    Trouble w/walk-in freezer Help!



    Looking for some advice regarding a walk-in freezer, that is running warn @ 22* F.

    Situation is as follows: suction line is iced up from evaporator to accumulator and compressor, there is no CPR on this unit, pressures are 245 (high) and 38 (low) sides. I measured approx. 41* superheat, by using gauges and thermocouple.

    This unit is a 2 H.P. copeland compressor, R-502 one of the guys decided it was the TXV and tinkered with the setting, then finally replaced the TXV.

    The unit has been defrosted many times and the defrost timer is functional, also the unit runs continously, unless the defrost timer is telling it to shutdown at its proper time.

    Any Ideas?

    Filter/drier? pressure control? compressor?

    Thanks so much!

    John



  2. #2
    rasheed2323's Avatar
    rasheed2323 Guest

    Re: Trouble w/walk-in freezer Help!

    TXV may requered fine tuning

  3. #3
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: Trouble w/walk-in freezer Help!

    CK for low amps and the difference in temperature between the condenser temperature and the ambient air the “Condensing Split,” and it should run from 25-30˚ on standard-efficiency condensers under normal heat loads you may have bad valves

  4. #4
    Join Date
    Feb 2007
    Location
    newcastle but now carlisle
    Age
    53
    Posts
    195
    Rep Power
    18

    Re: Trouble w/walk-in freezer Help!

    Do a pump test on the comp. see if it can pull and hold a vac. txv may be ok could be the comp ?

  5. #5
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: Trouble w/walk-in freezer Help!

    Well before you play with it, after reading some horror stories here and elsewhere, have you considered the fact that it's not built right?
    Maybe get some history on the install and equipment, do a heat load calc and check the evap, compressor and the rest of the gear is up to the job.

  6. #6
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Trouble w/walk-in freezer Help!

    I hate it when people tell me pressures instead of temperatures. They are forcing me to dig out my P/T chart. I don't care what the pressures are. I want to know what the corresponding temperatures are.
    Last edited by Gary; 01-09-2008 at 05:26 PM.

  7. #7
    jreding's Avatar
    jreding Guest

    Re: Trouble w/walk-in freezer Help!

    Thanks for the responses I will look more into it, If i remember correctly its about 8* low and 105* high.

    its located, (of course in the most god awful space) on top of the freezer, ( 2' of clearance in top).

    They did put a fresh air intake into the area, via a st of louvers through the exterior wall.

    Thanks again.

    John

  8. #8
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Trouble w/walk-in freezer Help!

    Quote Originally Posted by jreding View Post
    Thanks for the responses I will look more into it, If i remember correctly its about 8* low and 105* high.

    its located, (of course in the most god awful space) on top of the freezer, ( 2' of clearance in top).

    They did put a fresh air intake into the area, via a st of louvers through the exterior wall.

    Thanks again.

    John
    If the SST is 8F and the superheat is 41F, then the suction line must be 49F. Yet you are saying that the suction line is frosted. How is that possible?

  9. #9
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Trouble w/walk-in freezer Help!

    For a proper evaluation, we need the following information:

    Low side:

    Evap air in temp
    Evap air out temp
    Saturated suction temp (SST) converted from pressure
    Suction line temp at evap outlet

    High side:

    Cond air in temp
    Cond air out temp
    Saturated condensing temp (SCT) converted from pressure
    Liquid line temp at receiver outlet

  10. #10
    shawn626's Avatar
    shawn626 Guest

    Re: Trouble w/walk-in freezer Help!

    does the compressor pump down into a vacuum if you front seat the suction service valve?. aslo is there a low pressure control used as a safety that ma be set above the required sst?.

Similar Threads

  1. ice cream truck freezer
    By GaryC in forum Transport
    Replies: 7
    Last Post: 06-12-2008, 02:19 AM
  2. Hotpoint FFA71 Freezer High Temp Light / Fridge is Freezing
    By sumnerpa in forum Trouble Shooting
    Replies: 1
    Last Post: 19-08-2008, 03:16 PM
  3. Freezer compressor running 20 Hours/day
    By rickcw in forum Domestic
    Replies: 12
    Last Post: 08-03-2008, 11:50 PM
  4. Trolley freezer & blast freezer
    By smpsmp45 in forum NH3
    Replies: 0
    Last Post: 25-08-2007, 07:29 AM
  5. Project needs a freezer box.
    By NC-Joey in forum Fundamentals
    Replies: 14
    Last Post: 16-08-2007, 01:27 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •