Results 1 to 17 of 17
    Feb 2008
    Lima - Peru
    41
    49
    Blast Freezer Help me please
    HI guys:
    I have a big problem, i'm calculating a refrigeration load in a blast freezer but i have a question how can i compute the refrigeration load for the fan? i'm confused. i hope that you help me.
    Sorry i don't know to write very well in english.
    Jul 2006
    74
    865
    26
    Re: Blast Freezer Help me please
    Assuming the fan motor is in the space, which is almost always the case, all the electrical imput of the motor turns to heat. I forget home many BTUs per actual Horsepower used, but that is the method.
    Jun 2006
    jiansu
    38
    dear lussandoval,
    please sent emil to me. Maybe i can help you. liweijian@worldbase.cn
    India
    688
    You need to know the Evaporator fan HP or you have to assume it to start with.
    HP X 2546.699= btu/hr.
    With this you have to see what apacity & what fans are getting selected. If your assumption is not matching, you have to recalculate using the right fan HP.
    Feb 2008
    Lima - Peru
    41
    49
    Guys:
    thanks a lot, the blast freezer's parameters:
    * Five fans with fan motor inside of the blast freezer with a power of 12.7 KW c/u.
    *air temperature inside blast freezer is -35ºC.
    So
    Q= 5*17.27(HP)*2546.699= 219907.5 btu/h
    is correct this Compute???
    Aug 2008
    California
    28
    Following the units I get
    5*12.7KW *1000 W/KW * 3.4121 BTU/hr/W=190500 BTU/hr
    Dan
    Aug 2005
    5,302
    You cannot use the simple fan motor input power. It will be too low. The actual power input is increased due to the heavier air density. As the air gets colder it becomes more dense. This requires more input power to compensate for the increased mass flow of air.
    Fans are constant volume devices.
    The fan performance data is usually based on standard conditions which are sea level and about 70°F.
    Aug 2008
    Englewood, CO
    23
    I think the fact that more HP would be required would show itself by a larger motor being employed and that converting HP to BTU would still be the way to go and would in fact be generous if the motor isn't fully loaded.
    Aug 2005
    5,302
    While the colder air temperatures do overload the motor (higher amps than nameplate) the motor itself does not overheat due to the cold air itself.
    I've heard too many stories where electrician's wired up the motor to nameplate amps and found the wiring and starters were too small for the amp draw.
    The best way is to ask the manufacturers what the amp draw is at the operating temperature the unit is designed for.
    If the motor was operating at ambient temperatures (or elevated temperatures) then oversizing the motor is a good idea for two reasons:
    1. the motor will run cooler
    2. the motor is more efficient around 75-85% of it's full load nameplate rating.
    Oct 2003
    5,630
    34
    What about apparent power ?
    Aug 2008
    Englewood, CO
    23
    US Iceman is right. I also thought of this after making my previous reply. Manufacturers recognize the benefit of low ambient temp and take advantage effectively 'overloading' the motors. So, using the actual operating amps x volts and converting to BTU would be the way to go.
    Same with "air-over" motors on cooling towers. Always use nameplate amps to size starters.
    Aug 2005
    5,302
    The problem is you won't know the motor amps until you are down to temperature. The method I use to help get the estimate closer is to use:
    Nameplate FLA X (air density cold / air density ambient) = corrected amp load
    Or use this for the motor heat:
    Motor Input Power (kW or HP) X (air density cold / air density ambient) = estimated power input. Convert this to heat energy and you have the motor heat load.
    Oct 2003
    5,630
    34
    Altough this is interesting, we're drifting a litlle bit away from the initial question: determining the heat load from a fan.
    Aug 2008
    Englewood, CO
    23
    No, I don't think we're drifting at all. I look at it like this...
    All of the energy supplied to the motor shows up as heat energy to the enclosed space. The electrical energy could just as well operated a resistance grid heater instead of a motor/fan. It's all the same.
    India
    688
    Dear Us Iceman,
    Thanks for the nice inputs.
    Nov 2008
    alaska
    58
    11
    Hi all:
    I have these design issues regularly in my blast freezers. All energy put into motors is added as heat in the box (either as motor heat or fan friction heat)and must be removed. If the evap manufacturer matched the fan blades for the working temp, your nameplate amps will be a good number, if not, assume you will be running a higher amperage (as much as 20% over nameplate,not a problem usually with a -40 ambient).Both are out there commonly, especially if evaps are used in other than designed conditions (used evaps installed). If you have an operating system, amp clamping will give you a good number for the calculations.
    I can't locate the reference, but somewhere I recall a 1.1 factoring for load as well, probably to account for motor inefficiency (usually 93% ish on a high efficiency). I like to err on the high side for heat load, no customer complains if your system overperforms.
    I once worked on a blast tunnel that was running 500 hp of fans (spec'd by an airflow guy with no consideration for refer load), they were running 700hp of compressor just to chill the box !. I removed 360 hp of fans and reconfigured evaps for a 300% increase in production.
    Hope this helps
    Dan
    Jun 2001
    N.Ireland
    1,630
    Hi Guys
    another way to look at the fan load is start with a good design, fan power input wise.
    Blast freezers, 15 - 20% of required refrigeration will be the fans.
    Now this is dependant on good airflow design, we should be looking to use a good airflow design.
    Another point is smaller motors will be less efficent, it would require less actual power if you use larger motors and less of them.
    An 11kW motor times 1.1 for freezer use will use 12.1kW mechanical power or an electrical load of 15.125kW.
    Correct me if Im wrong this 15hp motor will load the refrigeration plant by over 15kW.
    Kind Regards Andy
  1. Trolley freezer & blast freezer
    By smpsmp45 in forum NH3
    Last Post: 25-08-2007, 07:29 AM
  2. Blast Freezer
    By w.l.ong in forum Industrial
    Last Post: 16-12-2006, 10:34 AM
  3. Blast Freezer Questions
    By rickmor in forum Industrial
    Last Post: 11-04-2006, 08:15 PM
  4. Blast Freezer Evaporators Selection
    By Mahmoud in forum Fundamentals
    Last Post: 21-09-2005, 04:31 PM