    hi guys:

    I dont know how can i calcute the refrigerated load for a room is not rectangle, i attach the room's drawing. i have i program for selection but my program only calculates rectangle room. please help me.
    Attached Files Attached Files



  2. #2
    Join Date
    Nov 2005
    Location
    New Zealand
    Posts
    550
    Rep Power
    19

    Re: refrigerated load

    Hi, you can calculate it by making numerous rectangles then add them up

    regards Norm
    My wife used to say you never listen to a word I say at least I think that what she said

  3. #3
    Join Date
    Apr 2008
    Location
    Kent
    Age
    41
    Posts
    68
    Rep Power
    17

    Re: refrigerated load

    surely that drawings not for one of your own jobs?

  4. #4
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: refrigerated load

    This is a good example of why it is important to understand how the calculations work. This example does not fit the parameters of the software, so the software is not entirely useful.

    The simplest way to solve this is to break up the areas into individual spaces/areas. Then sum the sub-totals of the individual spaces/areas.
    If all else fails, ask for help.


  5. #5
    Join Date
    Feb 2008
    Location
    Lima - Peru
    Age
    41
    Posts
    49
    Rep Power
    0

    Re: refrigerated load

    US ICEMAN

    thanks a lot, but i have a question for calculate the refrigerated load i need to know the temperature outside the room.
    if i broke the area in several rectangles and i'm going to solve one. what temperature should i consider on the side that is inside the room? i think the temperature of the room. is that correct?.....

  6. #6
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: refrigerated load

    If one of the walls of the imaginary rectangle is exposed to the inside temperature of the space, the heat load for that wall is zero. The temperature is the same on both sides of the wall.
    If all else fails, ask for help.


  7. #7
    Join Date
    Aug 2008
    Location
    Englewood, CO
    Posts
    23
    Rep Power
    0

    Re: refrigerated load

    With a little trial and error you could make an equivalent rectangle with the same total area and the same perimeter. Then, feed these dimensions into the formula.

  8. #8
    Join Date
    Feb 2008
    Location
    Las Vegas, NV
    Age
    67
    Posts
    330
    Rep Power
    17

    Re: refrigerated load

    luissan,

    I agree with the others with one exception.

    This looks like a large warehouse storage facility. If my conversions are correct, the bottom vertical rectangle is approximately 27ft x 118ft x 29ft with dock doors.

    I would run at least two, if not three separate loads: bottom section, top right section and top left section.

    If that is dock doors on the bottom section, the air infiltration load will be high compared to the other sections.

    If your not comfortable running a load on this box, get some more experienced help. There will be extra load factors to consider ie: fork lifts, people (100), heat producing equipment if applicable, humidity conditions for a working enviroment, dock door factors (air curtains and usage time) etc.
    Last edited by powell; 02-09-2008 at 08:07 PM.

  9. #9
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: refrigerated load

    Another point to be aware of is; the cooling capacity will have to be installed in the space to meet the requirements of the separate areas. The areas where the dock doors are located will have a significantly higher load than other areas. Therefore you will find these areas have the greatest concentration of cooling capacity that needs to be installed.

    If not, then some areas may be unable to maintain the desired temperatures.
    If all else fails, ask for help.


  10. #10
    Join Date
    Oct 2005
    Location
    Romania
    Posts
    44
    Rep Power
    0

    Re: refrigerated load

    Hi , luissandoval
    You want to calculate the refrigeration load ( for coldroom ) or cooling load ( for conditioning area ) ? !4 C deg. means conditioning not refrigerations . Please , send us more informations .
    Gramcor

  11. #11
    Join Date
    Feb 2008
    Location
    Lima - Peru
    Age
    41
    Posts
    49
    Rep Power
    0

    Re: refrigerated load

    Gramcor:

    I want to calculate the refrigeration load for conditioning area.

  12. #12
    Join Date
    Oct 2005
    Location
    Romania
    Posts
    44
    Rep Power
    0

    Re: refrigerated load

    Hi , luissandoval
    If you have coldroom , you must calculate only refrigerations load. If you have conditionning , you must calculate cooling load and fresh air change for 100 persons ( about 20 - 40 mc / h per each person.
    gramcor

  13. #13
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: refrigerated load

    Multiply the U factor of walls and ceiling with the total surface and multiply it with the temperature difference and add the heat load of the products.
    That's it. Simply, isn't it.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. Heat transfer coefficient - Coolpack
    By Graham in forum Fundamentals
    Replies: 10
    Last Post: 28-05-2008, 01:08 AM
  2. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  3. How is load divided between indoor units
    By mchild in forum Air Conditioning
    Replies: 26
    Last Post: 17-01-2008, 10:30 PM
  4. How to Design Refrigerated Cabinets
    By Rayin in forum Fundamentals
    Replies: 5
    Last Post: 26-11-2006, 08:27 AM
  5. AKV versus higher load
    By Peter_1 in forum Industrial
    Replies: 20
    Last Post: 18-04-2004, 11:05 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •