences, i.e. subtracting one temperature from another temperature (subcooling, superheat, TD's, dT's, approaches, etc.). Any single pressure/temperature, by itself, tells you nothing useful about the system.

  11. #11
    Join Date
    Aug 2008
    Location
    UK
    Posts
    19
    Rep Power
    0

    Re: how to use a refrigerant comparator

    Still looking for help regarding this matter..

    Maybe i did not explain my self to well the first time..

    What i would like to know is how suction pressure are related to operating tempatures.

    For example,

    A freezer with operating tempature of -21c, running on R404a with a suction pressure of 1 bar/14.7psi.

    I checked a comparator and for that pressure that would give you a lp vapour tempature of -32c... i think.

    So would that give you a 11 diff in tempature.

    So is there a simple rule of thumb to follow when trying to work out suction pressure from your operating tempatures and is it the same for all refrigerant.

    Hope this explains it better this time.

  12. #12
    Join Date
    Aug 2001
    Location
    Gold Coast, Australia
    Posts
    600
    Rep Power
    28

    Re: how to use a refrigerant comparator

    Basically for heat to flow, there must be a temperature difference. So to absorb heat in the evaporator, the temperature of the refrigerant must be 6 deg. or more less than the temperature of what you're cooling. Any less would be inefficient. And obviously to reject heat from the condenser, the cooling medium must be colder than the refrigerant temperature, again by at least 6 deg.
    It's many years sisnce I used R404a & LT systems, but the -32 for -21 case temp sounds right to me.

    Hope that helps.

  13. #13
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: how to use a refrigerant comparator

    I would add that TD is primarily a matter of coil sizing. A larger coil transfers heat faster resulting in a lower TD. A smaller coil transfers heat slower resulting in a higher TD.

  14. #14
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: how to use a refrigerant comparator

    maybe you need to download the "coolpack" program,and play a bit. you put in some numbers and it will calculate the outcom for you. you learn a thing or two.

    Ice

  15. #15
    Join Date
    Jan 2006
    Location
    Croatia
    Age
    68
    Posts
    2,263
    Rep Power
    31

    Re: how to use a refrigerant comparator

    Hi, ActiveEngineer

    Quote Originally Posted by icecube51 View Post
    maybe you need to download the "coolpack" program,and play a bit. you put in some numbers and it will calculate the outcom for you. you learn a thing or two.

    Ice
    you should download above mentioned program, and under CoolTools:Auxiliary you can find

    "COMPARISON OF REFRIGERANTS .... Comparison of three refrigerants in a simple refrigeration cycle" ...

    ... of course there is much more, then a thing or two, to learn

    Best regards, Josip

    It's impossible to make anything foolproof because fools are so ingenious...

    Don't ever underestimate the power of stupid people when they are in large groups.

    Please, don't teach me how to be stupid....
    No job is as important as to jeopardize the safety of you or those that you work with.

  16. #16
    Join Date
    Dec 2008
    Location
    manchester
    Age
    36
    Posts
    5
    Rep Power
    0

    Re: how to use a refrigerant comparator

    Quote Originally Posted by ActiveEngineer View Post
    Still looking for help regarding this matter..

    Maybe i did not explain my self to well the first time..

    What i would like to know is how suction pressure are related to operating tempatures.

    For example,

    A freezer with operating tempature of -21c, running on R404a with a suction pressure of 1 bar/14.7psi.

    I checked a comparator and for that pressure that would give you a lp vapour tempature of -32c... i think.

    So would that give you a 11 diff in tempature.

    So is there a simple rule of thumb to follow when trying to work out suction pressure from your operating tempatures and is it the same for all refrigerant.

    Hope this explains it better this time.

    usually you would be looking for a superheat (your TD) of around 7 degrees c, preferably 5 on freezer / cold store. it all depends on if its on a DX (direct expansion), fixed orifice, or capilary system.

    but 1 bar on 404a sounds right to me

  17. #17
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: how to use a refrigerant comparator

    Quote Originally Posted by murphyboy View Post
    usually you would be looking for a superheat (your TD) of around 7 degrees c, preferably 5 on freezer / cold store. it all depends on if its on a DX (direct expansion), fixed orifice, or capilary system.

    but 1 bar on 404a sounds right to me
    Would that be during pull down or approaching set point?

  18. #18
    Join Date
    May 2008
    Location
    Belgium
    Age
    66
    Posts
    802
    Rep Power
    16

    Re: how to use a refrigerant comparator

    look at the date of last post guy's.
    and he never told anyone if he has learnd a thing (or two) ;-))

    Ice

  19. #19
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: how to use a refrigerant comparator

    September 2008 was a good month, original post date people.

  20. #20
    Join Date
    Aug 2008
    Location
    UK
    Posts
    19
    Rep Power
    0

    Re: how to use a refrigerant comparator

    Boys and girls where can i find this cool pack program.

  21. #21
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: how to use a refrigerant comparator

    Quote Originally Posted by ActiveEngineer View Post
    Boys and girls where can i find this cool pack program.
    Ar you sure that you are active?
    http://tinyurl.com/32u4a3k

  22. #22
    Join Date
    Aug 2008
    Location
    UK
    Posts
    19
    Rep Power
    0

    Re: how to use a refrigerant comparator

    Quote Originally Posted by nike123 View Post
    Ar you sure that you are active?
    http://tinyurl.com/32u4a3k

    Ha ha ha funny guy how cool is that, I like it.

    Cheers for the info tho. don't really get on here to much as you can tell by my posts

    Still don't really understand how you guys work out the suction pressure/temperature. like I said above I never served my time as refrigeration engineer so was just looking for a ball park figure.

  23. #23
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: how to use a refrigerant comparator

    Quote Originally Posted by ActiveEngineer View Post
    Ha ha ha funny guy how cool is that, I like it.

    Cheers for the info tho. don't really get on here to much as you can tell by my posts

    Still don't really understand how you guys work out the suction pressure/temperature. like I said above I never served my time as refrigeration engineer so was just looking for a ball park figure.
    You seems to not reading carefully!
    Everything is alredy explained in this thread.
    There is no simple way by looking in thumb and aligning it with evaporator bottom line. We must measure some temperatures, consider some factors, than we came with expected value for evaporation temperatures and than we convert that in pressures for refrigerant in question.

  24. #24
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: how to use a refrigerant comparator

    Quote Originally Posted by ActiveEngineer View Post
    Still don't really understand how you guys work out the suction pressure/temperature. like I said above I never served my time as refrigeration engineer so was just looking for a ball park figure.
    If you know the pressure it tells you the temperature. If you know the temperature, it tells you the pressure.

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 01:24 AM
  2. Leak Testing?
    By Thana in forum Trouble Shooting
    Replies: 36
    Last Post: 31-08-2010, 02:57 PM
  3. CARE refigerants by BOC
    By dogma in forum Refrigerants
    Replies: 8
    Last Post: 23-03-2010, 12:39 PM
  4. MHI FDCA400HKXRE4 Tech Info Please
    By L.JT in forum Trouble Shooting
    Replies: 5
    Last Post: 23-08-2008, 11:00 PM
  5. fun quiz
    By Brian23 in forum New to RE
    Replies: 6
    Last Post: 02-10-2007, 10:18 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •