    Cooling towers Vs Riverwater cooling



    Hi guys, looking for a little help with my uni dissertation. I am looking into the CO2 & cost savings (long term) of using river water to cool a condenser as opposed to using a cooling tower. One question that has been thrown up from looking at other works is, why is there an increase in CoP when using river water? Is it as simple as the ambient temperature of the water is less than the wet bulb of air?

    cheers for any help clearing this up,.



  2. #2
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Cooling towers Vs Riverwater cooling

    If fresh water cooling is an option, then throw HSE regulations at the project and you will see that a cooling tower can't compete.
    The costs and environmental impact from water-treatment of a cooling tower will be astronomical in comparison to cleaning the strainers on the river water loop.

    Another option would be a closed loop (collector) submerged in the river.

    The CoP thing I think that you got sussed, it is also another heat exchange to take place in the cooling tower and the water going through the tower will not reach WBT.

  3. #3
    Cammy's Avatar
    Cammy Guest

    Re: Cooling towers Vs Riverwater cooling

    Thanks mate, glad i got that part sorted!

    DO you happen to know if there are any rule of thumb figures associated with the cost of dosing for cooling towers per Litre of water or something along those lines?

  4. #4
    Join Date
    Feb 2007
    Location
    UK
    Posts
    2,473
    Rep Power
    45

    Re: Cooling towers Vs Riverwater cooling

    Unfortunately it will vary depending on a lot of factors, one of which is what council it is located in.
    Your best option would be to contact a local water treatment company and ask them, another option to find someone that operates a cooling tower locally to you.

    A while back, we quoted for maintenance for a site with a cooling tower and IIRC, the annual cost for the water treatment were almost £10k.

  5. #5
    Cammy's Avatar
    Cammy Guest

    Re: Cooling towers Vs Riverwater cooling

    Jesus! that's pretty expensive.

    I have one more question, sorrythis could go on forever, if i am saying assume a CoP of 4 for a cooling tower cooled system, is it reasonable to assume that the CoP for water source cooling could be 7 (or 8)?

    Also, which calculation can i use to show this, cop=heat rejected/power input? the problem is i dont have any manufacturers data for this project so it's all a bit up in the air.

    thanks for any info

  6. #6
    Join Date
    Aug 2008
    Location
    Islamabad
    Age
    38
    Posts
    5
    Rep Power
    0

    Re: Cooling towers Vs Riverwater cooling

    Thanks a lot dear.

  7. #7
    Join Date
    Dec 2004
    Location
    Weihai,China
    Posts
    800
    Rep Power
    20

    Re: Cooling towers Vs Riverwater cooling

    Quote Originally Posted by Cammy View Post
    Jesus! that's pretty expensive.

    I have one more question, sorrythis could go on forever, if i am saying assume a CoP of 4 for a cooling tower cooled system, is it reasonable to assume that the CoP for water source cooling could be 7 (or 8)?

    Also, which calculation can i use to show this, cop=heat rejected/power input? the problem is i dont have any manufacturers data for this project so it's all a bit up in the air.

    thanks for any info
    Hi Cammy
    You're right to assume the COP of the cooling tower is around 4 ,but COP of the water source is 7 or above is not reasonable. Both the cooling system only affect the condensing temperature, the river water temp is lower than ambient air and the average water temp of the cooling season decide the chiller condensing temperature. If the cop up to 7 or above ,the theoretic condensing temp should be lower than 25C, it's not reasonable.

    Cooling tower and river water all need water treatment. River water cooling should be better use close-loop heat exchanger.


    regards
    LC
    I hear...I forget;I see...I remember;I do...I understand

  8. #8
    Join Date
    Aug 2008
    Location
    Englewood, CO
    Posts
    23
    Rep Power
    0

    Re: Cooling towers Vs Riverwater cooling

    What about the fish? We have a local power plant using river water to condense steam but environmental regulations force the operator to run the water through cooling towers before putting the water back into the River. In the end, he is only able to increase river temp by 2-3 degreesF.

Similar Threads

  1. cooling tower's free cooling issue
    By Lc_shi in forum New Technologies
    Replies: 12
    Last Post: 30-01-2011, 04:41 AM
  2. Book For Sale HVAC Water Chillers and Cooling Towers
    By johnyfreon in forum Chit Chat & Service Stories
    Replies: 14
    Last Post: 20-08-2008, 09:19 PM
  3. Compressor loading, cooling, and range of operation.
    By Air duster in forum Fundamentals
    Replies: 10
    Last Post: 02-04-2008, 08:39 AM
  4. energy cost comparison between chillers with cooling towers
    By kuruman in forum Tools and Calculators
    Replies: 7
    Last Post: 23-12-2006, 01:17 PM
  5. Cooling tower evaporation, blowdown, makeup and cycles
    By miltbeychok in forum Fundamentals
    Replies: 0
    Last Post: 13-10-2005, 05:14 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •