    YORK YAEP recip chiller fault



    Has anyone ever come accross the following fault on a York Millennium:REPROGRAM TYPE OF REFRIGERANT TO RUN?
    The original fault was a current/mp/hp and after checking the hp/mp circuit, the CT, the contactors, and changing the relay board... the Microprocessor board was replaced (swaptronic troubleshooting) and the old EPROM chip was moved to new board. As soon as this was done and unit powered up, the REPROGRAM fault occured. Now even with putting the old board back in it still shows the Reprogram fault.
    I'm pulling my hair out on this one.



  2. #2
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: YORK YAEP recip chiller fault

    Quote Originally Posted by chiller1 View Post
    Has anyone ever come across the following fault on a York Millennium:REPROGRAM TYPE OF REFRIGERANT TO RUN?
    The original fault was a current/mp/hp and after checking the hp/mp circuit, the CT, the contactors, and changing the relay board... the Microprocessor board was replaced (swaptronic troubleshooting) and the old EPROM chip was moved to new board. As soon as this was done and unit powered up, the REPROGRAM fault occured. Now even with putting the old board back in it still shows the Reprogram fault.
    I'm pulling my hair out on this one.
    Welcome chiller1.
    We are honoured have a member of the USA. Air force on line!


    Basically what has happened is when replacing the board or the eprom.
    You need to tell the software what refrigerant is being used , on that particular chiller.
    As I think there are possibly 4 different refrigerant options.

    Do you know of an York or ex York Engineer? Because you need someone with the relevant access codes.
    To reset the relevant software settings lost whilst "powering down" the micro board.
    If you don't have access to this info or a suitably trained Engineer.
    Then your only option is to call out York (now known as Johnson Controls)!

    Cheers Grizzly

  3. #3
    chiller1's Avatar
    chiller1 Guest

    Re: YORK YAEP recip chiller fault

    Thanks Grizzly,
    I was afraid it was something like that. unfortunately, although I am stationed out of the UK (Mildenhall) I am currently in Qatar and site access is extremely limited. I will have to see if the crazy people with the money will let me take the board downtown to JCI.

    Thanks again for the warm welcome,

    Chiller1

  4. #4
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: YORK YAEP recip chiller fault

    Quote Originally Posted by chiller1 View Post
    Thanks Grizzly,
    I was afraid it was something like that. unfortunately, although I am stationed out of the UK (Mildenhall) I am currently in Qatar and site access is extremely limited. I will have to see if the crazy people with the money will let me take the board downtown to JCI.

    Thanks again for the warm welcome,

    Chiller1
    Hi Chiller1.
    Your best bet is to speak to your local JCI Guys and between yourselves you should be able to resolve the access issues.
    As I doubt they will be able to "reset" just the board remotely, as far as I know it needs to be installed in the chiller.
    For ALL The different parameters to be checked and reset.
    Let us know how you get on?
    Grizzly

  5. #5
    Join Date
    Mar 2001
    Location
    ireland
    Age
    53
    Posts
    1,450
    Rep Power
    41

    Re: YORK YAEP recip chiller fault

    Chiller

    did you get sorted? unit needs to be told gas type, r22 or r407c, once set all other set points are automatically programmed, lp cut out etc.

    pm me if you want

    al

  6. #6
    chiller1's Avatar
    chiller1 Guest

    Re: YORK YAEP recip chiller fault

    Grizzly,

    I talked JCI out of the code and all is now good - thanks for the advise

    Chiller1

  7. #7
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,697
    Rep Power
    46

    Re: YORK YAEP recip chiller fault

    Quote Originally Posted by chiller1 View Post
    Grizzly,

    I talked JCI out of the code and all is now good - thanks for the advise

    Chiller1
    Thanks for the update and well done. It's not easy getting info from York oops JCI.
    I suspect it is your American Military Connection?
    You can knock Americans all you like, but they do respect and treat you guys as One should!
    Grizzly
    (But then again being ex UK. Services myself I am biased)

  8. #8
    chiller1's Avatar
    chiller1 Guest

    Re: YORK YAEP recip chiller fault

    Quote Originally Posted by al View Post
    Chiller

    did you get sorted? unit needs to be told gas type, r22 or r407c, once set all other set points are automatically programmed, lp cut out etc.

    pm me if you want

    al
    Thanks Al, I managed to get it sorted once I talked JCI out of the code.

    Chiller1

  9. #9
    genebryan06's Avatar
    genebryan06 Guest

    Re: YORK YAEP recip chiller fault

    hi, may i know how you reset the error in york chiller? reprogram type of refrigerant? can u pm me pls coz i have thesame trouble too.thank you very much

Similar Threads

  1. york recip chiller model ydaj77xt9
    By kolab technical in forum Trouble Shooting
    Replies: 9
    Last Post: 10-01-2011, 07:23 PM
  2. York Recip Millenium Chiller
    By iceman007 in forum Trouble Shooting
    Replies: 12
    Last Post: 28-07-2009, 07:21 PM
  3. York Screw Chiller How low will it go?????
    By bruceboldy in forum Industrial Compressors
    Replies: 11
    Last Post: 10-08-2007, 10:29 PM
  4. Chiller fault
    By iceman007 in forum Trouble Shooting
    Replies: 9
    Last Post: 27-06-2006, 06:15 AM
  5. Chiller Fault
    By iceman007 in forum Air Conditioning
    Replies: 2
    Last Post: 13-05-2006, 07:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •