Thread: Ref piping
-
28-08-2008, 11:40 AM #1
Ref piping
Plz help in designing pipe sizes for R134a refrigeration system form compressor to condensor and to DX evaporator.
-
28-08-2008, 11:24 PM #2
Re: Ref piping
Base your suction pipe sizes on the vapour velocity to return the oil back to the compressor.
The liquid line needs to be sized to prevent excessive pressure loss.
If you are designing new systems then you really need to have the correct text books to hand.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
29-08-2008, 05:58 AM #3
Re: Ref piping
Bryon, I believe this web page will get him the information he needs Ck it out on page 23 (piping Charts)
http://www.heatcraftrpd.com/res/pdf/H-IM-64L-002.pdf
-
05-09-2008, 06:36 AM #4
Re: Ref piping
Thanks Mr.Brian & Mr.Wambat
Piping i deigned referring ASHRAE handbbok.
My case one compressor,Bitzer Make capacity 272kw is pumping refrigerant 3 different AHU(DX coil).
1)AC Plant & one AHU of 36.5TR is in same room in Ground Floor.
2)Second AHU is in first floor of capacity14.5TR.
3)Third AHU is in 5th floor of 8TR.Each floor height is 2.3 Metres.
How to design the sysytem? like whether receiver,LOF etc required or not.If required how to select each equipment of what capacity.
Please give your valuable reply
Similar Threads
-
refrigerant piping desing guide
By german in forum Refrigeration BooksReplies: 11Last Post: 17-01-2009, 11:10 PM -
Q: Piping installation for Split Types
By brianubaldo in forum RefrigerantsReplies: 11Last Post: 30-04-2008, 02:23 PM -
Cable tray for refrigerant Piping
By harsen in forum FundamentalsReplies: 5Last Post: 13-02-2007, 02:02 PM -
Piping Advice
By Mickvee in forum Air ConditioningReplies: 10Last Post: 11-06-2006, 03:39 PM -
Vibration in refrigerant piping
By US Iceman in forum Technical DiscussionsReplies: 5Last Post: 01-05-2006, 11:53 PM