    Blast Freezer Help me please



    HI guys:

    I have a big problem, i'm calculating a refrigeration load in a blast freezer but i have a question how can i compute the refrigeration load for the fan? i'm confused. i hope that you help me.

    Sorry i don't know to write very well in english.



  2. #2
    Join Date
    Jul 2006
    Location
    USA
    Age
    73
    Posts
    865
    Rep Power
    26

    Re: Blast Freezer Help me please

    Assuming the fan motor is in the space, which is almost always the case, all the electrical imput of the motor turns to heat. I forget home many BTUs per actual Horsepower used, but that is the method.

  3. #3
    Join Date
    Jun 2006
    Location
    jiansu
    Posts
    38
    Rep Power
    0

    Re: Blast Freezer Help me please

    dear lussandoval,
    please sent emil to me. Maybe i can help you. liweijian@worldbase.cn

  4. #4
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: Blast Freezer Help me please

    You need to know the Evaporator fan HP or you have to assume it to start with.

    HP X 2546.699= btu/hr.

    With this you have to see what apacity & what fans are getting selected. If your assumption is not matching, you have to recalculate using the right fan HP.

  5. #5
    Join Date
    Feb 2008
    Location
    Lima - Peru
    Age
    41
    Posts
    49
    Rep Power
    0

    Re: Blast Freezer Help me please

    Guys:

    thanks a lot, the blast freezer's parameters:

    * Five fans with fan motor inside of the blast freezer with a power of 12.7 KW c/u.

    *air temperature inside blast freezer is -35ºC.

    So

    Q= 5*17.27(HP)*2546.699= 219907.5 btu/h

    is correct this Compute???

  6. #6
    Join Date
    Aug 2008
    Location
    California
    Posts
    28
    Rep Power
    0

    Re: Blast Freezer Help me please

    Following the units I get

    5*12.7KW *1000 W/KW * 3.4121 BTU/hr/W=190500 BTU/hr

    Dan

  7. #7
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Blast Freezer Help me please

    You cannot use the simple fan motor input power. It will be too low. The actual power input is increased due to the heavier air density. As the air gets colder it becomes more dense. This requires more input power to compensate for the increased mass flow of air.

    Fans are constant volume devices.

    The fan performance data is usually based on standard conditions which are sea level and about 70°F.
    If all else fails, ask for help.


  8. #8
    Join Date
    Aug 2008
    Location
    Englewood, CO
    Posts
    23
    Rep Power
    0

    Re: Blast Freezer Help me please

    Quote Originally Posted by US Iceman View Post
    You cannot use the simple fan motor input power. It will be too low. The actual power input is increased due to the heavier air density. As the air gets colder it becomes more dense. This requires more input power to compensate for the increased mass flow of air.

    Fans are constant volume devices.

    The fan performance data is usually based on standard conditions which are sea level and about 70°F.
    I think the fact that more HP would be required would show itself by a larger motor being employed and that converting HP to BTU would still be the way to go and would in fact be generous if the motor isn't fully loaded.

  9. #9
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Blast Freezer Help me please

    While the colder air temperatures do overload the motor (higher amps than nameplate) the motor itself does not overheat due to the cold air itself.

    I've heard too many stories where electrician's wired up the motor to nameplate amps and found the wiring and starters were too small for the amp draw.

    The best way is to ask the manufacturers what the amp draw is at the operating temperature the unit is designed for.

    If the motor was operating at ambient temperatures (or elevated temperatures) then oversizing the motor is a good idea for two reasons:

    1. the motor will run cooler
    2. the motor is more efficient around 75-85% of it's full load nameplate rating.
    If all else fails, ask for help.


  10. #10
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Blast Freezer Help me please

    What about apparent power ?
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  11. #11
    Join Date
    Aug 2008
    Location
    Englewood, CO
    Posts
    23
    Rep Power
    0

    Re: Blast Freezer Help me please

    Quote Originally Posted by US Iceman View Post
    While the colder air temperatures do overload the motor (higher amps than nameplate) the motor itself does not overheat due to the cold air itself.

    I've heard too many stories where electrician's wired up the motor to nameplate amps and found the wiring and starters were too small for the amp draw.

    The best way is to ask the manufacturers what the amp draw is at the operating temperature the unit is designed for.

    If the motor was operating at ambient temperatures (or elevated temperatures) then oversizing the motor is a good idea for two reasons:

    1. the motor will run cooler
    2. the motor is more efficient around 75-85% of it's full load nameplate rating.
    US Iceman is right. I also thought of this after making my previous reply. Manufacturers recognize the benefit of low ambient temp and take advantage effectively 'overloading' the motors. So, using the actual operating amps x volts and converting to BTU would be the way to go.

    Same with "air-over" motors on cooling towers. Always use nameplate amps to size starters.

  12. #12
    Join Date
    Aug 2005
    Location
    USA
    Posts
    5,302
    Rep Power
    25

    Re: Blast Freezer Help me please

    The problem is you won't know the motor amps until you are down to temperature. The method I use to help get the estimate closer is to use:

    Nameplate FLA X (air density cold / air density ambient) = corrected amp load

    Or use this for the motor heat:

    Motor Input Power (kW or HP) X (air density cold / air density ambient) = estimated power input. Convert this to heat energy and you have the motor heat load.
    If all else fails, ask for help.


  13. #13
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Blast Freezer Help me please

    Altough this is interesting, we're drifting a litlle bit away from the initial question: determining the heat load from a fan.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  14. #14
    Join Date
    Aug 2008
    Location
    Englewood, CO
    Posts
    23
    Rep Power
    0

    Re: Blast Freezer Help me please

    Quote Originally Posted by Peter_1 View Post
    Altough this is interesting, we're drifting a litlle bit away from the initial question: determining the heat load from a fan.
    No, I don't think we're drifting at all. I look at it like this...
    All of the energy supplied to the motor shows up as heat energy to the enclosed space. The electrical energy could just as well operated a resistance grid heater instead of a motor/fan. It's all the same.

  15. #15
    Join Date
    May 2007
    Location
    India
    Posts
    688
    Rep Power
    17

    Re: Blast Freezer Help me please

    Dear Us Iceman,

    Thanks for the nice inputs.

  16. #16
    Join Date
    Nov 2008
    Location
    alaska
    Age
    58
    Posts
    11
    Rep Power
    0

    Re: Blast Freezer Help me please

    Hi all:

    I have these design issues regularly in my blast freezers. All energy put into motors is added as heat in the box (either as motor heat or fan friction heat)and must be removed. If the evap manufacturer matched the fan blades for the working temp, your nameplate amps will be a good number, if not, assume you will be running a higher amperage (as much as 20% over nameplate,not a problem usually with a -40 ambient).Both are out there commonly, especially if evaps are used in other than designed conditions (used evaps installed). If you have an operating system, amp clamping will give you a good number for the calculations.
    I can't locate the reference, but somewhere I recall a 1.1 factoring for load as well, probably to account for motor inefficiency (usually 93% ish on a high efficiency). I like to err on the high side for heat load, no customer complains if your system overperforms.
    I once worked on a blast tunnel that was running 500 hp of fans (spec'd by an airflow guy with no consideration for refer load), they were running 700hp of compressor just to chill the box !. I removed 360 hp of fans and reconfigured evaps for a 300% increase in production.

    Hope this helps

    Dan

  17. #17
    Join Date
    Jun 2001
    Location
    N.Ireland
    Age
    50
    Posts
    1,630
    Rep Power
    24

    Re: Blast Freezer Help me please

    Hi Guys

    another way to look at the fan load is start with a good design, fan power input wise.

    Blast freezers, 15 - 20% of required refrigeration will be the fans.

    Now this is dependant on good airflow design, we should be looking to use a good airflow design.


    Another point is smaller motors will be less efficent, it would require less actual power if you use larger motors and less of them.

    An 11kW motor times 1.1 for freezer use will use 12.1kW mechanical power or an electrical load of 15.125kW.

    Correct me if Im wrong this 15hp motor will load the refrigeration plant by over 15kW.

    Kind Regards Andy
    If you can't fix it leave it that no one else will:rolleyes:

Similar Threads

  1. Trolley freezer & blast freezer
    By smpsmp45 in forum NH3
    Replies: 0
    Last Post: 25-08-2007, 07:29 AM
  2. Blast Freezer
    By w.l.ong in forum Industrial
    Replies: 17
    Last Post: 16-12-2006, 10:34 AM
  3. Blast Freezer Questions
    By rickmor in forum Industrial
    Replies: 2
    Last Post: 11-04-2006, 08:15 PM
  4. Blast Freezer Evaporators Selection
    By Mahmoud in forum Fundamentals
    Replies: 12
    Last Post: 21-09-2005, 04:31 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •