    Question Daikin Ducted Commission Probs



    I have just installed a daikin split ducted and am having problems with the setup process. The units are a RQ200KY1 / FDYQN200KV1.I have wired it up as follows. Three phase supply to ODU, Single phase supply picked up from the three phase on the ODU and run via a circuit breaker to terminal block on IDU, pair wires from F1/F2 on ODU to F1/F2 on indoor unit and a shielded pair from terminals P1/P2 on indoor unit supplying 16 volt supply to stat ( BRC1D61 ). The problem I am having is that I am unable to get the stat to operate the unit. It has a UH fault that I am unable to clear, the icon indicating that the stat is being over riden is displayed and the green LED on the outdoor unit pcb is indicating that the unit is operating as a multi split. Any suggestions would be appreciated.



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Daikin Ducted Commission Probs

    Not familiar with this specific model...(and can't get to a manual until tomorrow)

    But, UH indicates a communication fault between outdoor units.

    Without knowing the layout of the outdoor terminals, are you sure all communication cables are in the right terminals?

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Daikin Ducted Commission Probs

    The fault code UH refers to:

    "Improper connection of transmission wiring between outdoor and outdoor unit outside control adapter."

    Have you got and outside adapter fitted? (you must have because you have the 'Centralised Control' symbol displayed)

    Check your wiring.

  4. #4
    jdkmj's Avatar
    jdkmj Guest

    Re: Daikin Ducted Commission Probs

    re ran interconnecting wiring between idu and odu, replacing tps pairwire with twin shielded. Prob now fixed

  5. #5
    Join Date
    Apr 2008
    Location
    australia
    Age
    58
    Posts
    47
    Rep Power
    0

    Re: Daikin Ducted Commission Probs

    Quote Originally Posted by jdkmj View Post
    I have just installed a daikin split ducted and am having problems with the setup process. The units are a RQ200KY1 / FDYQN200KV1.I have wired it up as follows. Three phase supply to ODU, Single phase supply picked up from the three phase on the ODU and run via a circuit breaker to terminal block on IDU, pair wires from F1/F2 on ODU to F1/F2 on indoor unit and a shielded pair from terminals P1/P2 on indoor unit supplying 16 volt supply to stat ( BRC1D61 ). The problem I am having is that I am unable to get the stat to operate the unit. It has a UH fault that I am unable to clear, the icon indicating that the stat is being over riden is displayed and the green LED on the outdoor unit pcb is indicating that the unit is operating as a multi split. Any suggestions would be appreciated.

    Have you test run the system. You will get a uh fault if you don,t.

    martin

  6. #6
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Daikin Ducted Commission Probs

    Please read post above yours....
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  7. #7
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: Daikin Ducted Commission Probs

    it seems that you had run the comms with the 240 volt cable and there was induced voltage in the cable, this is why you lost the communications.

Similar Threads

  1. Daikin 4MX80HV1NB probs...
    By eggs in forum Air Conditioning
    Replies: 14
    Last Post: 21-07-2011, 07:48 PM
  2. Daikin not working... many problems
    By stankovicv in forum Air Conditioning
    Replies: 26
    Last Post: 11-12-2010, 09:01 AM
  3. Daikin ducted unit, never worked properly
    By Apples in forum Air Conditioning
    Replies: 15
    Last Post: 28-06-2009, 12:59 AM
  4. Problem with ducted Daikin
    By jutty in forum Trouble Shooting
    Replies: 8
    Last Post: 23-07-2007, 05:34 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •