    Pipework Pressure Testing



    Hi All,
    I'm new to air con and would appreciate some info from you guys.
    My question is with regard to pipework pressure testing and the gas type used. I understand that oxygen free nitrogen is prefered, but could any inert gas be used? I ask as I have access to an unlimited supply of pure argon. Is pure argon an option? If not, why not? Thanks in advance.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Pipework Pressure Testing

    Now there's a question that comes around now and again.

    Have a look here Mike......
    http://www.refrigeration-engineer.co...ighlight=argon
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Aug 2001
    Location
    UK
    Posts
    1,046
    Rep Power
    24

    Re: Pipework Pressure Testing

    .

    OFN is essential, not preferred. Any oxygen in ordinary industrial grade Nitrogen in contact with oil can be lethal. Plus it may contain moisture and other impurities.

    Similarly, welding grade or commercial grade Argon may contain impurities that you may not want in your system.


    Why not stick with the tried and tested methods?

    .
    Last edited by Argus; 27-08-2008 at 09:32 AM.

  4. #4
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34
    Argon is also an inert gas, so why not?
    Legally, he can use it anyhow.
    If you look once to the Material Safety data Sheet, you will notice that Argon is 100% pure with no impurities.
    http://praxair.com/praxair.nsf/AllContent/D03E8B4AA7B2958785256A86008095F7/$File/p4563h.pdf
    and
    http://encyclopedia.airliquide.com/s...003A_AL_EN.pdf

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Pipework Pressure Testing

    Also, of course, because the Argon molecules are larger than those of nitrogen it will not show up the smallest leaks.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Jun 2005
    Location
    California
    Posts
    394
    Rep Power
    19

    Re: Pipework Pressure Testing

    If I were working on centrifugal compressors again I would defintely try leak detection using the hydrogen method. THis is becoming
    more common in industry. One reason for this
    is that hydrogen is the cheapest tracer gas available.
    The actual gas mix used is a safe mixture of 5%
    hydrogen in nitrogen. Another reason is the inherent characteristics of hydrogen. Hydrogen is the lightest and least viscous of all gases. It spreads very quickly throughout the test object and seeps quickly through the smallest leak.

    Background interference is easily minimized because of the speed with which hydrogen dissipates.The method requires no pumps or vacuum and only needs a minimum of maintenance.

Similar Threads

  1. Pressure testing for leaks on split a/c systems
    By mrchatts in forum Air Conditioning
    Replies: 46
    Last Post: 08-04-2010, 10:02 AM
  2. Benji
    By benji in forum Trouble Shooting
    Replies: 29
    Last Post: 30-01-2008, 01:25 PM
  3. OFN Pressure testing hoses.
    By Teknicool in forum Trouble Shooting
    Replies: 7
    Last Post: 08-07-2007, 11:41 AM
  4. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •