    Hanbell Screw Compressor Not Loading



    Hi Guys, Just new in this forum I just want to ask all the expert in Hanbell Screw Compressor. I have a new 3 chillers with 2 hanbell screw compressor each. All the compressor is not loading to 100% even the 4 steps of loading is reach. The chiller refrigerant is 134-a the amp draw up to 53% only. All the controller, design water flow rate, pressure drop across the evaporator and condenser, sequence of loading and the compressor parameters are normal (subcooling, superheat and split temp. accros the evap. and condenser).

    Thank you very much

    God Bless



  2. #2
    Join Date
    Aug 2007
    Location
    Adelaide Australia
    Age
    70
    Posts
    562
    Rep Power
    24

    Re: Hanbell Screw Compressor Not Loading

    Hi Denjosh
    You said the 4 steps of loading have been reached. On the 4 step RC12 -RC24 compressor there should be 3 solenoids. As the solenoids de-energise in sequence the compressor should load up.
    If SV1 is energised the compressor will be at 25%, if SV1 is de-energised and SV3 is energised it will be at 50%, when SV2 is energised and SV3 is de-energised it will be at 75% and when all solenoids are de-energised it will be at 100%.
    Check to make sure teh sequence is correct.
    Hope this helps, let us know how you go.
    Paul

  3. #3
    Join Date
    Nov 2005
    Location
    kankroli
    Posts
    30
    Rep Power
    0

    Re: Hanbell Screw Compressor Not Loading

    Yes, me too would suggest the same procedure

  4. #4
    Denjosh's Avatar
    Denjosh Guest

    Re: Hanbell Screw Compressor Not Loading

    Hi guys thank you for the replies. We found out the cause and it was a design issue. Thanks again

  5. #5
    Join Date
    Jan 2006
    Location
    Valrico, Florida
    Posts
    509
    Rep Power
    19

    Re: Hanbell Screw Compressor Not Loading

    Quote Originally Posted by Denjosh View Post
    Hi guys thank you for the replies. We found out the cause and it was a design issue. Thanks again
    Just curious; what was the design issue?

  6. #6
    Refkid's Avatar
    Refkid Guest

    Re: Hanbell Screw Compressor Not Loading

    I would like to know about the design problem you found.

  7. #7
    Join Date
    Apr 2009
    Location
    israel
    Age
    50
    Posts
    778
    Rep Power
    19

    Re: Hanbell Screw Compressor Not Loading

    Quote Originally Posted by Denjosh View Post
    Hi guys thank you for the replies. We found out the cause and it was a design issue. Thanks again
    Hi we had a similar problem,on rc-10 turned out to be a faulty seal on sv we replaced all the seales all is ok compressor loads to 100% as demanded to.
    THE DEFINITION OF A SMART PERSON IS ONE WHOM LEARNS FROM HIS MISTAKES!!!

Similar Threads

  1. VSD on screw machines
    By Mike Hopkins in forum New Technologies
    Replies: 14
    Last Post: 20-02-2011, 12:10 AM
  2. Compressors - screw or reciprocating?
    By Josip in forum Industrial Compressors
    Replies: 18
    Last Post: 27-01-2009, 10:36 PM
  3. Replies: 7
    Last Post: 23-09-2008, 09:24 AM
  4. Autoloading slide valve for Screw compressor
    By screw_geek in forum Industrial Compressors
    Replies: 32
    Last Post: 04-04-2008, 03:47 AM
  5. Mono or twin screw
    By Nirmalya in forum Industrial Compressors
    Replies: 43
    Last Post: 12-09-2006, 03:19 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •